Near boiler piping
tlavite
Member Posts: 3
Got a question about my near boiler piping... it just doesn’t seem right to me. I have no formal knowledge in one pipe steam heating but I have read books and quite a bit of stuff over the last couple of years owning this system. I’ve done allot of Maintinence to this system since I moved in and did allot of work to balance my system. It works perfectly for me but my big question is boiler cycle times... for instance once it fires up and finally hits full pressure which is 2psi how long should the system be able to hold that pressure before bleeding off and kicking back on? My system seems to bleed it’s pressure off quite quick. But the near boiler piping looks nothing like everything else I have seen in my 3 years of research and playing with my system.
Well, the near boiler piping is perhaps a little unusual -- but that has nothing whatever to do with how long it's going to take the steam in the radiators to condense once the burner shuts off and the pressure drops to the cutin level (or lower, if there is a longish post purge and prepurge). In a more direct answer to your question, the system won't hold pressure at all -- the pressure will start to drop immediately when the boiler cuts out. Depending on the size of the system, if might take anywhere from 30 seconds to a minute or two for it to drop to the cutin.Br. Jamie, osb
Thanks for the response. Sounds like it’s operating normally then I have 8 relatively large radiators in my house 2 stories. So once it shuts off after reaching pressure it takes about a minute or 2 before the cut in happens. At least I know now that’s within normal time.0
You have a Weil-McLain EG50. It definitely needs to be repiped it’s completely wrong.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......2 -
Your main air vent hiding up in the rafters could be bigger.
But upgrade will be limited by the riser nipple size.
As Ed said, another example of a really badly piped boiler that fairly works OK.
You can download the install manual for that to see the minimal piping requirement.0 -
Surprisingly it has no water hammer at all and no vents spit any water... like I said the system seems to operate perfectly fine. The main does need upgraded I’m gonna tap that pipe for a larger riser. When I moved in the main vent it did have was clogged like crazy and half the vents on the rads didn’t work either. Plus all valves needed repacked and I had to replace one rad for a big crack in it.0
