Well that could have been worse
Mike_Sheppard
Mike_Sheppard Member Posts: 696
edited May 2019 in THE MAIN WALL
I don’t have any more details. Just thought you guys would get a kick out of the relief valve... Was found by a co-worker. Was brand new.
The two lines coming down into the relief valve tapping are returns from zones....
Never stop learning.
    Steamhead Member Posts: 17,879
    Once again- you can't fix stupid!
    Consulting
    Solid_Fuel_ManIronman
    EBEBRATT-Ed Member Posts: 18,119
    Little bit of shrapnel.
    Well, there's a lawsuit waiting to happen
    CLamb
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,881
    I would not want to be the one who left that relief valve down stream of a shutoff.valve! Sorta like painting a bullseye on your back.
    Yours, Larry
  • Mike_Sheppard
    > Yours, Larry
    Not only that, it’s also installed backwards!
  • ratio
    ratio Member Posts: 4,040
    The mind boggles.
  • delta T
    delta T Member Posts: 884
    Well......at least the relief valve is installed in the upright position....*sigh*
    Solid_Fuel_ManCanuckerJean-David Beyer
  • ScottSecor
    ScottSecor Member Posts: 994
    With regard to the relief valve, it looks like they went with the lowest bidder, or was it the owner's brother in law that's kind of handy???
    What's left of the boiler and burner look like they may have been installed by a professional. Maybe not the very best installation, but probably acceptable. I'm guessing the installer was long gone when that relief valve was installed?
    ethicalpaul Member Posts: 7,720
    Wow. So did some other control fail?
  • SeanBeans
    SeanBeans Member Posts: 525
    Ouch
  • Mike_Sheppard
    To my knowledge, this was a brand new boiler. They had just installed it and started it up for the winter. I believe it was installed like this from day 1.
    edited May 2019
    But, if you’re not careful, stupid will fix you? >:)
    Yours, Larry
    If only it were that simple. Stupid usually "fixes" innocent people, and not in a good way.
    For the benefit of non-pros reading this- not sure what type of building this is in, but if the boiler had exploded worse than it did, it could have taken the whole building with it, along with everyone inside.
    Consulting
    In that case, if you haven't already done so, you need to go over the whole installation. No telling what else they did that was stupid, and you were the last one to touch it.
    Consulting
    CLamb
  • ScottSecor
    Wow, I just looked a little closer at the picture of the Powerflame burner. Notice the shutoff valve on the small pilot pressure regulator with the copper compression fitting. You are never supposed to install a shutoff valve on the vent of a gas pressure regulator. Must have been same guy that piped the boiler relief valve.
    I also noticed yet another shutoff valve that is piped into one of the 1/4 inch tapping on the bottom of the Honeywell gas valve, wonder where that goes?
    I realize all contractors make mistakes, but this one is getting more interesting as the story develops. After further review, I take back my earlier comment about it looking like a professional install. I hope no one got hurt!
  • ScottSecor
    Please keep us posted as things develop. Maybe we'll all learn something.
    Still wondering what failed first? With this limited information, my guess is the limits were incorrectly wired and did not turn off burner during an unsafe condition.
  • Jean-David Beyer
    Lucky that shutoff valve is closed off. That way it protects the pressure relief valve (installed backwards) from the rest of the system. Gawd!
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,644
    edited May 2019
    With the welded steel pipe, and a boiler big enough to warrant that size Power Flame, I'm guessing this is at least a light commercial system. There are many things wrong here! Wow! While it is amusing now, that could have been catastrophic for sure.
    That really is the definition of stupid. Whoever did that should not be in the heating business. Valved relief....dumb, backwards relief........Stupid! Compressions on gas line....against code, valved ragulayor vent......Stupid! Returns T'd into relief port is just weird.
    I dont use the word stupid lightly when applied to people.
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,781
    @Mike_Sheppard Can I use that pic for my classes
    Ray Wohlfarth
    Boiler Lessons
  • Alan Welch
    Alan Welch Member Posts: 270
    Maybe the relief valve can be salvaged and used on the new boiler,
    Solid_Fuel_Man
    @Mike_Sheppard , I sure hope the licensing authorities get involved..............
    Consulting
    Jean-David Beyer
  • Mike_Sheppard
    LOL! I did not even notice the valve on the vent. Wow!
  • Mike_Sheppard
    edited May 2019
    Sure!
    I want to see it in your next book! Lol
  • Mike_Sheppard
    This was an apartment building.
    The boiler is gone by now. A new boiler with a proper install and permits was done.
    The section blew out because the relief valve was isolated. Those sections are rated for 80 psi. I’m sure it saw well above 80 psi.
    Nothing the controls could have done about it, it was a water boiler. No pressuretrols.
  • ScottSecor
    Mike, was there no expansion tank on this system, or was that valved off too? Aquastats jumped too (wonder if they even installed them)?
  • Mike_Sheppard
    @ScottSecor I am not sure. A co-worker was the one who found this and sent me pictures.
    @ScottSecor
    Your right about the valve on the pilot regulator vent, I haden't noticed that. The other 1/4" coming of the bottom of the Honeywell valve is for checking gas pressure or it is sometimes used for a low gas pressure switch, although I don't like coming off the bottom for a safety control
  • Intplm.
    Intplm. Member Posts: 2,663
    Every once in a while we come across something like this.
    Can't help but wonder how many are installed in such a dangerous way. This is maybe the sixth boiler I have either seen in a picture or come across first hand.
    Makes me wonder, are installations getting worse or better? Is the qualified tech. surely becoming extinct?
