Filter drier
I saw a lot time a filter drier on suction line of carrier unit why? This should be removed after two week only for replace compressor when it’s burn out right ? This won’t cause restriction? It sitting every year every time I go back do the ac maintenance
  • pedmec
    pedmec Posts: 1,484
    Because unless you are have a pressure drop thru the filter-drier you are ok. that type of filter drier is not a removal drier core style so opening up the system to remove is something you want to avoid. which would mean adding another filter drier on the liquid side after removing.
    if you are worried about acid still being in the system you can test the system for acids. might give you piece of mind.
    Ironman
    pecmsg Posts: 7,486
    edited June 2022
    Scott to the book
    a suction filter is installed after a compressor burnout to aid in acid clean up. Check acid level after 24 - 48 hours of operation. If clean remove filter. If still acidic remove and replace. Repeat as needed.
    I add the time to remove to the compressor change.
    EBEBRATT-Ed Posts: 20,937
    If a suction drier was put in the system to remove acid, then the acid is still in the system........it's just trapped in the dryer. The acid could be released back into the system if the dryer breaks down. It should be removed
  • ratio
    ratio Posts: 4,304
    It probably should be removed, but if you're there for a PM, I wouldn't touch it without explicit instructions from the office. A PM isn't the time to be making significant changes like that. A note on the work order mentioning it & a recommendation that it be removed might be appropriate.
    pecmsg