How not to vent a Gas condensing boiler
  • SuperTech
    SuperTech Member Posts: 2,606
    Lol. It just needs a little more RTV
  • Jean-David Beyer
    Do not gas condensing boilers require two "vents," one for air supply and one for exhaust, so that the differential pressure between them is extremely low?
  • nibs
    nibs Member Posts: 516
    My Rinnai E50 allows for using room air.
    Steamhead Member Posts: 17,880
    Once again- you can't fix stupid!
    Consulting
    Ironman
  • Ironman
    Ironman Member Posts: 7,724
    Are you kidding? What idiot did this?
    Bob Boan
  • JUGHNE
    JUGHNE Member Posts: 11,450
    Any pictures of the rest of the install?
    Homeowner job?
    EBEBRATT-Ed Member Posts: 18,135
    edited January 2019
    Probably not a homeowner. Most of them have more sense.
    RTV coated flue. Must be a new design.
    I am surprised the off gassing from the curing RTV didn't take someone out.
  • Grallert
    Grallert Member Posts: 969
    I think that Viessmann allows for room air, I guess that's why the cover is off.
  • Leonard
    Leonard Member Posts: 903
    edited January 2019
    that RTV burns,
    not knowing any better I used it to line a rusted exhaust suction fan cavity on a Carrier nat gas flat roof HVAC unit we owned. When I tested it red hot burning bits of red "fire-proof" RTV blew out........ I replaced it.
  • Do not gas condensing boilers require two "vents," one for air supply and one for exhaust, so that the differential pressure between them is extremely low?
    They could also have removed one or two of the rubber flaps on top of the boiler to allow air in.
    rwhtg
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    edited February 2019
    We use room air on most install of furnaces and boilers unless it’s a very tight home. Too many service calls for plugged intakes to make it worth the minimal impact or the cost of extra piping. Code requires it on some cases.
    But code book writers and inspectors don’t have to clear frozen intakes when it’s -15F outside in 2’ of snow.
  • NY_Rob
    NY_Rob Member Posts: 1,370
    If you're venting with PVC and are in an area where snow buildup/blockage is a concern, you could always install a Cleanout Tee with Cap in the intake piping and just remove the cap for as long as needed if it becomes necessary. No going outside to shovel.
    FWIW- I have read regarding mod-cons that it desirable to use outdoor air for combustion vs. indoor air whenever possible because the outdoor air is generally "cleaner".
    https://www.supplyhouse.com/Spears-P444X-030-3-PVC-DWV-Cleanout-Tee-w-Standard-Plug
    mikeg2015
  • mikeg2015
    Outdoor air is cleaner so long as there’s no grass clippings. But lint and dust would be less and chemicals depending on location. Downside is bugs getting in. We’ve just found we have dramatically fewer issues using indoor air all around and of course you can offer a slightly lower installed price.
    The clean out is a good idea on longer runs.
  • Slimpickins
    Slimpickins Member Posts: 359
    When it says it allows room air you first have to do the math and determine if you have enough cubic feet to allow it. You're really doing your customer a dis-service by not bring intake air into the appliance unless it's absolutely impossible.
    Alan Muller
  • Leonard
    Seems a plus to using interior air in cellar is ventilation ..... if have radon, mustiness, etc......
  • ChrisJ
    ChrisJ Member Posts: 16,806
    Not that I'm defending this disaster but most red RTVs are rated to be used at 600 degrees F and the only "off gassing" would be acedic acid which smells like vinegar from the RTV curing. Once cured I wouldn't expect any smell.
    I wouldn't think you would be venting at 600+ into that vent.
    Like I said, not defending anything in that picture.
    rick in Alaska
  • mikeg2015
    It’s not a disservice if there are fewer call backs that way. These are not tight construction cookie cutter modern homes.
    That combustion air gets heated regardless of where its introduced, direct or indirectly. So there no change to net system efficiency.
    We use 2 pipe where it’s nessesary. Most of these installs were previously B vent or chimney vent furnaces at one time, and most were just gravity coal furnaces before that.
  • plumbbob
    plumbbob Member Posts: 19
    whats wrong with it it looks great :)
  • Timco
    Timco Member Posts: 3,040
    Can I play?
    Just a guy running some pipes.
    Intplm.Zman
  • Timco
    I'll add this beauty....
    rick in AlaskaZman
  • Jean-David Beyer
    And the inspector passed this?
  • ChrisJ
    That's a 50 50.
    Are you surprised if one did?
  • Leon82
    Leon82 Member Posts: 684
    Is the intake teed into the exhaust?
  • Leon82
    It's like they saw a diagram of the concentric vent and moved it to there.
    That couldn't have run more than a few seconds before it started convulsing
  • mikeg2015
    You think they opened the manual?
    Easy fix since it’s not newer tight construction. Just make it 1 pipe.... assuming HTP/Westinghouse allows that.
  • Jean-David Beyer
    Not really. One inspector approved my new heating system when there was a 12 foot (or so) long piece of bright yellow CSST gas pipe going straight across the garage (where my heating system is) that was neither bonded nor grounded. A different inspector approved the condensate drain just dumping the condensate on the ground outside. Another inspector ... . The list never ends.
  • Timco
    And it did not...We do allow for room air intake and there are provisions in our manuals for that, and tables showing required openings to rooms that do not provide enough free air or space. Clearly they saw a concentric and said I can do that! Same pipe is easy!
  • Nutjob
    Nutjob Member Posts: 8
    ChrisJ said:
    In vehicle exhaust systems this would be scavenging - moving exhaust flow from a small diameter pipe to a larger diameter. But what do I know? I'm not a plumber.
  • CapnCurt
    CapnCurt Member Posts: 1
    Room air is often permitted with the appropriate room volume etc. But if the fundamental principle of a condensing boiler is to capture heat from flue gas condensate, it seems to me that the colder the intake air, the more efficient the condensate heat recovery would be... particularly if using a concentric flue arrangement. Thoughts?
