Switching 240V 5KW garage heater
ChrisJ
ChrisJ Member Posts: 17,068
Just wanted to bounce an idea off of everyone before pulling the trigger.
My dad wants to switch his ceiling hung garage heater with a remote thermostat because it's internal one is effected by the heater it self too much.
My plans are to use a 40A contactor controlled by a 24VAC transformer + standard thermostat. Contactor will be enclosed in a metal box on the side of the heater. The heater's internal thermostat will still be in use for limiting reasons. Basically, the heater will be 100% original, I'll just be switching it's input.
The heater is on a 30A circuit so I chose a 40A contactor just to be on the safe side.
Is there a better way to do this?
«1
  • KC_Jones
    KC_Jones Member Posts: 5,907
    Chris I am pretty sure Johnson controls makes something to do this in a single unit. I have a friend that uses one on a chest freezer that he runs as a beer cooler. From what he told me it can be used for heating also. The one he has was only like 30 bucks, but it's a 120V, I would guess they make one for 240V also? Might be worth a look?
    2014 Weil Mclain EG-40
    ChrisJ
  • SWEI
    SWEI Member Posts: 7,348
    Check out the Aube (Honeywell) line voltage stats. Most even modulate...
    ChrisJ
  • ChrisJ
    The modulate part got my attention. :)
    The only issue I'd have is I don't want to switch the line voltage 40 feet from the heater which is where I want the stat?
  • SWEI
    Looks like they make a RedLink EIM, but it only switches 3k. I'd give them a call -- Honeywell takes care of English language support here in the US.
    ChrisJ
    hot_rod Member Posts: 26,579
    ChrisJkcopp
  • ChrisJ
    hot rod said:
    Interesting, but only has a 20A rating. Cutting it kind of close. :(
  • SWEI
    edited January 2016
    Most of the line voltage stats run a PWM type algorithm on TRIACs (to switch at the zero crossing) rather than phase chopping (like a lamp dimmer.) A solid state relay would work better than a contactor for this kind of on/off cycling.
    Thermolec, Electro, and several others make controls for electric resistance heating that might be another option.
  • Steve Minnich
    Steve Minnich Member Posts: 2,868
    What is the make and model of the unit? Q-Mark? Many of them are very specific in the installation instructions on the type of stat to use. Many are already setup to use a 24 volt thermostat
    Steve Minnich
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,875
    Why are you guessing at the amperage?
    ME
  • Steve Minnich
    edited January 2016
    20.83 amps @ 240 volts, single phase. If it's a Marley, Q-Mark, or Dayton they usually just required a single pole thermostat hooked up to control board. No contactor necessary.
    Steve Minnich
    ChrisJ
  • ChrisJ
    edited January 2016
    ME
    I'm not?
    I don't know why you think I am?
  • Steve Minnich
    The 2YU62 is a 208/240 5kw heater using a SPST thermostat (field supplied) and already has a contactor built into it.
    Steve Minnich
    ChrisJ
  • ChrisJ
    After you said this I decided to find the actual heater and look it up. It appears to be made by Marley even though it's a "Berko".
    Sure enough, there's a contactor in it and it sure looks like I can easily get rid of the factory thermostat if I want.
  • ChrisJ
    What kind of wire would typically be used to connect a line voltage thermostat like this?
  • Steve Minnich
    It's hard to see exactly what the stat is actually seeng in terms of amp draw based on that drawing, but if it's the full boat of 20.83 amps, 20' distance like you said, #10 THHN is what I'd use.
    Steve Minnich
  • ChrisJ
    edited January 2016
    I'm mistaken.
    We had found a few heaters, that's not the one heat bought in the end though.
    Dang it.
    No contactor in the heater.
  • Steve Minnich
    I still don't see the need to add a contactor.
    Steve Minnich
    ChrisJ
  • ChrisJ
    edited January 2016
    I suppose it isn't absolutely necessary, but he wants the thermostat 40 feet from the heater and I'd rather switch the current right at the heater if possible.
    Running 18-2 wire that whole length will be cheaper and harder to see as well. The last place I want to go is in the attic. :)
    I could also do a 25A SPST relay, but the contactor seems safer.
    Would you still use a line level thermostat and run the wire all that length?
  • ChrisJ
    I think you may have changed my dad's mind.
    He apparently has the wire on hand and a line level thermostat is a whole lot cheaper. :p
    Jamie Hall Member Posts: 26,833
    That's fine -- but remember while you are playing that the lines in question must be sized according to the protective breaker or fuse on the circuit, not the draw of the unit.
  • ChrisJ
    Absolutely.
    Though to be honest, I don't "play" with this stuff.
    Now my dad has gone back to wanting me to set him up with a 24VAC thermostat. He doesn't want to run the wire and apparently he has 10-3 on hand which would be a waste.
    The circuit is a 30A.
    You know what they say, the customer is always right. Especially when he's your old man.
  • SWEI
    I would install the contactor (or the SSR -- I still think that's a better option here since it switches on the zero crossing) inside the heater. That way, you can safely interrupt only one of the hot legs. Anything mounted externally should really interrupt both ungrounded current-carrying conductors.
  • ChrisJ
    He says he wants it external so it's easy to swap heaters.
    My plans are to use a double pole contactor to interrupt both hots as you said.
    One thing I am concerned about is he wants the metal box mounted on the sheetrock, not the heater where I want it. Thoughts?
  • Steve Minnich
    Honeywell makes a contactor specifically for electric resistance heat, opens and closes quietly from what I remember. R8246?
    Steve Minnich
    ChrisJ
  • ChrisJ
  • SWEI
    Sure -- just put the contactor and a 240V 24VAC transformer in a NEMA enclosure and mount that on the wall.
    We keep these on the shelf in both 120 VAC and 24 VAC coil versions -- mostly for controlling well pumps.
  • Steve Minnich
    I was thinking of the R8246A1038. Is that what Kurt recommended?
    Steve Minnich
  • Steve Minnich
    Cutting it close on the amp draw.
    Steve Minnich
    ChrisJ
  • ChrisJ
    It is, but being a pre-assembled unit I assumed they came up with those specs with a 5kw heater or similar in mind. What I don't like is it's wires are 12awg.
  • ChrisJ
    Don't like the 12awg wires, and like Stephen Minnich said it's 22amp rating is cutting it close.
    Going to go with a contactor + transformer in a NEMA rated enclosure as per @SWEI s recommendation. Looks like Supplyhouse has everything I need but the enclosure unless I just can't find it.
    Found a few nice ones elsewhere though, specifically a Bud brand one.
  • Mark Eatherton
    That bolded statement to me would indicate you don't know what the actual amperage is, hence my comment. I always size the relay or contactor to the connected load.
    ME
  • ChrisJ
    edited January 2016
    ME
    Mark I'm surprised you don't know me better by now. :(
    It's a 5KW heater rated 20.8A input. As far as I know it's likely either completely, or mostly resistive. It has a fan so I suppose it can't be completely resistive.
    I liked sizing the contactor to the fuse rating on the circuit, but I suppose you're right when dealing with a switch like this. But for this the size and price are right even on a 40A unit, I see no reason to go smaller. It'll also allow my dad to swap in a larger heater if he ever wants to and I never have to worry about the load being oversized as the circuit breaker will protect it.
    Here's what I went with for a NEMA rated enclosure. I'm really happy with it, thanks @SWEI as it's much nicer than the plain U shaped boxes I was considering.
  • ratio
    ratio Member Posts: 4,176
    If that second schematic is the correct one, the plan to break both hots external to the heater will most likely cause problems. There's a fan switch that holds the fan on after the elements drop out to cool them off. If the fan drops out before the elements are cool enough, the high limit will trip.
    I've found these to be a real life-saver, but it doesn't look like it's quite got the rating you need. (I might try it anyway...)
    Barring that, an SCR would be fun to play with, but perhaps not the most cost-effective way to control it.
    But whatever you do to control it, put it in place of the stat in the diagram, don't just break the incoming power unless you're planning on visiting Dad every evening...
    ChrisJ
  • ChrisJ
    That's an interesting point I didn't think of.
    The second schematic is correct. If that is the case, I can't switch either of the lines outside of the heater, I'd specifically have to switch the thermostat line.
    Allwell, we'll see what happens. I can't have the hi-limit tripping all the time so it'll be what it'll be.
    Thanks for the heads up though, it is a very good point.
  • ratio
    You're welcome. That particular little thing's bit me on the rear before, but I didn't catch it until the heating season - long after the Sparkys were gone. Guess who had to fix it. :/ I watch for it on electric heat now.
    ChrisJ
  • ChrisJ
    edited January 2016
    njtommy said:
    Hi njtommy, thanks for commenting.
    No good. I needed to drive a 20.8A 5000W load.
    Watts (240V): 3000W
    Amps (240V): 12.5
  • njtommy
    njtommy Member Posts: 1,105
    edited January 2016
    That's fine. You could still you this and use a contactor with a 240v coil.
    ChrisJ
  • BobC
    BobC Member Posts: 5,539
    I've used these and can tell you they are bullet proof.
    http://www.mcmaster.com/#general-purpose-power-relays/=10m41d5
    Bob
    3PSI gauge
  • njtommy
    The price is right @BobC on target of what a contactor would be to. Bullet proof is a nice way to go too.