#1 boiler killer you're NOT testing (Low pH will destroy your boiler fast)
In this weeks video I talk about pH in the boiler water, how to test, and why you should.
Boiler Lessons
Comments
-
I'm testing it, Ray, I'm testing it 😅
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Ive always heard that a TSP cleaning leaves the system on the alkaline side, which is preferred?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
the alkaline side is greatly preferred
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
@ethicalpaul Good job! LOL
I was consulting on a project where the water was high alkaline. They had the old sections in the parking lot and i was able to break them with my hands. Kinda made me feel like Superman
Ray Wohlfarth
Boiler Lessons0 -
how high do you think it was, and how did it get that high…over time it seems like it would tend back toward neutral unless they had a broken treatment adding system or something
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Ray, thanks for your expertise. I'm a home owner with a Weil McClain Gold boiler about 6 years old. Small house with only 6 radiators. Should I be adding something to the water to clean and balance the water? I tried using an F.W. Webb solution they recommended. I followed the instructions and pour the solution in to the boiler. Ran the boiler for the night but got concerned because of the banging. Very loud through this small system. Next day I emptied the water out completely and refilled with fresh, clean water. No banging. I tried testing the PH but I was doing it wrong now that I've seen your video. So if I take a sample the proper way and need to balance the PH, what solution do you suggest? Thanks again!
0 -
@ethicalpaul Not sure what causes the ph to fluctuate. Depends on blowdown, leaks, and treatment program
@robertelozeau Thanks you very much I appreciate it
@joeshrapnel I would look at the boiler manufacturers site for their recommendations on the cleaner or treatment. Each one is different depending on the metallurgy and components. Some cast iron boilers use elastomer seals between the sections and others push nipples
Ray Wohlfarth
Boiler Lessons0 -
How about low pH plus sacrificial materials? Some claim success with high pH plus anti-scales gizmos.
0 -
I'm not sure why you'd purposely have low pH in your boiler regardless of sacrificial material. All you need to do is add a little 8-way to get it up to 8-10, then rusting slows way way down
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
@ethicalpaul Low pH is supposed to prevent scale.
0 -
Rhomar has a good section on steam boiler water in their manuals
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hmm well it may but I’m not allowing acid in my boiler. The treatments typically have anti scale chemicals
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Thanks for having my back @hot_rod
The only guidance I would suggest is to follow the manufacturers recommendations to cover yourself.
Ray Wohlfarth
Boiler Lessons0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements