House Not Getting to 70 in Sub Freezing Weather
JesseG
Member Posts: 19
I have 1 floor hour house (about 1200 sq ft) which uses a boiler and radiators for heating. Ever since I have moved in the house I have been fighting a losing battle trying to get the house warm. After the first year, the old boiler died and I got it replaced with a new boiler. Ever year I bleed the radiators to remove any air bubbles that hasn't helped. Last year, I had a heating audit performed where they found where air was leaking in the house and got it all sealed and put in insulation into my attic and sub-basement. All of this still has not resulted in the house getting above 66 when the temperature outside is 20 or below?
Is there anything else I can do? Tired of freezing in my own home and other then space heaters I feel like there are not real options.
Jesse can you get a little more specific. If your not super technical load up some pix of your system. Once the Pros have an idea what we are all talking about some good questions and feedback will come your way0
GW,
Sure, sorry about that should have thought about taking some pictures. Below are some images. As for my radiators, i have 8 in total with 7 being base board radiators and 1 being cast iron.
I also took a picture of the temperature gauge which was at 170 degrees.0
In your last photo, you will see a gray box with the name "Honeywell" on it. Remove the cover of the box.
Take a look at figure 2 on page 4 the following documentation and confirm that it is identical to your control:
https://customer.honeywell.com/resources/Techlit/TechLitDocuments/60-0000s/60-2278.pdf
If it is identical, turn the high limit dial to 190F and then wait. See if that solves your issue (it will probably take six hours in this cold).
If you’re handy, turn up the temp a little in that Honeywell (grey box) control. If you’re not handy, don’t, you may shock yourself or kill the control
You may need 180 or even higher.
Make sure your baseboards are clear and good proper convection can take place. Grab a flashlight, you want to be able to “see” through the fins. Make sure the louvres are fully opened (sometimes get close on by themselves)0 -
That boiler has a internal piped primary secondary arrangement. Most likely cause is the system pump is not running. The culprit is normally the mixing board which is in the 3rd photo. It can be bypassed and have both pumps run at the same time until part arrives.0
Looks like a Burnham Revolution boiler. They have an internal mixing pump, make sure it is set up and working properly as Uncle suggested. The controller on the early versions were somewhat finicky, as were the early Honeywell Smart Valves.Bob "hot rod" Rohr
Need some temperature data to evaluate flows. Supply temp, return temp.
Is the boiler running continuously or cycling on and off.
Next I’d want to know what the radiant load is. Then knowing the gas bill compared to heating degree days to estimate builds gheat loss.0 -
So I had a professional come out and they said that the boiler is working fine and the temperature is correct. The issue is that the circulator pumped was installed backwards so that water isn't getting reheated after it circulates around the house. He said that he will replace the circulator pump and that should fix the issue.0
They said the part was overheating from years of operating that way. They finished putting in the new part and about an hour later my house is still 65 degrees.
So frustrating, not sure what else I can do.0 -
@unclejohn I was going to say you know how much work is involved cutting all the pipes loose and turning the boiler 180 degrees so the pump is pumping the right direction
sorry to the OP I couldn't resist.... 0 -
Call the company back and ask to speck to the owner. Like I said the issue is most likely the board or the internal pump. Use this link to find you install book, look at page 74. Your system pump is designed to pump away which it most likely was and now it is installed backwards. If the internal boiler pump doesn't work no water flows through the heat exchanger.
https://file.ac/izXtTdMo_L4/
Good luck.0 -
Thank you @unclejohn. I've already reached out to the company and waiting to hear back.0
How about a picture of the pump they just fixed, but from the back side of it. People here familiar with that system can tell if it is now backwards from where it should be.
Include the pipes above and below it.0 -
So the guys came back out and said the internal pump and the board are fine. They weren't thrilled with the choice of the boiler but functionally they say it is fine as well.
The senior engineer come along this time to assist and he said the problem is it needs to be re-piped. He said the placement of the pumps are completely wrong which is why the house never can get warm. I'm sure I'm butchering the explanation, but basically he says they need to repipe it.
What do you guys think? Does that seem reasonable?0 -
Yup.Br. Jamie, osb
OP said one large cast iron radiator, and the rest baseboard... Sounds like a thermal balancing issue to me, and based on what I can see from his pictures, that Taco 007 was pumping away, correctly.
If you were water, and you had a choice of going through a large, wide open cast iron radiator or a 3/4" long skinny tunnel, which way would YOU go...?
Just guessing, but I'd bet the radiator is hotter than blazes, and the baseboard, is just kinda hot...
We've sent him through the "Turn it up" syndrome, to no avail, and no one has asked how long the boiler actually runs for.... Is it doing a 100% duty cycle, or?
ME0 -
@Mark Eatherton after the circulator pump was changed I haven't its seems like the pipes feeding into the baseboard radiator panels and the iron radiator itself are both very hot. I hear the furnace running every few minutes but its now 100% of the time.0
By the way this is an excellent forum. I wish I had found it earlier with years of battling this issue. Really appreciate all of the help and guidance from everyone, especially being someone who is really out of their element on this subject.0
Just to update everyone, I had a second expert come out. There thought was repiping may or may not help but he was doubtful that it would provide the heat needed during cold weather. What he suggested to me was adding a forced air heating system to work in combination or instead of the radiant heating.
He said that while he liked radiant heating because my subbasement is not finished and no matter what I do it may not get the house warm during really cold temperatures. I mentioned that my AC unit (forced air) was about 20 years old (installed July 98) and that I would eventually need to replace it. What he then suggested was putting in a unit that would allow me to get forced air heating and AC. He said they could put a coil in the attic that would kick on during cold days that could provide extra heat in addition to kicking on my radiator.
I'm intrigued by this option since growing up and in my first house I had forced air heating and never experienced any issues even with the houses being much bigger than my current house.
Any thoughts on this approach over repiping?0 -
Did this problem exist your first winter? Or did it start after the boiler was replaced?
Either there is a very simple piping problem with your system, or there was never enough radiation to deal with the weather you are experiencing.0 -
Yes it did happen the first winter and then the boiler died the next year.0
So you have a complete ducted forced air system for the AC now? If so a coil could be added to heat via that system, from the boiler.
I believe that boiler is around 84,000 BTU/hr. it should be plenty of horsepower for a 1200 sq ft home, probably twice what you need.
Somehow, somewhere you are not getting the heat energy from the boiler to the space.
If all pipes are hot, sounds like you do not have enough heat emitters, radiators and or fin tube.
Seems a hydronic pro would be able to see that and be able to add more or bigger emitters.Bob "hot rod" Rohr
Yes you are correct, I already have ducts in every room for AC. In the summer the house never has a problem getting cold. It seems from looking at the forums the heating pros seem to favor radiant over forced air. I guess my issues with getting the house warm for so long have turned me off to the thought of it. I have a few more experts coming out later this week for more opinions.
So far, I have
- Repipe
- Add Forced Air0 -
When you get one of these they will tell you what the problem is and make you warm. Seriously 85k BTU for 1200 square feet is way more than enough.JesseG said:Yes you are correct, I already have ducts in every room for AC. In the summer the house never has a problem getting cold. It seems from looking at the forums the heating pros seem to favor radiant over forced air. I guess my issues with getting the house warm for so long have turned me off to the thought of it. I have a few more experts coming out later this week for more opinions.
So far, I have
- Repipe
- Add Forced Air
If the person who installed the boiler doesn't understand why it's not working then I would suggest they don't know what they are doing. The problem isn't the system, it sounds like the problem is the contractor.
I wouldn't trust the advice you got from that contractor.0 -
Absolutely, all of these contractors are no longer the ones that did the original install. I essentially gave up on them figuring this out after having them come back several times over. Both the contractor who suggested repiping and the other who is saying to put in forced air are completely new contractors.0
If the forced air option was a hot water coil run from the boiler, it might be a viable option -- provided the piping and radiation problem is simply that there isn't enough radiation and you can't add any more.
If it is a heat pump, then no. A heat pump is a decent bet in the shoulder seasons, but in the more severe cold we have been having it isn't, at least in my view. Particularly when you have ample capacity in the boiler and just need someone competent to make use of it.
Where are you located? Have you tried the "find a contractor" tab on this site? Or we may know someone who works in your area who actually knows what they are doing.Br. Jamie, osb
Good idea didn't check out the contractors listed on this site. I live in Bethesda, MD just outside of Washington, DC.0
Get hold of @Steamhead . He's in Baltimore, and if he can't take it on (he does mostly steam) he'll know someone reliable in your area who will.Br. Jamie, osb
@Jamie Hall Thanks will do.0
Thanks, @Jamie Hall . Before calling us, @JesseG should see if @Dan Foley is available- he serves the DC metro area.All Steamed Up, Inc.
Consulting1 -
@Steamhead Thanks will do.0
The boiler is only half the system and I must confess is usually the source of most problems, but the piping to the heat emitters and the heat emitters are the other half of the system. How about pictures of that. You say the baseboards are hot. Anything over 98.6 degrees is hot. Take measurements with a thermometer, both input and output. That way you know.0
Resting a thermometer on the pipe coming into one of radiators it reads at 113 degrees. Doing the same on a pipe coming out of the radiator reads at 97 degrees.0
Sounds like your flow is going somewhere other than the radiators. Please post a diagram of all boiler and radiation piping. Hand drawn is fine.0
So just an update on this issue. @Dan Foley came out and resolved my issue! Sounds like the issue was similar to what @unclejohn and @hot rod mentioned with the injection pump not coming up to speed. So he hot wired the injection pump and in just a few minutes i saw my thermostat hitting 75!!! Next step is to get piping insulated which he also recommended.
Thanks again to @Dan Foley who within an hour helped solve a problem I have been fighting for years!6 -
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam