Boiler repair estimate

Options

Hello, I'm in need of some expertise. We have an old steam boiler, probably 1950/1960's and our LWCO has been failing, with it flooding twice last winter. Ive had a difficult time finding anyone even willing to work on it and was finally able to have a company from about 90 miles away give us an estimate. Does this sound reasonable or totally off base? Two of the main vents are leaking as well. Also attached is a pic of our boiler. What is the reason to want to relocate the presuretrol? I will obviously ask them too but wanted another take on it. Thanks so much!!!

1000009512.jpg 1000013792.jpg

Comments

  • pecmsg
    pecmsg Member Posts: 7,524

    pricings not allowed. It’s a regional thing.
    where is this boiler located, we may know someone that services that area.

  • 1902Shingle
    1902Shingle Member Posts: 30

    I'm in North Central West Virginia.

  • Jamie Hall
    Jamie Hall Member Posts: 27,769

    Beautiful country. Bit short on steam people…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • 109A_5
    109A_5 Member Posts: 4,408

    For that money I'd learn to do the work myself. How many days do they anticipate it will take ? I'd probably get other bids.

    One option is to change to a more modern electronic probe type LWCO and water feeder, way less expensive for the parts. The Cast Iron stuff is expensive.

    Whats wrong with the Pressuretrol location, is the Pressuretrol defective also ? If it is not defective and the cover is just missing I'd buy a cheap used one just for the cover. Touching other stuff on the other side of the boiler may just open up a can of worms, I'd avoid that.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 1902Shingle
    1902Shingle Member Posts: 30

    Yes indeed.

  • TheUpNorthState88
    TheUpNorthState88 Member Posts: 128
    edited 12:23AM

    Pricing discussions aren’t allowed here, but what I will say is for that price, it’s time for a new boiler. That’s exactly why they are protecting themselves with that statement at the end. I would not be dropping almost 7 grand on “fixing” a 60-70 year old boiler.

    It has served its time.

    Lifelong Michigander

    -Willie

  • mattmia2
    mattmia2 Member Posts: 18,044

    if the problem is that the lwco is sticking it can be rebuilt. it should be disassembled and cleaned every year or 2.

    what type of vents should be called out. those will have to be dealt with regardless of of the boiler is replaced.

    is the boiler being over fed because of issues with the lwco or because the water is leaving the boiler because of system issues.

    i wouldn't expect them to assume all liability for the system if they touch it but i would expect them to troubleshoot to determine if the issue is the lwco or an issue causing the water to exit the boiler during a heating cycle.

    if you're going to replace the pressuretrol you should replace it with a vaporstat.