Natural gas boiler sidewall vent issue

Now the issue that I am having is that the exhaust coming from the flue is making me feel sick to my stomach. The exhaust flue is situated under our living room window and near our kitchen window, within the "required" distance of about 5' away from any window.
Which is ridiculous to me because when the exhaust clouds come out it can blow back into our home from any window opened thats nearby, backdrafting.
I cant be anywhere around that exhaust pipe, in the backyard or even open my bedroom windows which is on the second floor adjacent to this exhaust pipe.
I've called the company and they told me that the exhaust pipe is within the required length away from any window. And that a kit was available, but it would only be a maximum of 6' up. But again the issue of the exhaust coming back through our windows is an issue. Ive consulted with different contractors who came by my home and said the most they can do was run the exhaust pipe to the other side of the house from the basement where our system is installed. That would still create the same issue.
I have asked them if there was a way to run the exhaust pipe all the way up through the roof, but our home does not have a full chimney still intact. I have throught about running the flue pipe from the side of the house, even with an external chimney made, but there is the risk of the elements freezing the steam that rises and can create many issues.
The only way I am able to be in the backyard is if I turn the boiler emergency shut off switch, but I feel if I repeatedly do this it might impact the system in some way.
This has been a challenging time for my family and I. They have also been having some ongoing allergic reactions, sore throat, coughing, sinus and sneezing.
It seems sidewall venting of natural gas boilers is common in my town. Not all houses have them, but some do. I was under the impression that once the exhaust makes contact with the outside air, it is no longer harmful.
I just dont know what to do anymore. We have a beautiful home and this ongoing issue. Ive also thought about replacing the whole system with something that does not vent through the house or another way of working. Any thoughts, suggestions and opinions welcome. Thank you.
Comments
-
-
Sidewall venting is common, and for many people it is not a problem. For some it is. While the diluted exhaust may not be harmful -- in the sense that it won't kill you -- it can certainly be a nuisance.
That said, the first thing to do is to make sure that the boiler really is burning cleanly. It should be checked for proper combustion settings by someone who has the correct combustion testing equipment -- and knows how to use it. It is possible that it is sufficiently far out of adjustment as to cause problems.
Other than that, the best solution is going to be to extend the exhaust vertically through the roof up the side of the house. This really shouldn't be that difficult, and would solve the problem.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England3 -
JUGHNE said:How much of your original chimney is still intact? Is this a 2 story house? The chimney could have been used for a chase for the PVC piping and go thru the roof.
I would have hoped it was as simple as that, Ive talked to two plumbers and a boiler/heating contractor and they could not really give me another solution other than the ones I mentioned. I did speak to an hvac contractor who advised me that it would be an expensive job, I tried to get an estimate from him, but it seemed like he was after a bigger job and never called me back.
I am not sure what other type of contractor I could speak to. I don't even know who installed the system in my home.0 -
Jamie Hall said:Sidewall venting is common, and for many people it is not a problem. For some it is. While the diluted exhaust may not be harmful -- in the sense that it won't kill you -- it can certainly be a nuisance. That said, the first thing to do is to make sure that the boiler really is burning cleanly. It should be checked for proper combustion settings by someone who has the correct combustion testing equipment -- and knows how to use it. It is possible that it is sufficiently far out of adjustment as to cause problems. Other than that, the best solution is going to be to extend the exhaust vertically through the roof up the side of the house. This really shouldn't be that difficult, and would solve the problem.
My concern is not that it will kill me right away, but the potential long term health effects it may have on my family or me.
Thank you for the suggestion of having someone skilled in checking to see if the boiler is in the correct adjustments with the proper equipment and burning clean. I havent thought of that and will have it done soon.
I would run the exhaust system through the side of the house onto the roof, but since we get really cold winters here one of the contractors said that because its condensed steam coming outside the exhaust that when it rises on the outside it would cool down and the water would freeze potentially freezing the line to the point of expanding and damaging it, as well as potentially damaging the boiler system itself.
0 -
@StoicsDream
Why not post a few pictures of the boiler the flue pipe and where it vents outside.
If the chimney is still standing which it is (no parts of the chimney have been removed it they did it would fall down)
You may be able to vent that way through the roof.
Also post your location and check "find a contractor on this site"
also post the boiler model #2 -
Once in a long time we here of a situation where the exhaust through the roof has had ice problems. I think there was one here four or five years ago. However, if the pipe run is inside the envelope -- very very unlikely. If it's outside the envelope, you can create a very nice face "chimney" on the face of the house with a box and the exhaust running up inside it. There are thousands of them! Your guy who's afraid of freezing is not correct.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
@EBEBRATT-Ed, the model series is phntm180hnt1suc and here is a pic where the intake and exhaust flue is right under the living room window, not to far off is our kitchen window.0
-
@Jamie Hall I thought so too. What type contractor/s would I speak to? Chimney, plumber, hvac? Ive spoken to one of each individually and keep hitting a dead end. Maybe there is a type that will do all, but Im not sure if there is a specific contractor that will specialize in something like this.
0 -
In cold climates, you can extend the pipe on the outside of the house and up through the roof, but it has to be in an insulated chase to stop the freezing problems you were referring to.
And yes, it does look like it is installed per manufacturer, and it could be burning badly and causing bad fumes, but most likely you are just more sensitive to it than most. I am mostly an oil burner guy, but I am getting to the point where I can't stand the smell of diesel burning. And then I just bought a diesel pickup, so that is also a problem.
Rick1 -
I would vent the boiler outlet up through the chimney. I looked for the boiler model you posted on Velocity Boile and couldn't find the exact model. They have several Phantom models.
But the venting instructions look like you can vent the outlet up the chimney with the air intake can be left as is in the building side wall.
Your installer needs to read and understand the venting instructions and follow them.
1 -
I might be losing my mind here, but that termination does not meet the manufacturers specification based on what I'm reading. It clearly states and shows it must be 12" away from any window. The 12" is measure horizontally (shown in diagram), that termination is directly under a window, which is obviously not 12" away. It is also required to be 4' away from the gas meter so it would either have to move significantly to the right or left from it's current position.
That location defies logic, I don't need a manual to tell me that.
All that said, did the contractor perform a full combustion analysis and tune on the burner to make sure it's running properly?
Do you have a gas stove in the house? If that doesn't bother you, then this shouldn't either, unless it's not running properly.3 -
Well, the termination for the exhaust is on the right, which does look like 12" away. Also, it depends on if the window can be opened, which this one might be fixed, but I think I see a screen in it, so maybe not.
The gas company would dictate if the exhaust is far enough away before they set the meter, so it either meets there specs, or someone messed up.
As a side note: That ugly rusty pipe is the reason I went to using galvanized pipe. Nothing looks worse on the Homer spit than black pipe that has been hammered with salt water under the boardwalks. 1/2" pipe gets really big.
Rick
1 -
rick in Alaska said:
Well, the termination for the exhaust is on the right, which does look like 12" away. Also, it depends on if the window can be opened, which this one might be fixed, but I think I see a screen in it, so maybe not.
The gas company would dictate if the exhaust is far enough away before they set the meter, so it either meets there specs, or someone messed up.
As a side note: That ugly rusty pipe is the reason I went to using galvanized pipe. Nothing looks worse on the Homer spit than black pipe that has been hammered with salt water under the boardwalks. 1/2" pipe gets really big.
Rick
Doesn't look like it meets requirements to me.
I interpret this is meaning it cannot be under a window, period. It must be 12" or more to the side of it horizontally as @KC_Jones said.
But I also agree, if that's burning even remotely right it shouldn't really be bothering anyone either. I'd want it checked out regardless of moving the exhaust.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
2 -
-
ChrisJ said:
............But I also agree, if that's burning even remotely right it shouldn't really be bothering anyone either. I'd want it checked out regardless of moving the exhaust.
THIS!HomerJSmith said:Do a combustion analysis if it hasn't been done with a recently calibrated combustion meter.
@StoicsDream , where are you located? You need this looked at NOW. Don't use this unit until it successfully passes a combustion test.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
Those CO numbers are way too high. I doubt anyone on this board would tolerate them. @Tim McElwain ? @captainco ?pedmec said:not true regarding "if it burns right it shouldn't bother you". a perfectly tune boiler still produces co. even asme boiler code allows up to 400 ppm of undiluted co as acceptable in the flue gas although most manufactures will try and keep it under 200.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting3 -
-
I agree with @EBEBRATT-Ed that if the chimney is in the basement and is also in the attic it is probably all there. Removing the chimney in the living space and adding supporting structure to the house framing to hold up the attic portion makes no sense. Builders are good at hiding chimneys behind closets and built in cabinets or just the way the walls are designed. If there is an easily removable cover where the former boiler exhaust vented to the chimney in the basement you could use a mirror to see if you can see daylight at the top of the chimney (assuming it was not capped off). You may feel a draft also.
If the combustion analysis is OK and the chimney is usable I would use the chimney.
If you have to extend the exhaust venting on the side of the house you may want to consider the prevailing wind and go towards down wind. Also why is the exhaust drafting into the house? Is the boiler air intake partially plugged or not connected to the boiler in the house? So the boiler is drawing combustion air from inside the house.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
-
i stand corrected. its an ansi standard. its maximum in flue.
Table 1: CO Thresholds for Fossil Fuel-Fired Combustion Appliances
4
See Carbon Monoxide Air Free in Annex B |Terms and Definitions for further details.
Table 1
CO Thresholds for Fossil-Fuel Fired Combustion Appliances
Appliance Threshold Limit
Central Furnace (all categories) 400 ppm air free4
Boiler 400 ppm air free
Floor Furnace 400 ppm air free
Gravity Furnace 400 ppm air free
Wall Furnace (BIV) 200 ppm air free
Wall Furnace (Direct Vent) 400 ppm air free
Vented Room Heater 200 ppm air free
Unvented Room Heater 200 ppm air free
Water Heater 200 ppm air free
Oven/Broiler 225 ppm as measured
Clothes Dryer 400 ppm air free
Refrigerator 25 ppm as measured
Gas Log (gas fireplace) 25 ppm as measured in vent
Gas Log (installed in wood burning fireplace) 400 ppm air free in firebox1 -
-
ill have to look it up but i believe the burnham alpine at high fire is in the 165ppm range. id have to verify but that's how i remember it (but maybe i'm just getting old, lol).
if your not getting co then your just running a little lean. just losing a little efficiency but safer.
0 -
nope not the alpine0
-
everybody's favorite boiler, the munchkin is 70-135 ppm at high fire0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements