    If CO was high that would be a real danger. PROVIDING the tech took the readings before the draft damper. Too many variables
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • GW
    GW Member Posts: 4,692
    Options
    Cleaning the boiler: it’s all easy when you know what you’re doing😀
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    ratio
  • adasilva
    adasilva Member Posts: 144
    edited December 2018
    Options

    Double the fire rate is an immediate danger. Wow! Please confirm the rotation of the meter

    OK so my android doesn't like to play with microsoft & the video is too big of file. Anyway the 1/2 foot meter turns one total revolution every 12 seconds..........................
  • GW
    GW Member Posts: 4,692
    Options
    Ahh that’s better, 150,000
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • adasilva
    adasilva Member Posts: 144
    Options
    @GW Yes but the boiler from what I was told shouldn't get more than 140,000?
  • GW
    GW Member Posts: 4,692
    Options
    And it’s easier to move the video to YouTube and then paste the link, but I think you’re good, just need a good sweeping
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    adasilva
  • GW
    GW Member Posts: 4,692
    Options
    1.05 is 147000 unless I’m having a bad math moment
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    adasilva
  • adasilva
    adasilva Member Posts: 144
    Options
    @GW OK one last thing.....this meter should spin smoothly and not have any hesitations while the boiler runs? I did notice some hesitations as it turned.............
  • GW
    GW Member Posts: 4,692
    Options
    I don’t really like to rely on the 1/2 foot dial, maybe I’m too OCD who knows. But did you make a mistake on the 4 cu fit per minute? Your two numbers don’t align with each other. Maybe time for a tie breaker
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    adasilva
  • Steamhead
    Steamhead Member Posts: 16,835
    Options
    Well, THAT's a relief.

    A good cleaning, proper burner tuning and combustion test, and you'll be in a lot better shape.

    Still need to know if the boiler has the proper gas-type barometric with a blocked-flue switch on it. This is the swinging disc that is mounted in the smoke pipe. Post a pic of this so we can see.

    Then you can work on getting your steam system optimized.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • adasilva
    adasilva Member Posts: 144
    Options
    @GW I mave have had a hiccup on that one! It appears that it's about 2.5 per min.........
  • adasilva
    adasilva Member Posts: 144
    Options
    Steamhead said:

    Well, THAT's a relief.

    A good cleaning, proper burner tuning and combustion test, and you'll be in a lot better shape.

    Still need to know if the boiler has the proper gas-type barometric with a blocked-flue switch on it. This is the swinging disc that is mounted in the smoke pipe. Post a pic of this so we can see.

    Then you can work on getting your steam system optimized.

    No blocked flue switch........don't scold me as I just learned this yesterday. The man that Tim M suggested is who I am going to get to tweak my system & make sure that the orifice, diffuser plate is correct ETC. I'm sure that he will mention that the flue is an issue............
  • adasilva
    adasilva Member Posts: 144
    Options
    @Steamhead FYI the pic is from last year and I know it's not the best.
  • GW
    GW Member Posts: 4,692
    Options
    Uhoh now you’re gonna get some feedback on the general boiler installation 😀
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    Canuckerratioethicalpaul
  • adasilva
    adasilva Member Posts: 144
    Options
    @GW eh let em bring it,if it was my personal work I'd be embarrassed but it's what I got with my house. It's come a long way from the way it was that's for sure!!
    GWethicalpaul
  • Steamhead
    Steamhead Member Posts: 16,835
    Options
    Here is a thread with pics of what a well-installed steamer should look like. It contains a link to one we did:

    https://forum.heatinghelp.com/discussion/168108/most-times-when-we-post-a-diy-install
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaul
  • adasilva
    adasilva Member Posts: 144
    edited December 2018
    Options
    @Steamhead not to inflate your ego or anything but I have that photo as a reference for when I do my drop header and move my equalizer pipe to where it belongs! You sir are a master at your craft!
    Erin Holohan Haskell
  • adasilva
    adasilva Member Posts: 144
    Options
    I detest spell correction on my phone......
  • Steamhead
    Steamhead Member Posts: 16,835
    edited December 2018
    Options
    adasilva said:

    I detest spell correction on my phone......

    You thought that was bad..............
    Well, I tried to link to some "Damn You Auto-Correct" videos but they displayed in such a way as would tarnish the reputation of this family-friendly site- check them out on YouTube.

    >:)
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    adasilva
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,520
    Options
    Seems like when I first mentioned over firing it was an understatement. I hope the meter reading is wrong. 240k input would give a higher stack than that I would think but something is off
    adasilvaCharlie from wmass
  • gfrbrookline
    gfrbrookline Member Posts: 753
    Options
    Look up @New England SteamWorks he is based out of RI and is a true steam master.
    adasilva
  • adasilva
    adasilva Member Posts: 144
    Options
    @gfrbrookline if the young man I contacted does not touch base with me by next week I will see if he can help me out!