No heat
tomboretos
Member Posts: 5
I have a HTP EFTC-140W. It has the outdoor temp sensor icon flashing. There is no outdoor temp sensor. I can't figure it out. Please help
0
Comments
-
Is this a new installation or a sudden problem with an existing system?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Existing system0
-
Sorry was busy0
-
Per the IO&M for EFT, the "house" symbol flashes if neither the 0-10V or ODR sensors is connected. It is a status only event, not an error unless you previously had a ODR or 0-10V input connected. Without a ODR, the unit will run max SWT per the configuration settings when "TT" line are closed.
Is the thermostat calling for heat?
Is circulator pump running (look for solid pump symbol on status panel)?
When did the unit stopped working? What other symptom do you see?
@Ironman has worked with these units but hard to say with current information.1 -
You can access the IO&M here: https://htproducts.com/literature/lp-520.pdf
0 -
I have noritz CB 199. I think I have a similar user interface for control. You need to go in setting and set up whether you wanted ODR in your system or not. Some system is not by default, in that case, it will keep flashing. if you activate the ODR in your setting it will stay solid in the panel.
Read Page # 50 in the manual (Above link posted by @PC7060 )Thank you,
Hiren Patel1 -
The thermostat is calling for heat and the pump is running. Its been this way since the gas company turned it back on after redoing the gas lines outside. Everything else seems to be fine0
-
-
-
What other icons does it have? a good picture of the panel will help. is it turned on with the button next to the display? not sure if the odr icon flashes with it off or not.0
-
Second @Ironman recommendation; look at page 2 of the IO&M for gas shutoff valve instructions.The error codes are on page 56. The instructions to get into installer mode to check out error codes starts at the bottom of page 52.Page 58 has the ignition flow; no gas will result in E11 failure.Don’t ask me how I know this error code so we’ll.0
-
Since it is a mod con, it needs to have the circulator running whenever it is firing to keep flow through the hx.0
-
If its like my Noritz POS I have in my house, once every 3-6 months it just loses its mind and blows out all the configuration settings in the controls. Don’t ask me why. At least I got it for free second hand (tore it out after the customer was fed up with it for same issues and poor application).0
-
This might be on the simplistic side, try disconnecting the outdoor sensor and see what happens.Might need to cycle the power after you disconnect.0
-
It produces hot water just no heat0
-
-
@tomboretos - what @mattmia2 (and I) said, go into installer mode and look to see what error codes are listed.You will have to some leg work since none of us can see your boiler from our offices or homes. A bit more information in your posts would help too.Read the IO&M manual I previously posted link to.Look at page 2 of the IO&M for gas shutoff valve instructions.The error codes are on page 56. The instructions to get into installer mode to check out error codes starts at the bottom of page 52.Page 58 has the ignition flow; no gas will result in E11 failure.0
-
Sounds like a problem with the three-way valve. I have installed two HTP EFTC-140W s. Replaced the three-way valve three times, most recently last week. Hot water would work, no error codes, but will not switch to heat. Internal pump would run on heat call. Known problem with this model. Three way valve part #: 7855P-247. Part does NOT come with needed gaskets and o-rings. Get two(2) EFTC-140 spare parts kits. Need to remove internal pump and CH Return block to change this. Pg 69 of install manual1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements