Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Switching 240V 5KW garage heater

ChrisJ
ChrisJ Member Posts: 16,205
Just wanted to bounce an idea off of everyone before pulling the trigger.

My dad wants to switch his ceiling hung garage heater with a remote thermostat because it's internal one is effected by the heater it self too much.

My plans are to use a 40A contactor controlled by a 24VAC transformer + standard thermostat. Contactor will be enclosed in a metal box on the side of the heater. The heater's internal thermostat will still be in use for limiting reasons. Basically, the heater will be 100% original, I'll just be switching it's input.

The heater is on a 30A circuit so I chose a 40A contactor just to be on the safe side.

Is there a better way to do this?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
«1

Comments

  • KC_Jones
    KC_Jones Member Posts: 5,785
    Chris I am pretty sure Johnson controls makes something to do this in a single unit. I have a friend that uses one on a chest freezer that he runs as a beer cooler. From what he told me it can be used for heating also. The one he has was only like 30 bucks, but it's a 120V, I would guess they make one for 240V also? Might be worth a look?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    ChrisJ
  • SWEI
    SWEI Member Posts: 7,356
    Check out the Aube (Honeywell) line voltage stats. Most even modulate...
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,205
    SWEI said:

    Check out the Aube (Honeywell) line voltage stats. Most even modulate...

    The modulate part got my attention. :)

    The only issue I'd have is I don't want to switch the line voltage 40 feet from the heater which is where I want the stat?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • SWEI
    SWEI Member Posts: 7,356
    Looks like they make a RedLink EIM, but it only switches 3k. I'd give them a call -- Honeywell takes care of English language support here in the US.
    ChrisJ
  • hot_rod
    hot_rod Member Posts: 22,965
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    ChrisJkcopp
  • ChrisJ
    ChrisJ Member Posts: 16,205
    hot rod said:
    Interesting, but only has a 20A rating. Cutting it kind of close. :(

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • SWEI
    SWEI Member Posts: 7,356
    edited January 2016
    Most of the line voltage stats run a PWM type algorithm on TRIACs (to switch at the zero crossing) rather than phase chopping (like a lamp dimmer.) A solid state relay would work better than a contactor for this kind of on/off cycling.

    Thermolec, Electro, and several others make controls for electric resistance heating that might be another option.
  • Tinman
    Tinman Member Posts: 2,808
    What is the make and model of the unit? Q-Mark? Many of them are very specific in the installation instructions on the type of stat to use. Many are already setup to use a 24 volt thermostat
    Steve Minnich
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    Why are you guessing at the amperage?

    ME

    There was an error rendering this rich post.

  • Tinman
    Tinman Member Posts: 2,808
    edited January 2016
    20.83 amps @ 240 volts, single phase. If it's a Marley, Q-Mark, or Dayton they usually just required a single pole thermostat hooked up to control board. No contactor necessary.
    Steve Minnich
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,205
    edited January 2016

    Why are you guessing at the amperage?

    ME

    I'm not?
    I don't know why you think I am?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Tinman
    Tinman Member Posts: 2,808
    The 2YU62 is a 208/240 5kw heater using a SPST thermostat (field supplied) and already has a contactor built into it.
    Steve Minnich
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,205

    20.83 amps @ 240 volts, single phase. If it's a Marley, Q-Mark, or Dayton they usually just required a single pole thermostat hooked up to control board. No contactor necessary.

    After you said this I decided to find the actual heater and look it up. It appears to be made by Marley even though it's a "Berko".

    Sure enough, there's a contactor in it and it sure looks like I can easily get rid of the factory thermostat if I want.


    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ChrisJ
    ChrisJ Member Posts: 16,205
    What kind of wire would typically be used to connect a line voltage thermostat like this?

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Tinman
    Tinman Member Posts: 2,808
    It's hard to see exactly what the stat is actually seeng in terms of amp draw based on that drawing, but if it's the full boat of 20.83 amps, 20' distance like you said, #10 THHN is what I'd use.
    Steve Minnich
  • ChrisJ
    ChrisJ Member Posts: 16,205
    edited January 2016
    I'm mistaken.
    We had found a few heaters, that's not the one heat bought in the end though.

    Dang it.

    No contactor in the heater.


    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Tinman
    Tinman Member Posts: 2,808
    I still don't see the need to add a contactor.
    Steve Minnich
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,205
    edited January 2016

    I still don't see the need to add a contactor.

    I suppose it isn't absolutely necessary, but he wants the thermostat 40 feet from the heater and I'd rather switch the current right at the heater if possible.

    Running 18-2 wire that whole length will be cheaper and harder to see as well. The last place I want to go is in the attic. :)

    I could also do a 25A SPST relay, but the contactor seems safer.

    Would you still use a line level thermostat and run the wire all that length?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ChrisJ
    ChrisJ Member Posts: 16,205

    I still don't see the need to add a contactor.

    I think you may have changed my dad's mind.
    He apparently has the wire on hand and a line level thermostat is a whole lot cheaper. :p
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Jamie Hall
    Jamie Hall Member Posts: 24,401
    ChrisJ said:

    I still don't see the need to add a contactor.

    I think you may have changed my dad's mind.
    He apparently has the wire on hand and a line level thermostat is a whole lot cheaper. :p
    That's fine -- but remember while you are playing that the lines in question must be sized according to the protective breaker or fuse on the circuit, not the draw of the unit.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ChrisJ
    ChrisJ Member Posts: 16,205

    ChrisJ said:

    I still don't see the need to add a contactor.

    I think you may have changed my dad's mind.
    He apparently has the wire on hand and a line level thermostat is a whole lot cheaper. :p
    That's fine -- but remember while you are playing that the lines in question must be sized according to the protective breaker or fuse on the circuit, not the draw of the unit.
    Absolutely.
    Though to be honest, I don't "play" with this stuff.

    Now my dad has gone back to wanting me to set him up with a 24VAC thermostat. He doesn't want to run the wire and apparently he has 10-3 on hand which would be a waste.

    The circuit is a 30A.

    You know what they say, the customer is always right. Especially when he's your old man.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • SWEI
    SWEI Member Posts: 7,356
    I would install the contactor (or the SSR -- I still think that's a better option here since it switches on the zero crossing) inside the heater. That way, you can safely interrupt only one of the hot legs. Anything mounted externally should really interrupt both ungrounded current-carrying conductors.
  • ChrisJ
    ChrisJ Member Posts: 16,205
    SWEI said:

    I would install the contactor (or the SSR -- I still think that's a better option here since it switches on the zero crossing) inside the heater. That way, you can safely interrupt only one of the hot legs. Anything mounted externally should really interrupt both ungrounded current-carrying conductors.

    He says he wants it external so it's easy to swap heaters.
    My plans are to use a double pole contactor to interrupt both hots as you said.

    One thing I am concerned about is he wants the metal box mounted on the sheetrock, not the heater where I want it. Thoughts?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Tinman
    Tinman Member Posts: 2,808
    Honeywell makes a contactor specifically for electric resistance heat, opens and closes quietly from what I remember. R8246?
    Steve Minnich
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,205
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • SWEI
    SWEI Member Posts: 7,356
    Sure -- just put the contactor and a 240V 24VAC transformer in a NEMA enclosure and mount that on the wall.

    We keep these on the shelf in both 120 VAC and 24 VAC coil versions -- mostly for controlling well pumps.
  • Tinman
    Tinman Member Posts: 2,808
    I was thinking of the R8246A1038. Is that what Kurt recommended?
    Steve Minnich
  • Tinman
    Tinman Member Posts: 2,808
    Cutting it close on the amp draw.
    Steve Minnich
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,205

    Cutting it close on the amp draw.

    It is, but being a pre-assembled unit I assumed they came up with those specs with a 5kw heater or similar in mind. What I don't like is it's wires are 12awg.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ChrisJ
    ChrisJ Member Posts: 16,205
    Don't like the 12awg wires, and like Stephen Minnich said it's 22amp rating is cutting it close.

    Going to go with a contactor + transformer in a NEMA rated enclosure as per @SWEI s recommendation. Looks like Supplyhouse has everything I need but the enclosure unless I just can't find it.

    Found a few nice ones elsewhere though, specifically a Bud brand one.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    ChrisJ said:

    Just wanted to bounce an idea off of everyone before pulling the trigger.

    My dad wants to switch his ceiling hung garage heater with a remote thermostat because it's internal one is effected by the heater it self too much.

    My plans are to use a 40A contactor controlled by a 24VAC transformer + standard thermostat. Contactor will be enclosed in a metal box on the side of the heater. The heater's internal thermostat will still be in use for limiting reasons. Basically, the heater will be 100% original, I'll just be switching it's input.

    The heater is on a 30A circuit so I chose a 40A contactor just to be on the safe side.

    Is there a better way to do this?

    That bolded statement to me would indicate you don't know what the actual amperage is, hence my comment. I always size the relay or contactor to the connected load.

    ME

    There was an error rendering this rich post.

  • ChrisJ
    ChrisJ Member Posts: 16,205
    edited January 2016

    ChrisJ said:

    Just wanted to bounce an idea off of everyone before pulling the trigger.

    My dad wants to switch his ceiling hung garage heater with a remote thermostat because it's internal one is effected by the heater it self too much.

    My plans are to use a 40A contactor controlled by a 24VAC transformer + standard thermostat. Contactor will be enclosed in a metal box on the side of the heater. The heater's internal thermostat will still be in use for limiting reasons. Basically, the heater will be 100% original, I'll just be switching it's input.

    The heater is on a 30A circuit so I chose a 40A contactor just to be on the safe side.

    Is there a better way to do this?

    That bolded statement to me would indicate you don't know what the actual amperage is, hence my comment. I always size the relay or contactor to the connected load.

    ME

    Mark I'm surprised you don't know me better by now. :(

    It's a 5KW heater rated 20.8A input. As far as I know it's likely either completely, or mostly resistive. It has a fan so I suppose it can't be completely resistive.

    I liked sizing the contactor to the fuse rating on the circuit, but I suppose you're right when dealing with a switch like this. But for this the size and price are right even on a 40A unit, I see no reason to go smaller. It'll also allow my dad to swap in a larger heater if he ever wants to and I never have to worry about the load being oversized as the circuit breaker will protect it.


    Here's what I went with for a NEMA rated enclosure. I'm really happy with it, thanks @SWEI as it's much nicer than the plain U shaped boxes I was considering.





    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ratio
    ratio Member Posts: 3,770
    If that second schematic is the correct one, the plan to break both hots external to the heater will most likely cause problems. There's a fan switch that holds the fan on after the elements drop out to cool them off. If the fan drops out before the elements are cool enough, the high limit will trip.

    I've found these to be a real life-saver, but it doesn't look like it's quite got the rating you need. (I might try it anyway...)

    Barring that, an SCR would be fun to play with, but perhaps not the most cost-effective way to control it.

    But whatever you do to control it, put it in place of the stat in the diagram, don't just break the incoming power unless you're planning on visiting Dad every evening...

    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,205
    ratio said:

    If that second schematic is the correct one, the plan to break both hots external to the heater will most likely cause problems. There's a fan switch that holds the fan on after the elements drop out to cool them off. If the fan drops out before the elements are cool enough, the high limit will trip.

    I've found these to be a real life-saver, but it doesn't look like it's quite got the rating you need. (I might try it anyway...)

    Barring that, an SCR would be fun to play with, but perhaps not the most cost-effective way to control it.

    But whatever you do to control it, put it in place of the stat in the diagram, don't just break the incoming power unless you're planning on visiting Dad every evening...

    That's an interesting point I didn't think of.
    The second schematic is correct. If that is the case, I can't switch either of the lines outside of the heater, I'd specifically have to switch the thermostat line.

    Allwell, we'll see what happens. I can't have the hi-limit tripping all the time so it'll be what it'll be.

    Thanks for the heads up though, it is a very good point.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ratio
    ratio Member Posts: 3,770
    You're welcome. That particular little thing's bit me on the rear before, but I didn't catch it until the heating season - long after the Sparkys were gone. Guess who had to fix it. :/ I watch for it on electric heat now.
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,205
    edited January 2016
    njtommy said:
    Hi njtommy, thanks for commenting.

    No good. I needed to drive a 20.8A 5000W load.

    Watts (240V): 3000W
    Amps (240V): 12.5
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • njtommy
    njtommy Member Posts: 1,105
    edited January 2016
    That's fine. You could still you this and use a contactor with a 240v coil.
    ChrisJ
  • BobC
    BobC Member Posts: 5,495
    I've used these and can tell you they are bullet proof.

    http://www.mcmaster.com/#general-purpose-power-relays/=10m41d5

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • njtommy
    njtommy Member Posts: 1,105
    The price is right @BobC on target of what a contactor would be to. Bullet proof is a nice way to go too.