HEAT HELP!!!!
inwannunu
Member Posts: 1
in Gas Heating
I think the last guy completed ruined our heating system. Check out the pics. He snatched out the transformer. Now thermostats are not connected. The heat seems to come on when it wants. It's too hot in the house when the temp outside is about 40 degrees but not enough heat kicks in when it's freezing outside!!! Someone help!
-1
Comments
-
Nobody is going to be able to help you without more information. You didn't provide pictures of the heating system, but #2 looks like there is some sort of boiler system there. Is that correct? Could you provide more photos of it and the wiring connected to it? Something must tell the system to run. If it runs intermittently, there must be some sort of signal telling it to do that.2
-
GroundUp said:Nobody is going to be able to help you without more information. You didn't provide pictures of the heating system, but #2 looks like there is some sort of boiler system there. Is that correct? Could you provide more photos of it and the wiring connected to it? Something must tell the system to run. If it runs intermittently, there must be some sort of signal telling it to do that.
But yes lots more information and photos are needed.
And if that is how that "professional" left that j box... Find a new one.1 -
Even with good pics, it would be almost impossible to try and explain over the internet what exactly needs to be done. Obviously, there are thermostats missing as well as the transformer, but someone knowledgeable needs to be on site to know the details of how to correct it.
Where are you located?
Have you tried the contractor locator above?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Whatever else, I looked at that first picture of the junction box.
Do NOT let that contractor -- if he is one -- back in the house. I would consider reporting the situation to your local building code enforcement people. Whoever left the house that way should have his license revoked -- if he even has one.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
If I had to guess, I'd say that several zone stats were removed & replaced with one main stat that opens all the zone valves. <https://heatinghelp.com/find-a-contractor/ >might help you find someone to figure out exactly what's going on.0
-
That looks like there are both Line Voltage and Low Voltage circuits in the junction box. That would be ok if all the conductors (wires) were at least 16 Gauge wire, but some of those wires look like 18 gauge or smaller. That would not pass a code inspection by a competent electrical inspector. (the key word is competent)
Im thinking you should get a competent professional HVAC tech, Plumber, or Electrician (Competent = One who understands control wiring ...not just house wiring) to resolve your issue.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
looks like looks there is some Romex wire on the one sub base?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
You can’t have high voltage and low voltage in the same box unless the wires are rated the same.0
-
EdTheHeaterMan said:That looks like there are both Line Voltage and Low Voltage circuits in the junction box. That would be ok if all the conductors (wires) were at least 16 Gauge wire, but some of those wires look like 18 gauge or smaller. That would not pass a code inspection by a competent electrical inspector. (the key word is competent) Im thinking you should get a competent professional HVAC tech, Plumber, or Electrician (Competent = One who understands control wiring ...not just house wiring) to resolve your issue.
Edit: actually it makes sense there would be low and line voltage near by. I bet that's where the transformer was, still shouldn't have been in the same box. And yea I'd report that fool. He left a serious shock and fire hazard in your house. If the wrong wire from that made contact with that copper pipe inches below it you could energize half your house... For the split second it takes to short out, possibly arc out. Look on YouTube for what a good arc flash can do to a person. It is why the maintenance techs at my employer have flame resistant uniforms and are the only ones allowed in machine electrical panels. I actually just had to refresh my LOTO training the other day.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements