Moline Steam System - Update
Ironman
Member Posts: 7,550
Anyone know if Moline radiator supply valves can still be obtained or any alternatives?
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.
You can choose to do what you want, but you cannot choose the consequences.
0
Comments
-
Why does it have to be Moline?0
-
-
You could replace it with a regular steam valve and an orifice plate if you can't clean up the old valve.0
-
Tunstall will make anything if you can get them a sample. Send pics please..Mad Dog 🐕0
-
For a regular Right Angle shutoff, I think Hoffman is the Highest Qaulity. Mad Dog 🐕0
-
Some more Moline info and pics:
https://forum.heatinghelp.com/discussion/182196/found-a-moline-heat-system-near-baltimoreAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
A little info about the job:
The house was built in the 1890’s and has been owned by the late Mary Kay (cosmetic fame) and presently by her daughter since the 1950’s. I’m not sure if the system is original.
I got my first look at it yesterday and it’s been knuckleheaded over the years. Some of the Moline valves have been replaced standard ones, traps and air vents installed, etc.
I’ll post more info after I evaluate it more thoroughly in a couple of weeks.
Any helpful advice is greatly appreciated.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
@Ironman , if all the rads look like the one in the second pic, it's not original. That type of rad came out about 1925. Before that they would have used column-type rads like the American Peerless or Rococo.
If the house originally had one-pipe steam, it's possible the Moline was retrofitted.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
-
Steamhead said:@Ironman , if all the rads look like the one in the second pic, it's not original. That type of rad came out about 1925. Before that they would have used column-type rads like the American Peerless or Rococo. If the house originally had one-pipe steam, it's possible the Moline was retrofitted.
The more original ones are column.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Here are some more pics of the system and boiler. It’s been knuckleheaded.Someone removed the Moline vent and put a trap in its place.
Obviously, the near boiler piping is wrong.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
@Steamhead, @TheSteamWhisperer, @Dan
And any others familiar with a Moline system.
How would you suggest correcting this?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Is that a plug where the relief valve once was?0
-
@Ironman , it looks like that thermodynamic trap is piped from the end of the long condensing pipe and down into the return. If true, there is no air vent anymore, and I'll bet the system doesn't heat well if at all.
The trap is not needed. Remove the concentric reduction at the flange union. Put a tee whose run is the same size as the condensing pipe after the flange union and install two Gorton #2 vents in the bull. Then pipe over to a reducing 90 pointing down and connect the drip line.
Replace the Pressuretrol with a Vaporstat set to no more than 8 ounces.
Then try it out and see if everything heats quickly, evenly and quietly. If not, go after whatever problems you find at that point.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting4 -
Steamhead said:@Ironman , it looks like that thermodynamic trap is piped from the end of the long condensing pipe and down into the return. If true, there is no air vent anymore, and I'll bet the system doesn't heat well if at all. The trap is not needed. Remove the concentric reduction at the flange union. Put a tee whose run is the same size as the condensing pipe after the flange union and install two Gorton #2 vents in the bull. Then pipe over to a reducing 90 pointing down and connect the drip line. Replace the Pressuretrol with a Vaporstat set to no more than 8 ounces. Then try it out and see if everything heats quickly, evenly and quietly. If not, go after whatever problems you find at that point.@Steamhead
Thank you. That was what I was thinking too, but I’m glad to hear it from you.
Obviously, the near boiler piping needs to be re-done and that’s gonna be the biggest expense.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I guess that some folks don’t understand that a trap will let air pass through, but it won’t remove it.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The near boiler piping isn't right and should be fixed if you have to cut in to it, but because that is an older boiler with some sort of a steam chest it might work ok like that, i would make sure steam isn't blowing right through the radiators in to the returns before I would start repiping the boiler.0
-
You can't fix stupid!Ironman said:I guess that some folks don’t understand that a trap will let air pass through, but it won’t remove it.
Let us know how you make out.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
mattmia2 said:The near boiler piping isn't right and should be fixed if you have to cut in to it, but because that is an older boiler with some sort of a steam chest it might work ok like that, i would make sure steam isn't blowing right through the radiators in to the returns before I would start repiping the boiler.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Two photos in this thread from 2014. I wonder if an old supply house in the quad cities might have some dusty valves in a back room? Might be worth a phone call.
https://forum.heatinghelp.com/discussion/151231/moline-system-in-moline-illinois
0 -
-
Update on this job:
We repiped the near boiler with a 4” drop header and Hartford loop, removed the trap and installed two Gorton #2’s as Frank suggested and replaced some rotted/clogged wet return pipes.
The steam piping will be cleaned up and insulated next week along with a vaporstat being installed.There was a major water leak on some return piping inside of a wall and this is what I found when I opened the wall:Apparently, someone thought that it was necessary to install drains on these return line so that the house could be winterized?
By putting the valves down at the bottom, the pipes filled with water and froze when the system was running. Don’t you love the Sharkbites?
I don’t know why someone would do this and I explained to the owner that the lines automatically drain toward the boiler.
The system is up and running and all radiators work except for one which may have a clogged return. It takes about 10 minutes for the vents to remove the air once the boiler is steaming.
The boiler block is a V905 with a V904 burner package. It’s sooted and needs some attention because it’s vented directly into a masonry chimney that needs to be lined.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.5 -
I bet the owner remembers having to get that wall repaired last time, does she remember any other wall repairs done at the same time? Don't want another surprise hiding..
Excellent workOne way to get familiar something you know nothing about is to ask a really smart person a really stupid question0 -
Ah... what is the small diameter soft copper pipe I see? Any chance this is old enough for gas???Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:Ah... what is the small diameter soft copper pipe I see? Any chance this is old enough for gas???Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Well, that's a new one on me. You never see it all............Ironman said:Update on this job:
We repiped the near boiler with a 4” drop header and Hartford loop, removed the trap and installed two Gorton #2’s as Frank suggested and replaced some rotted/clogged wet return pipes.
The steam piping will be cleaned up and insulated next week along with a vaporstat being installed.There was a major water leak on some return piping inside of a wall and this is what I found when I opened the wall:Apparently, someone thought that it was necessary to install drains on these return line so that the house could be winterized?
By putting the valves down at the bottom, the pipes filled with water and froze when the system was running. Don’t you love the Sharkbites?
I don’t know why someone would do this and I explained to the owner that the lines automatically drain toward the boiler.
The system is up and running and all radiators work except for one which may have a clogged return. It takes about 10 minutes for the vents to remove the air once the boiler is steaming.
The boiler block is a V905 with a V904 burner package. It’s sooted and needs some attention because it’s vented directly into a masonry chimney that needs to be lined.
(snip)
No, those were connected to the return lines to drain them.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
Steamhead said:
Update on this job:
Well, that's a new one on me. You never see it all............
We repiped the near boiler with a 4” drop header and Hartford loop, removed the trap and installed two Gorton #2’s as Frank suggested and replaced some rotted/clogged wet return pipes.
The steam piping will be cleaned up and insulated next week along with a vaporstat being installed.There was a major water leak on some return piping inside of a wall and this is what I found when I opened the wall:Apparently, someone thought that it was necessary to install drains on these return line so that the house could be winterized?(snip) No, those were connected to the return lines to drain them.
By putting the valves down at the bottom, the pipes filled with water and froze when the system was running. Don’t you love the Sharkbites?
I don’t know why someone would do this and I explained to the owner that the lines automatically drain toward the boiler.
The system is up and running and all radiators work except for one which may have a clogged return. It takes about 10 minutes for the vents to remove the air once the boiler is steaming.
The boiler block is a V905 with a V904 burner package. It’s sooted and needs some attention because it’s vented directly into a masonry chimney that needs to be lined.It was certainly a new one for me also.
The lower return was just slightly back graded, but not enough to hold any appreciable amount of water. It seems to be returning water towards the boiler just fine.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
https://us.v-cdn.net/5021738/uploads/editor/na/033fjrht5sek.jpegShark fittings in the wall?Not allowed!1
-
-
EBEBRATT-Ed said:Looks great!! Only thing I see is the make-up water from the feeder shouldn't go directly into the boiler. It should go into a return or the lower Hartford loop to mix with the return before it goes in the boiler.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
pecmsg said:https://us.v-cdn.net/5021738/uploads/editor/na/033fjrht5sek.jpegShark fittings in the wall?Not allowed!
Manual drains on dry returns? Why?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
This is in Bath County, Va (google the Homestead) where there are folks who have some very expensive second or third homes, but we have to deal with some cheap slipshod contractors.This boiler replacement by “Hatchet Jack” is all too typical:Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements