Welcome! Here are the website rules, as well as some tips for using this forum.

Need to contact us? Visit https://heatinghelp.com/contact-us/.

Click here to Find a Contractor in your area.

If our community has helped you, please consider making a contribution to support this website. Thanks!

Dope & tape?

Options
2

Comments

  • JMWHVAC
    JMWHVAC Posts: 134

    Too many leaks back when…. Both gives the best of both worlds.

  • ratio
    ratio Posts: 4,344

    If some is good, and more is better, then too much must be best.

  • In my world, tape and dope are the same. But some days, I feel like dope; others I feel like tape. And others, I feel like both.
    And on buggered up threads, I’ll dope the female side.
    There are even days that I fantasize about my work being judged. Those days I use dope as to me, it looks professional and until I drop my contractor’s license, I am a professional.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • HomerJSmith
    HomerJSmith Posts: 2,837

    I've givin' up on the yellow stuff for Megatape on just about everything. Megatape just feels good the way it goes on. Last week, I used Locktite on a Lochinvar indirect tank on the 1-1/2" stainless to copper in and out water supply. I learned my lesson. NO LEAKS. I did use Megatape and the blue dope on the heat exchanger to copper connections which cause me some concern on an earlier job. When everything got fired up, NO LEAKS. I did my happy dance.

    Alan (California Radiant) Forbes
  • JMWHVAC
    JMWHVAC Posts: 134

    Just had an irritating leak. The MIPT connections on an NTI boiler are machined so smooth, and it’s hard to put tape on up under boiler. When turning on the fitting, the tape sometimes turns up the threads with the fitting. If you miss it…drip, drip. So takes something like Nylog first, then tape, then dope.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Belt and suspenders when you don't want a leak….which is all the time but especially in walls or inaccessible locations. I have done jobs with dope only. Teflon tape makes fitting go on smoother IMHO.

    I don't know when Teflon Tape started but I started in 73' and it was in use then.

    I can remember a huge job at Amherst College when I started, and we went there for some reason while it was being built.

    There was an apprentice sitting in the corner with crates full of black nipples…tons of them. His job was to sit there all day and put Teflon tape on all the nipples…. think I would have quit if I was him.

  • GGross
    GGross Posts: 2,104

    when I started it was always the older guys that said you need to use both, the younger guys always said they only use one. so it kind of surprises me that it was more common to use one and not both back in the day. for what its worth I have seen both connection styles leak, and both not leak. for what its worth we never deal with any import fittings.

    I am gonna take a wild stab and quote a previous reply on this same thread though to answer the question correctly

  • Tape was available when I started in 1980, but it was thin. Easy to snap off when you’re done winding, but you had to wrap it 10 times to get enough material on the threads. I found a place back east that offered a thicker mil tape and ordered it by the case.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • jumper
    jumper Posts: 2,625

    I believe that improved dope came along in the eighties?

  • ChrisJ
    ChrisJ Posts: 17,763

    I have no idea what that is but it sounds like it's laced with something.

    What's improved dope?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    What did you do yesterday?

    We talked about pipe dope all night.

    Maybe we should talk about a Hartford Loop or a Drop Header or something.

    GGross
  • psb75
    psb75 Posts: 1,181

    How about…PONPC! That's good for a few pages itself. It has kept me up at night.

  • ChrisJ
    ChrisJ Posts: 17,763

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Alan (California Radiant) ForbesPC7060epmillerGGross
  • Intplm.
    Intplm. Posts: 3,162

    Maybe it was thirty years or so ago when we started importing goods from other countries that didn't have the same thread tolerances and standards we had for decades, this brought forth different thread characteristics that, in turn brought on the leaks that we now have developed this habit of both dope and tape. Before then one or the other was used and rarely both. We still do not trust the threads to be proper from the factory(s).

  • Viessmann's Lambda Pro combustion system anyone?

    It uses an ionization probe to monitor flue gases, allowing the boiler to auto-calibrate for gas type, quality, and altitude, ensuring high efficiency (up to 98%) and low emissions without manual adjustments.

    How come others don't use it?

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @Intplm. very true. I noticed may 25 years ago that the tolerances on threaded fittings were not as good as they used to be. At least it seemed that way to me.

    Once in a while i would do some HP steam that was spec for schedule 80 pipe and 250 or 300# fittings and the quality and tolerances seemed much better.

    Intplm.
  • GGross
    GGross Posts: 2,104
    edited April 15

    baxi does, calls it GA "gas adaptive"

    you will also see it as a spec option for some commercial units, common engineering term now is "O2 trim" I think the lochinvar name is "hellcat" (an option for Crest boilers), aerco offers "aertrim" for their Benchmark boilers. I'm not positive they all function on the exact same principles as lambda pro, which itself has gone through changes. (just looked up aerco, they are directly monitoring o2 with a sensor, so similar results but a much more expensive way to get there imo)

    the current lambda pro+ (plus!) also uses a mass flow air sensor in its calculations in addition to the ionization current.

    as to why most don't utilize this? cost primarily. but also they aren't nearly as in control of their supply chain as a company like Viessmann has been. seems silly but the more complicated your burner control, the tighter tolerances you need for components. That adds cost sure, but its also just really hard to do.

    I am very much a fan of lambda pro but I am also confident I could steel-man an argument against it if called upon

    Alan (California Radiant) Forbes
  • jumper
    jumper Posts: 2,625

    I think that I remember when neither was used? If connection dripped then there was epoxy; chewing gum; and other good stuff.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @JohnGoad

    There is no requirement to use yellow "gas Teflon tape" on gas or anything else. Regular Teflon is allowed.

    On fuel oil piping no Teflon tape is allowed which is a stupid requirement IMHO.

    I have always been happy with regular Teflon tape. I don't care for 'Blue Monster" and never tried the yellow tape.

    ChrisJIntplm.
  • ChrisJ
    ChrisJ Posts: 17,763

    I like blue monster on larger pipe but the typical thin stuff in small stuff like 1/4" and smaller.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Tom_133
    Tom_133 Posts: 990

    Dont tell that to my local gas monopoly… they will explain as you redo your work they are the local jurisdiction having authority, and you will obey!! They dont allow mega press yet!

    Tom
    Montpelier Vt
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @Tom-133

    I know what you mean. Years ago we had some high pressure 4" gas to pipe all outside on a roof. It was less than 5 psi so in MA. it was legal to thread it.

    We would have usually welded it but at that time our welder was out sick.

    The gas utility said we had to weld it.

    When I got the permit I complained to the inspector. He said "4" HP is legal threaded, if you thread it I will approve it" But if Columbia gas won't turn the gas on there is nothing I can do.

  • Lance
    Lance Posts: 344

    TO teach is one thing to learn is another, to practice perfectly requires perfect practice. All connections require education to do it right. The hardest teacher is experience but it is the truest. But experience can be wrong. Just because it looks simple, or won't leak right away doesn't mean it won't fail. The tragedy of many failures prove that.

    Anything ,wiring, welding, carpentry, piping all fail because it is done poorly. And the ways are many. Pipes are not all the same, threads, torque, materials, even what the pipe is used for makes a difference. water v chemicals, pressure, temperature, low or high. Torque applied. All thread dopes are not equal, but all dopes who use them are. The correct choice is just that choosing all the right things required to make it leak free.

    Too loose, too tight. The variables in any pipe joint require not just the skill in application, but the knowledge of what is approved and proven works. If it is wrong in any way, it can leak. It's a skilled job because it requires skill. Pipe compounds have restrictions and permissions in can degrade over time. Ambient temperature changes between build and use can make it leak. Even if all that is correct, you still have material defects, and then the skill of the person, who even if they know what to use, may not know the how.

    It is why training in the trades is a lifelong school of instruction as things always change! and who knows, Even manufactures, teachers can be wrong. Imagine if the advice you learned was wrong, incomplete, or it will not work in all situations. The classic sign of a novice is they have yet much to learn. And we can learn a lot from heating help.com

    Alan (California Radiant) ForbesLarry WeingartenIntplm.
  • 8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    Intplm.
  • jumper
    jumper Posts: 2,625

    I wonder how connections are tested. In the seventies the first plastic pipe was approved for DHW. I could make nylon compression ring connections fail quite quickly with fast shut-off.

  • HomerJSmith
    HomerJSmith Posts: 2,837
    edited April 20

    I always tighten pipe till the fitting cracks, then I give it one more turn. Works for me.

    ratioAlan (California Radiant) Forbes
  • ratio
    ratio Posts: 4,344

    @HomerJSmith, that one gas fitting you did, I fixed it for you. 😉

    HomerJSmith
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I was installing a boiler myself, asked for help but didn't get any. I got the boiler set up and I did a 4" threaded steam header and 3" threaded condensate return.

    I got the 4" header done and was quite happy with it as everything fit perfectly.

    They sent a sheet metal guy over from our company to do the flue and fix the fresh air intake. I had just started on the condensate, and he finished the flue, so he was helping me. Really good guy and strong as an ox.

    I was measuring and cutting and threading with a Ridged 141 and he was putting the stuff together and I was keeping an eye on him. He was telling me about his buddy that worked for another union pipe shop and how they would do side jobs together so he 'knew about piping"

    Nothing on the condensate was fitting, everything was coming up short and I knew my measurements were good.

    He was cranking the fittings on so tight.

    When I mentioned it he said "my buddy told me to crank them in until no threads were showing"

    Alan (California Radiant) Forbes
  • Intplm.
    Intplm. Posts: 3,162

    When I first started using the blue monster tape, I was tightening fittings as I always would with the white stuff. After cracking a few fittings and valves using the blue, I read the directions on the label that was still intact. Three raps from now on and no cracked fittings. I never needed written directions for tape until then. I was treating the blue as if it were the white stuff. Go figure.

  • pecmsg
    pecmsg Posts: 7,634

    When I mentioned it, he said "my buddy told me to crank them in until no threads were showing"

    I was told tighten with only 2 threads showing!

  • ChrisJ
    ChrisJ Posts: 17,763

    I can't imagine either way working, there's too many variables.

    You need to feel the connection and what it's doing.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Intplm.EBEBRATT-EdAlan (California Radiant) Forbes
  • pecmsg
    pecmsg Posts: 7,634

    45 - 50 years ago the quality was much better. American made pipe and fittings.

    Today that standard is gone.

    Intplm.
  • ChrisJ
    ChrisJ Posts: 17,763
    edited April 21

    I mostly agree, but I've also seen a lot of guys threading pipe with a machine and stopping at random points making the threads either too shallow or too deep.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • jumper
    jumper Posts: 2,625

    These last posts reinforce my suggestion to use straight threads with sealant. One feature is that lengths can be adjusted. Another is that unions are not necessary.

  • ChrisJ
    ChrisJ Posts: 17,763
    edited April 21

    How exactly do straight threads make unions uncessary?

    I greatly prefer tapered threads that really, if done correctly do not rely on gaskets or sealant. The straight threads I've used like BSPP still need to be fully tight, you can't just load the threads up and stop wherever you want.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • jumper
    jumper Posts: 2,625

    Parallel pipe threads, both male and female. Preferably a sealant that doesn't get too hard. The notion that a bad tapered thread connection can be fixed by strenuous tightening is problematic.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @ChrisJ

    Your right. How tight it feels is important.

    I used to dislike guys who made the fittings on with the pipe machine for that reason. I only did that if I was in a real hurry and when working on something where it was unlikely to cause an issue like an oil tank vent line or a condensate tank vent or overflow etc.

    When I was threading with dies, I was unfamiliar with the first thing I would do is take a piece of pipe and make a mark 6" from the end then thread it dope it and put a fitting on it and measure how far it made in and go from there. In a tight spot 1/8-1/4" is a big deal. Out in the open its not.

    ChrisJ
  • HomerJSmith
    HomerJSmith Posts: 2,837
    edited April 24

    @ratio Thanks much. In 40 years, I've never had a complaint.

    I tell all my customers after I finish a job, that all complaints are handled by our office in Budapest. .