Update in comments:100yo boiler crack (not cracked)
We have a 1921 A.D. Dennison, Cleveland, OH, gravity hot water boiler.
It developed a crack and we can keep everything dry by keeping the pressure low.
Can the crack be fixed? Can we live with the low pressure indefinitely?
Thank you all for keeping this site informative and fun.
Comments
-
-
If it's a crack and not a rust through (have you seen the crack?), you can attempt a weld if it's in an accessible position, but as Bob said above, it's boiler time. Hey, 100 years is a good run...SkyBluePink said:
Can the crack be fixed? Can we live with the low pressure indefinitely?
If you want to hold off replacment until the weather gets warm and if the leak gets worse even at low pressure, then you can add stop leak (Hercules makes a liquid) which will buy some time.
You'll also use a lot less oil/gas with a modern boiler.
1 -
Never thought about it rusting through. When I looked for the crack, I don't actually see one.
I mentioned it has been dry for awhile. Upon further interrogation of the husband, a bit more info has come to light. When it was wet, the asbestos came off in a chunk. The boiler looks rough. Why would it stop leaking on its own?
0 -
-
-
-
It is so very cool to learn how these work. I suppose nothing in today's market is like this.
I can only guess our thoughts were to wrap the boiler in a hot water tank blanket when we saw a not-too-smooth asbestos coating.
Inside the fired-up boiler, corrosion is visible.
We took down a wall to get at the ginormous marshmallow. Evidence of leakage is obvious now.
0 -
-
-
@SkyBluePink
Your pictures don't show any corrosion or water leaking. If the combustion is safe (no excessive Co) and no water leaking keep running it no panic. 1920 boiler, yes it does need to be replaced. Budget for a replacement and most important find the right contractor1 -
**Update: We learned a number of things.
It seems most likely that one of the pancakes has corroded and we see the slow leak from there. We have been bleeding incorrectly. We should have been draining the expansion tank regularly. The feed valve was defective.
Our flue gas numbers: 84ish% efficiency (!), CO is 220-something ppm, CO2 is 7.4. The numbers are what I remember-what they measure may be mixed up.
So we have a choice: not broke, don't fix it OR replacement is inevitable so may as well.
In the meantime, we replaced the feed valve, discovered the expansion tank drain is clogged, bled the rads correctly. Thankfully we have good weather and can address these without freezing.0 -
-
-
That water heater blanket isn't a great idea either. It is not noncombustible, or at least some parts of it are combustible like the facing and the binder in the fiberglass so it isn't designed to be one something like that boiler where numerous parts of it get hot enough to start something on fire.4
-
You should have both a smoke detector and Carbon monoxide detecter near it. Here is why: as @mattmia2 said, your insulation shell is melting. And, modern burners emit carbon monoxide in the 0 to 5ppm. You have around 200ppm. And, your boiler is leaking enough to melt plastic so, your health and safety is at risk because that CO is escaping into house.1
-
Yep. It's leaking - the fact it's not leaking from a crack specifically changes nothing.EdTheHeaterMan said:if it ain't broke???
you need a new boiler. it IS BROKE
1 -
-
-
Possibly, because I am still learning, I mixed up the CO and CO2 numbers.EBEBRATT-Ed said:Yes. 220 Co is too high, Co measured in the flue gas should be below 50 and anything over 100ppm is considered unacceptable.
Co is very dangerous0 -
It is very possible that I mixed up those 2 numbers. CO detector actually detects nothing, but I agree about the blanket...still learning!SlamDunk said:You should have both a smoke detector and Carbon monoxide detecter near it. Here is why: as @mattmia2 said, your insulation shell is melting. And, modern burners emit carbon monoxide in the 0 to 5ppm. You have around 200ppm. And, your boiler is leaking enough to melt plastic so, your health and safety is at risk because that CO is escaping into house.
0 -
We are fortunate to approach this issue in a dry and warm house--not pressing our luck.
I have learned so much from you, considering becoming a groupie. A six-pack to you all, with our deepest gratitude!!0 -
There are complications about how the UL standard for CO detectors is written that means they don't alarm until there is a fairly significant amount for a significant period of time. Some of the one with LED or LCD displays can indicate lower levels, sometimes only if you push a button.0
-
I believe you have the CO correct. If anything is mixed up, it would be O2 with CO2.
As long as you have something to warn you, regardless of its sensitivity, it is better than nothing.
Still, there is nothing about your boiler worth saving. It is a fuel pig that should have given up its ghost in 1950. You should think of it as a zombie. a living dead.0 -
@SlamDunk Would it surprise anyone that our average winter gas bill is just under $100?0
-
If I bought a house and it had a decent 1920s-30s three pass boiler in the basement, I would probably hesitate replacing it until I had to. At least if it was setup well and seemed reasonably sound (no leaks etc).
But that style boiler..........with whatever it's going on for insulation. That needs to go. That's about as appealing as an outhouse breeze.
You're talking about something you depend on during the winter. Something you literally cannot be without.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
3 -
There's no way that's CO2 7.4 and your efficiency is 84%. There's also no way it's 84% in general, which if true is only the burner efficiency, not total system efficiency which is at best 50%.
There was an error rendering this rich post.
0 -
Isn't combustion efficiency calculated by the analyzer using the difference between calculated flame temperature and exhaust temperature?STEVEusaPA said:There's no way that's CO2 7.4 and your efficiency is 84%. There's also no way it's 84% in general, which if true is only the burner efficiency, not total system efficiency which is at best 50%.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Not just that. @Jim Davis could explain it much better.
There was an error rendering this rich post.
0 -
Very surprised!SkyBluePink said:@SlamDunk Would it surprise anyone that our average winter gas bill is just under $100?
Because I used to have two houses with similar systems.
One was a 1920 oil furnace (1800sqft house) in NYC and the other was a 1930 (1000 sq ft house) steam boiler in NC. The 1930 boiler most resembles what you have.
The fuel bills were GI-normous when compared to the upgrades. So, less than $100 tells me you are in a bungalow in Miami with your own gas well.1 -
Or the meter is as old as the conversion burner and underreads significantly. Or the regulator is running much higher pressure than the meter is calibrated for.0
-
mattmia2 said:Or the meter is as old as the conversion burner and underreads significantly. Or the regulator is running much higher pressure than the meter is calibrated for.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
@MaxMercy lol! Connecticut Loot and PlunderServing Northern Maine HVAC & Controls. I burn wood, it smells good!1
-
It looks like there is a hole in the firebox next to the door0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements