#1 boiler killer you're NOT testing (Low pH will destroy your boiler fast)
RayWohlfarth
RayWohlfarth Member Posts: 2,017
edited November 2025 in THE MAIN WALL
In this weeks video I talk about pH in the boiler water, how to test, and why you should.
Ray Wohlfarth
Boiler Lessons
ethicalpaulSiteReader
    ethicalpaul Member Posts: 8,922
    I'm testing it, Ray, I'm testing it 😅
    hot_rod Member Posts: 27,695
    Ive always heard that a TSP cleaning leaves the system on the alkaline side, which is preferred?
    the alkaline side is greatly preferred
  • RayWohlfarth
    @ethicalpaul Good job! LOL
    I was consulting on a project where the water was high alkaline. They had the old sections in the parking lot and i was able to break them with my hands. Kinda made me feel like Superman
    Ray Wohlfarth
    Boiler Lessons
    how high do you think it was, and how did it get that high…over time it seems like it would tend back toward neutral unless they had a broken treatment adding system or something
  • robertelozeau
    robertelozeau Member Posts: 1
    Excellent Video Ray, that is 100% true and accurate. I'm going to share this with our HVAC/R Technicians.
    Thank you.
    gianni
  • joeshrapnel
    joeshrapnel Member Posts: 9
    Ray, thanks for your expertise. I'm a home owner with a Weil McClain Gold boiler about 6 years old. Small house with only 6 radiators. Should I be adding something to the water to clean and balance the water? I tried using an F.W. Webb solution they recommended. I followed the instructions and pour the solution in to the boiler. Ran the boiler for the night but got concerned because of the banging. Very loud through this small system. Next day I emptied the water out completely and refilled with fresh, clean water. No banging. I tried testing the PH but I was doing it wrong now that I've seen your video. So if I take a sample the proper way and need to balance the PH, what solution do you suggest? Thanks again!
  • RayWohlfarth
    @ethicalpaul Not sure what causes the ph to fluctuate. Depends on blowdown, leaks, and treatment program
    @robertelozeau Thanks you very much I appreciate it
    @joeshrapnel I would look at the boiler manufacturers site for their recommendations on the cleaner or treatment. Each one is different depending on the metallurgy and components. Some cast iron boilers use elastomer seals between the sections and others push nipples
    Ray Wohlfarth
    Boiler Lessons
  • jumper
    jumper Member Posts: 2,574
    How about low pH plus sacrificial materials? Some claim success with high pH plus anti-scales gizmos.
    I'm not sure why you'd purposely have low pH in your boiler regardless of sacrificial material. All you need to do is add a little 8-way to get it up to 8-10, then rusting slows way way down
  • jumper
    @ethicalpaul Low pH is supposed to prevent scale.
    Rhomar has a good section on steam boiler water in their manuals
    IMG_1669.jpeg IMG_1670.jpeg IMG_1671.jpeg IMG_1672.jpeg IMG_1673.jpeg IMG_1674.jpeg
    hmm well it may but I’m not allowing acid in my boiler. The treatments typically have anti scale chemicals
  • RayWohlfarth
    Thanks for having my back @hot_rod
    The only guidance I would suggest is to follow the manufacturers recommendations to cover yourself.
    Ray Wohlfarth
    Boiler Lessons
  • jumper
    Not challenging you, Roy. Just saying there are many factors and approaches to water quality. If makeup water is adequately demineralized positive pH can be beneficial. If scale is an issue then negative pH might be considered.
  • RayWohlfarth
    @jumper I agree I just wanted something simple to test that will tell the owner if the water is acidic
    Ray Wohlfarth
    Boiler Lessons
