PVC primer + combustion analyser
ratio
Member Posts: 4,176
Would a PVC primer spill (cleaned up, but still noticeable) make an impact on the combustion of a modcon? The cover has to be off to access the gas valve, so it's definitely sucking fumes in.
I suspect there's no way for anyone to answer this unless they've been in the same exact situation and tested before and after the fumes cleared.
Is there a huge purple stain on the floor?
Guessing, I'd say it may lower your excess O2, in theory as it's a fuel.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I would be surprised if the primer had any effect.
For best results, you would measure the combustion with the cover on as that is how the system will operate. I have found it is always a bit different open vs closed. Usually you would get it close with the door off then open and close it to make the fine tune adjustments."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
When you start up your combustion analyzer out side then bring it inside what do you get for numbers? Any changes?0
Small purple stain. CO2 was a little higher than they wanted, but I wasn't able to fire it on high long enough to get reliable numbers. I've got to go back. I was just wondering if anyone knew for certain that it does or doesn't make a noticeable difference.0
Zman, the manual indicated I should expect about .2 difference cover off vs cover on, i was planning on accounting for that, then verify with the cover on.
kcopp, I don't recall any difference inside to outside.
In any case, I expect the fumes to be cleared out before I get there next week. It was more of a 'I wonder' question. Maybe I'll pour a little out after I've dialed it in & see what it does!