Cyclegard woes
kcopp
kcopp Member Posts: 4,630
I have pretty much had it w/ the std probe type low water cutoffs that came w/ many packaged boilers. The critical time you are trying to make steam it "takes a break"... Is the safeguard 450 a straight swap out to the CG450?
Thanks.
  • EzzyT
    EzzyT Member Posts: 1,378
    Yes it is. can’t stand the cycle guard too. I must of over 50 of them in stock from the boiler installs I’ve done over the past year.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    kcopp
  • Fred
    Fred Member Posts: 8,542
    Yep, and the probe is the same so you don't even have to drain the boiler.
    kcopp
  • Gordo
    Gordo Member Posts: 857
    I wish there was a good way to disable the "psycho-guard" feature after the boiler gets a proper cleaning.
    kcopp
  • Canucker
    Canucker Member Posts: 723
    If you have 50 of them build a small trebuchet and fire them on the roof of 126 Bailey Road, North Haven, CT 06473. ;)
    You can have it good, fast or cheap. Pick two
    kcopp
  • kcopp
    Of course the boiler Mfg is really the "culprit"... They spec them out. I guess We need to start complaining to them.
    Canucker
  • ChrisJ
    ChrisJ Member Posts: 17,072
    I'd easily rather a MM 67 over a cycleguard.
  • kenlmad
    kenlmad Member Posts: 56
    I figured out how to disable the intermittent "Test" mode on the CG-450-1560. It requires soldering in a short jumper wire on the circuit board. I verified it on my workbench and confirmed that all regular LWCO features remains fully functional. Is it safe to post the modification here?
    I could easily add a $3 toggle switch to disable or enable the Test mode, depending upon the quality of the boiler water.
    kcopp
  • amitjm1980
    amitjm1980 Member Posts: 33
    I just swapped mine for a Safgard too! I would just have people PM you instead of posting it here to be safe. I still have my cyclegard so I could use the instructions to mod it and keep as a back up. Can you send to amitjm1980@gmail.com?
  • hvacfreak2
    hvacfreak2 Member Posts: 500
    And quite a few other models and brands actually.
    hvacfreak
    Mechanical Enthusiast
    Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV's
    Easyio FG20 Controller
  • Ironman
    Ironman Member Posts: 7,869
    Would you p/m the info to me, please?
    Bob Boan
    pecmsg Member Posts: 6,781
    Maybe run that by the manufacture before changing the design of a Safety Device!
    Canucker
  • kenlmad
    @pecmsg - I agree with you. I will not post the mod. Replacing the Cyclegard with the corresponding Safgard is the proper approach if the intermittent on/off anti-foam cycling isn't necessary on your system.
  • kcopp
    Better yet.... can we get a trade in program? Return the Psycho-gaurd for a Safe guard? I would certainly like to know how to modify it.
  • Fred
    We may need to rethink our dislike for the Cyclegard. At least for those who have over-sized steam boilers, which is a good portion of the steam market. One of the Steam Pros did some assessment on the Cyclegard and posted here (see Link Below) and that suggests that the Cyclegard reduced boiler output by about 10%. That's a decent start to taming an over sized boiler. It may not be enough but coupled with extra good main venting, maybe some down firing, and/or a two stage gas valve, it could bring a boiler into a reasonable range, until it is replaced.
    https://forum.heatinghelp.com/discussion/169155/loss-of-boiler-capacity-due-cycle-guard#latest