Old basic gravity hot water boiler

Options
Sanddy0908
Sanddy0908 Member Posts: 14
Can a convert an old gravity hot water boiler into a steam system leaving old piping to radiator in place?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,326
    Options
    Very unlikely. Nothing's impossible, but... why not convert to a pumped circulation hot water system?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2Ironman
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,215
    Options
    I would say very likely, but you need to hire someone that knows steam to check it out and do it.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • pecmsg
    pecmsg Member Posts: 4,861
    Options
    Can a convert an old gravity hot water boiler into a steam system leaving old piping to radiator in place?
    Highly doubtful. Different dynamics steam / water
  • Sanddy0908
    Sanddy0908 Member Posts: 14
    Options
    I understand, besides of the system not having a steam trap, doe sit nees to have a pipe in the high side or it can do it with a low piped
  • Gilmorrie
    Gilmorrie Member Posts: 185
    Options
    Why are you wanting to do that?
    mattmia2
  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    Can you post pictures of the boiler showing the piping around it, floor to ceiling?
  • Sanddy0908
    Sanddy0908 Member Posts: 14
    Options
    The issue i have is that i am an idiot, i went to see the job and just look fast at the basement and been an idiot went ahead and thought the system was steam and order and installed an steam boiler. I found out when i saw how the radiator were vented and the steam boiler was going of on 5 psi of pressure.Technically no vents for a steam system. I order to main air vents for the two returns. I installed them and got rid off the expansion tank in the attic. It seems to be working every radiator is getting hot. But would it keep workingbor would it just fill up with water with time? 
  • Sanddy0908
    Sanddy0908 Member Posts: 14
    Options

  • Ironman
    Ironman Member Posts: 7,376
    Options
     :o 
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2SuperTech
  • Steamhead
    Steamhead Member Posts: 16,844
    Options
    What you want to do is change the boiler to work with hot-water, and change the piping appropriately.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Ironmanmattmia2
  • Sanddy0908
    Sanddy0908 Member Posts: 14
    Options

  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    Like @Steamhead said, change the boiler trim to hot ware and add a small circulator. I think you might want to find a contractor that knows hot water well to help you that can help you learn since you will have to do a few minor things to convert from the gravity system with an open expansion tank to a system with a circulator and modern expansion tank and air removal. None of it is difficult or particularly expensive but you will have to have a good knowledge of hot water to make it work well.
  • Sanddy0908
    Sanddy0908 Member Posts: 14
    Options
    @mattmia2 you mean to change a setting in the steam boiler to set it to work as a hot water boiler? Please explain and sorry for my dumbness i would like to learn more
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    It is more than settings. You remove the site glass, add a combination aquastat of some sort, change the relief valve, add an expansion tank and prv and air elimination, add a circulator, change some piping, add a tridicator, plug some unused tapings. Most boilers can be set up for steam or how water but they use different controls and accessories for each application. The manual may have a diagram although many don't put the air elimination, expansion tank, and circulator in the best location.
  • Sanddy0908
    Sanddy0908 Member Posts: 14
    Options
    @mattmia2 thanks so much for the advice will follow i appreciate the information thanks
  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,215
    Options
    Yes, to make the system work as steam you'd need to change at least some of the near boiler piping to add drip lines to the supplies since they drain back toward the boiler (typically), add orifices to the radiator supply valves to control the steam distribution and provide air venting on the return mains. May some main vents at the end of the mains might be needed to get the steam out to the end of the mains quickly.

    The other alternative is to set up the boiler for hot water and repipe it and add all the necessary additional equipment for a hot water system....pressure reducing valve, hot water pressure relief valve, aquastat and circulator relay, circulator, air seperation equipment, isolation valve to service the boiler, and a compression tank or two depending on water volume of the system.

    After all that, it may just be easier to complete the conversion to steam.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,545
    Options
    :*
  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    When this heats, where is the water line in the sight glass?

    Could the system be completely full of water and working by gravity?

    Depending upon the height of the house, if it were completely full, water pressure would open the pressure switch.

    What did the attic expansion tank do when first turned on?
    Where is the overflow pipe directed to?
  • Sanddy0908
    Sanddy0908 Member Posts: 14
    Options
    @JUGHNE, ghe water goes a bit low when it is operating, it does not go full pressure doesn't go up anymore after i added the main vents in the two main return lines, and i removed the expension tank and cap the pipe that was going to it.
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    WMno57 said:
    This is why I DIY.
    You and me both my friend.  You and me both.....
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    mattmia2KC_JonesJakeCKPC7060
  • Sanddy0908
    Sanddy0908 Member Posts: 14
    Options
    @KC_Jones yea i mess up big. I did measure the radiators and came up with the calculations for the sq footage of steam needed, where i mess up the most it was that it is my first time seem a gravity hot water system. I guess there is always a first time. Everything is slope as it should. I didnt see the expansion tank till the new boiler was in and the eye opening was when i was draining the system that when i noticed i have messed  up.
  • KC_Jones
    KC_Jones Member Posts: 5,739
    Options

    @KC_Jones yea i mess up big. I did measure the radiators and came up with the calculations for the sq footage of steam needed, where i mess up the most it was that it is my first time seem a gravity hot water system. I guess there is always a first time. Everything is slope as it should. I didnt see the expansion tank till the new boiler was in and the eye opening was when i was draining the system that when i noticed i have messed  up.

    These questions still stand:

    "Did you ask the customer if they want their system converted to steam?

    It’s their house I really don’t see how you think you have the right to make dramatic decisions about someone else’s house like this, it’s dishonest at the minimum. Does the homeowner even know how badly you messed up?"

    As a homeowner this whole situation has my blood boiling. I am knowledgeable and know better, but this homeowner I'm guessing does not. The OP appears to be trying to pull the wool over their eyes and get away with something instead of being honest about it. You made a mistake, fess up to it and make it right, and making it right could mean a whole new properly sized and installed hydronic (not steam) boiler. The way you sized it is wrong for water, the way you piped it is wrong, the way you apparently quoted it is wrong.

    This is a hot water system, you should not be attempting a conversion unless you have explicit written permission from the homeowner to do such and the homeowner is clear on the implications of such a conversion, which I question if you even know. As said above this is dishonest at a minimum.

    We all make mistakes, it's what we do after that makes all the difference.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    Solid_Fuel_Man
  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    The homeowner may be afraid of having steam.
    Hot water gravity was developed over 100 years ago as an alternative to steam heat which has a bad reputation of explosions.
    Gravity was used because there were no pumps for hot water and in some cases no electricity.

    All history, but the word of "steam" has been ingrained in some people's mind as dangerous.

    You should check with the boiler manf. if this steamer could be converted to hot water. Often it is the same boiler with different trim.

    You could get all the hot water trim that would have come with HW boiler.
    Every safety device must be installed.

    If you used both supply and returns provided and piped them to the full size, you might get the gravity flow restored without a pump.
    The existing attic exp tank might be salvageable if you haven't burned that bridge completely.

    The HO had the simplest system possible. The only moving part was the gas valve.

    Steam will give them more devices that will need attention. LWCO probe, sight glass, water feeder perhaps, more flushing needed, skimming off oils, etc.

    Where are you located? Is your work subject to local inspections?
    Ironman