Switching 240V 5KW garage heater
My dad wants to switch his ceiling hung garage heater with a remote thermostat because it's internal one is effected by the heater it self too much.
My plans are to use a 40A contactor controlled by a 24VAC transformer + standard thermostat. Contactor will be enclosed in a metal box on the side of the heater. The heater's internal thermostat will still be in use for limiting reasons. Basically, the heater will be 100% original, I'll just be switching it's input.
The heater is on a 30A circuit so I chose a 40A contactor just to be on the safe side.
Is there a better way to do this?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Comments
-
Chris I am pretty sure Johnson controls makes something to do this in a single unit. I have a friend that uses one on a chest freezer that he runs as a beer cooler. From what he told me it can be used for heating also. The one he has was only like 30 bucks, but it's a 120V, I would guess they make one for 240V also? Might be worth a look?1
-
-
The modulate part got my attention.SWEI said:Check out the Aube (Honeywell) line voltage stats. Most even modulate...
The only issue I'd have is I don't want to switch the line voltage 40 feet from the heater which is where I want the stat?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Looks like they make a RedLink EIM, but it only switches 3k. I'd give them a call -- Honeywell takes care of English language support here in the US.1
-
Maybe a RIB wireless relay?
http://www.functionaldevices.com/building-automation/wireless.php#enoceanVidsBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
Interesting, but only has a 20A rating. Cutting it kind of close.hot rod said:Maybe a RIB wireless relay?
http://www.functionaldevices.com/building-automation/wireless.php#enoceanVids
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Most of the line voltage stats run a PWM type algorithm on TRIACs (to switch at the zero crossing) rather than phase chopping (like a lamp dimmer.) A solid state relay would work better than a contactor for this kind of on/off cycling.
Thermolec, Electro, and several others make controls for electric resistance heating that might be another option.0 -
What is the make and model of the unit? Q-Mark? Many of them are very specific in the installation instructions on the type of stat to use. Many are already setup to use a 24 volt thermostatSteve Minnich0
-
Why are you guessing at the amperage?
METhere was an error rendering this rich post.
0 -
-
I'm not?Mark Eatherton said:Why are you guessing at the amperage?
ME
I don't know why you think I am?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
After you said this I decided to find the actual heater and look it up. It appears to be made by Marley even though it's a "Berko".Stephen Minnich said:20.83 amps @ 240 volts, single phase. If it's a Marley, Q-Mark, or Dayton they usually just required a single pole thermostat hooked up to control board. No contactor necessary.
Sure enough, there's a contactor in it and it sure looks like I can easily get rid of the factory thermostat if I want.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
What kind of wire would typically be used to connect a line voltage thermostat like this?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
It's hard to see exactly what the stat is actually seeng in terms of amp draw based on that drawing, but if it's the full boat of 20.83 amps, 20' distance like you said, #10 THHN is what I'd use.Steve Minnich0
-
I'm mistaken.
We had found a few heaters, that's not the one heat bought in the end though.
Dang it.
No contactor in the heater.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
I suppose it isn't absolutely necessary, but he wants the thermostat 40 feet from the heater and I'd rather switch the current right at the heater if possible.Stephen Minnich said:I still don't see the need to add a contactor.
Running 18-2 wire that whole length will be cheaper and harder to see as well. The last place I want to go is in the attic.
I could also do a 25A SPST relay, but the contactor seems safer.
Would you still use a line level thermostat and run the wire all that length?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I think you may have changed my dad's mind.Stephen Minnich said:I still don't see the need to add a contactor.
He apparently has the wire on hand and a line level thermostat is a whole lot cheaper.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
That's fine -- but remember while you are playing that the lines in question must be sized according to the protective breaker or fuse on the circuit, not the draw of the unit.ChrisJ said:
I think you may have changed my dad's mind.Stephen Minnich said:I still don't see the need to add a contactor.
He apparently has the wire on hand and a line level thermostat is a whole lot cheaper.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Absolutely.Jamie Hall said:
That's fine -- but remember while you are playing that the lines in question must be sized according to the protective breaker or fuse on the circuit, not the draw of the unit.ChrisJ said:
I think you may have changed my dad's mind.Stephen Minnich said:I still don't see the need to add a contactor.
He apparently has the wire on hand and a line level thermostat is a whole lot cheaper.
Though to be honest, I don't "play" with this stuff.
Now my dad has gone back to wanting me to set him up with a 24VAC thermostat. He doesn't want to run the wire and apparently he has 10-3 on hand which would be a waste.
The circuit is a 30A.
You know what they say, the customer is always right. Especially when he's your old man.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I would install the contactor (or the SSR -- I still think that's a better option here since it switches on the zero crossing) inside the heater. That way, you can safely interrupt only one of the hot legs. Anything mounted externally should really interrupt both ungrounded current-carrying conductors.0
-
He says he wants it external so it's easy to swap heaters.SWEI said:I would install the contactor (or the SSR -- I still think that's a better option here since it switches on the zero crossing) inside the heater. That way, you can safely interrupt only one of the hot legs. Anything mounted externally should really interrupt both ungrounded current-carrying conductors.
My plans are to use a double pole contactor to interrupt both hots as you said.
One thing I am concerned about is he wants the metal box mounted on the sheetrock, not the heater where I want it. Thoughts?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I was thinking of the R8246A1038. Is that what Kurt recommended?Steve Minnich0
-
-
It is, but being a pre-assembled unit I assumed they came up with those specs with a 5kw heater or similar in mind. What I don't like is it's wires are 12awg.Stephen Minnich said:Cutting it close on the amp draw.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Don't like the 12awg wires, and like Stephen Minnich said it's 22amp rating is cutting it close.
Going to go with a contactor + transformer in a NEMA rated enclosure as per @SWEI s recommendation. Looks like Supplyhouse has everything I need but the enclosure unless I just can't find it.
Found a few nice ones elsewhere though, specifically a Bud brand one.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
That bolded statement to me would indicate you don't know what the actual amperage is, hence my comment. I always size the relay or contactor to the connected load.ChrisJ said:Just wanted to bounce an idea off of everyone before pulling the trigger.
My dad wants to switch his ceiling hung garage heater with a remote thermostat because it's internal one is effected by the heater it self too much.
My plans are to use a 40A contactor controlled by a 24VAC transformer + standard thermostat. Contactor will be enclosed in a metal box on the side of the heater. The heater's internal thermostat will still be in use for limiting reasons. Basically, the heater will be 100% original, I'll just be switching it's input.
The heater is on a 30A circuit so I chose a 40A contactor just to be on the safe side.
Is there a better way to do this?
ME
There was an error rendering this rich post.
0 -
Mark Eatherton said:
That bolded statement to me would indicate you don't know what the actual amperage is, hence my comment. I always size the relay or contactor to the connected load.ChrisJ said:Just wanted to bounce an idea off of everyone before pulling the trigger.
My dad wants to switch his ceiling hung garage heater with a remote thermostat because it's internal one is effected by the heater it self too much.
My plans are to use a 40A contactor controlled by a 24VAC transformer + standard thermostat. Contactor will be enclosed in a metal box on the side of the heater. The heater's internal thermostat will still be in use for limiting reasons. Basically, the heater will be 100% original, I'll just be switching it's input.
The heater is on a 30A circuit so I chose a 40A contactor just to be on the safe side.
Is there a better way to do this?
ME
Mark I'm surprised you don't know me better by now.
It's a 5KW heater rated 20.8A input. As far as I know it's likely either completely, or mostly resistive. It has a fan so I suppose it can't be completely resistive.
I liked sizing the contactor to the fuse rating on the circuit, but I suppose you're right when dealing with a switch like this. But for this the size and price are right even on a 40A unit, I see no reason to go smaller. It'll also allow my dad to swap in a larger heater if he ever wants to and I never have to worry about the load being oversized as the circuit breaker will protect it.
Here's what I went with for a NEMA rated enclosure. I'm really happy with it, thanks @SWEI as it's much nicer than the plain U shaped boxes I was considering.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
If that second schematic is the correct one, the plan to break both hots external to the heater will most likely cause problems. There's a fan switch that holds the fan on after the elements drop out to cool them off. If the fan drops out before the elements are cool enough, the high limit will trip.
I've found these to be a real life-saver, but it doesn't look like it's quite got the rating you need. (I might try it anyway...)
Barring that, an SCR would be fun to play with, but perhaps not the most cost-effective way to control it.
But whatever you do to control it, put it in place of the stat in the diagram, don't just break the incoming power unless you're planning on visiting Dad every evening...
1 -
That's an interesting point I didn't think of.ratio said:If that second schematic is the correct one, the plan to break both hots external to the heater will most likely cause problems. There's a fan switch that holds the fan on after the elements drop out to cool them off. If the fan drops out before the elements are cool enough, the high limit will trip.
I've found these to be a real life-saver, but it doesn't look like it's quite got the rating you need. (I might try it anyway...)
Barring that, an SCR would be fun to play with, but perhaps not the most cost-effective way to control it.
But whatever you do to control it, put it in place of the stat in the diagram, don't just break the incoming power unless you're planning on visiting Dad every evening...
The second schematic is correct. If that is the case, I can't switch either of the lines outside of the heater, I'd specifically have to switch the thermostat line.
Allwell, we'll see what happens. I can't have the hi-limit tripping all the time so it'll be what it'll be.
Thanks for the heads up though, it is a very good point.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Hi njtommy, thanks for commenting.njtommy said:
No good. I needed to drive a 20.8A 5000W load.
Watts (240V): 3000W
Amps (240V): 12.5Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
I've used these and can tell you they are bullet proof.
http://www.mcmaster.com/#general-purpose-power-relays/=10m41d5
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements