Electric Radiant Boilers
I am looking for recommendations on electric radiant boilers. It will be powered by 208 volt 3 phase (wye) and will require 125,000 btu output.
(Before you recommend a different energy source...we only pay 2.7 cents per kilowatt hour)
Thanks in advance, Alan
http://www.electromn.com/gen/boilers.htm
Check these out. I've used them in remote locations and liked them.Steve Minnich0 -
They both look like good options. Thank you.
Any thoughts on the Slantfin units? http://www.slantfin.com/products/monitron-eh-boiler/0 -
Is your power Wye or delta?
The slantfin units are nice, but they run on Wye and the largest model only has a little over 100,000 btu output with 208 volts.0 -
Is there a source that will sell these boilers online?
http://www.thermo2000.com/index_en.aspx
I am running in to the standard protectionist BS..."We only sell complete systems" or "We only sell to contractors" or if it's the manufacturer, "We only sell through distributors"0 -
I buy a lot of Electro factory direct as they are only 40 miles from my house and provide better support than the local distributors do anyway, but there are a couple decent online suppliers I've had good luck with in the past. Just type the model number into the Google search bar and you'll find what you need0
WyeHarvey Ramer said:Is your power Wye or delta?
Thermo 2000 at Menards. maybe not all the models however. A 3 phase is probably a special order. Look up the rep in your area and ask for dealer info.winesalot said:Is there a source that will sell these boilers online?
I am a little puzzled by the Delta vs Wye conversation. I am under the impression that most US systems are either 3 phase Wye (120/208 or 277/480) or split single phase (120/240).
3 phase Delta is more common in industrial applications and involves concepts like corner grounding, sine approach angles and other things that give me a headache thinking about.
Perhaps @Jamie Hall could explain it better....
Albert Einstein0 -
You are an optimist, @Zman ! Almost all North American systems are three phase Y, and your voltages are correct: the 120 or 277 is any single phase to neutral, and the 208 or 480 is between phases. And there is a neutral as well as a ground. Three phase delta doesn't have a neutral (there is a ground) and the phase to phase voltage is usually 240 by the time it gets into any normal switchboard. The split single phase which is the normal house connection is taken from either one by a transformer (which may be either phase to ground from a Y main line or phase to phase from a delta main line -- you'd have to ask the power company, but the former is more common) which has a center tapped neutral and ground). Converting one to the other is no big deal -- but does require transformers.
The reason Y is used is that unbalanced loads on the phases don't matter, assuming that the neutral is intact. Delta tends to get squirrely if the loads on the phases aren't very very close to the same.Br. Jamie, osb
What, no mention of 3Φ 4 wire Δ, @Jamie Hall?
Think of a 120/240 V can with two 240 V cans closing the triangle. The best thing about this setup is the wild leg, the phase that's directly opposite the neutral tap on the 120/240 V can. Through the miracle of physics, it runs at around 208 V to ground! (Not as uncommon around here as one might hope.) The best tell is a panel with every 3rd space open or a multi-pole breaker.
Then there's the open delta service, which is just what it sounds like, three phases with only two transformers. I have actually seen one of these in the wild.
- 85.7K THE MAIN WALL
- 51 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
