Free Electricity, Maybe GeoThermal Is The Way To Go?
I had 15kw of solar installed last year and it's providing more than enough power throughout the year for us. When I installed the Buderus, I put in some valving to possibly accommodate solar thermal input assistance. Given my abundance of electricity, I'm wondering if a geothermal heat pump with a heat exchanger interface to the current radiant system might be a worthwhile investment. Use up the solar and stop burning the oil. We don't have NG available.
I'm on Cape Cod in Massachusetts. My delivery temps on the floors runs anywhere from 95 to a max of 115.
Anyone out there can walk me through the pros and cons?
Thanks as usual.
Comments
-
The only heat pumps I’ve found that stand a chance on solar are mini splits. Without an inver driven compressor and small one at that a standard compressor will draw more inrush current then your system can provide.0
-
John Siegenthaler has a whole series of articles I believe in the publications of Radiant & Hydronics and PMEngineer including his own personal experience designing and installing the system in his daughters house. I don't know how to tell you how to find them, perhaps someone here could tell you how.0
-
I assume you're net metered and not off grid? If so geothermal could work but has a relatively high first cost. For the cost of the loop you might be able to install another 10kw of solar.
I would be tempted to install an air to water heat pump, and possibly an electric boiler, depending on how much excess production you have. The heat pump will give more than double the BTU per kwh but if you have a lot of excess generation the electric boiler is cheap to install (and expensive to run).
You could even skip the hydronics and just put some electric heaters in the house to use up your kwh credit. Hopefully your utility allows you to see usage on a day to day (or hour by hour) basis so you don't end up with a month of over usage though.
If the goal is to run the equipment off grid via solar and batteries that's a whole different discussion.0 -
There is a fundamental problem with solar PV: the sun doesn't always shine. In fact, when you need heat, it is quite likely that the sun isn't shining. Therefore... unless you also have a large battery bank and a big enough array to charge it, you have to be looking at net metering -- or not use PV for heat, even by a heat pump.
This is not to say that it can't be done, although for new construction it is much better and more efficient to use solar heat gain and thermal mass storage directly, rather than losing the efficiency through the conversion to electricity. It's only to caution that if you want to use solar PV for heat, do your math very carefully A couple of rather general rule of thumb numbers to start you off on the math, in New England -- including the Cape -- the general rule is that one can expect three hours of usable sunlight, on average, in a day, but, also on average, you can expect no usable sun at all for three days at a time. Therefore, to simplify, you need to be able to store enough kilowatts to run for three days with no input, and enough solar array to recharge that battery capacity in no more than nine hours. If you are using net metering, and your electricity rate is the same for use from and sale to the grid, then the math is a little different: you need to be able to generate in 3 hours the total electricity you use in 24.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Regardless of solar, I like ground source heat pumps better than oil. The up front cost is an issue for sure, but the operating cost is equivalent to cheap natural gas in my experience. Here's my story:
I had a vertical well. It was a 2000 sq ft cape cod two story house in Connecticut and my engineer sized it for a single 500 foot well.
You do a regular heat loss calculation on the building, and then size the heat pump and the well to that BTU rating. You do want to have (or eventually install) good insulation. I purposely had him size mine a little small with a plan to increase insulation (which I did).
The well I contracted out to a driller. His quote included putting in the plastic loop, then sealing the well with the thermal grout, and running the loop into my basement terminated with fittings.
I got the heat pump from an internet supplier that I can recommend called Ingram. I got a slightly older version of this unit: https://iwae.com/shop/3-ton-variable-speed-climatemaster-central-air-handler-multiposition-ha12537.html
So that's the "heat pump". It heats and cools. Then you also need a pump (flow center) to circulate the ground loop. I went with this one: https://iwae.com/shop/geo-pulse-non-pressurized-flow-center-single-pump-ha12100.html
It is an "atmospheric" pump meaning the ground loop is not under pressure. I chose it due to its simplicity...you don't have to "purge" and pressurize the loop with this kind of flow center. I ran a little food-safe antifreeze in the loop, but I never got the loop water down to 32dF.
Ingram has lots of good information and product manuals to look over.
I was able to plumb everything with pex and wire it myself even though back then I knew a lot less about heating and cooling systems.
I previously had an oil burning forced air furnace in place that I removed with a dolly and slid this unit right in its place. In a house with a water boiler, I would of course get a water-to-water unit. I was done in a day (It was cold out, so I ran the oil furnace to get the house nice and warm and then went for it.
In more southern climates I think this system would be perfect. Up north in the winter, to be honest, it was a little slow to heat the house. It always did heat the space, but you really don't want to use a setback because it just can't blast the house with hot air like a burner can. So my wife wasn't always happy with it, but it's really just an adjustment of expectations. Even during bitter stretches it could heat the house fine. You can monitor the temperature of your loop water incoming and outgoing to see how it changes during the seasons.
The operating cost was similar to today's cheap natural gas (which was not available at my location), and the air conditioning was super cheap because it is using constant 50 degree water and it can dump a lot of heat out of the house easily into unlimited 50 degree water.
Feel free to ask any questions you think ofNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Ill agree but the energy required to get that Ground Source Heat Pump up and running with solar? Not going to happen. It is possible to fire the oil gun or Gas controls!ethicalpaul said:Regardless of solar, I like ground source heat pumps better than oil. The up front cost is an issue for sure, but the operating cost is equivalent to cheap natural gas in my experience
0 -
Now if someone would come up with a ground source heat pump which would boil water...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Air to water HP are getting more and more common. I suspect if you are grid tied you get little to any money for excess, may as well use as much as possible. GEO does have a small efficiency over air to water, but installation of the loop field can be $$.
The make or break is the SWT required, you might be in a good position to use a A2WHP.
Some more reading
https://www.caleffi.com/sites/default/files/file/idronics_27_na.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Air to water HP are getting more and more common. I suspect if you are grid tied you get little to any money for excess, may as well use as much as possible. GEO does have a small efficiency over air to water, but installation of the loop field can be $$.
The make or break is the SWT required, you might be in a good position to use a A2WHP.
Some more reading Google Idronics 27, can't seem to attach a file tonight.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
I agree with that @pecmsg but I read his post as "I am generating a lot of electricity and want to stop buying oil" not "I am off the grid and want to heat exclusively with my generated power"pecmsg said:
Ill agree but the energy required to get that Ground Source Heat Pump up and running with solar? Not going to happen. It is possible to fire the oil gun or Gas controls!ethicalpaul said:Regardless of solar, I like ground source heat pumps better than oil. The up front cost is an issue for sure, but the operating cost is equivalent to cheap natural gas in my experience
If he was saying the latter, then yeah it's not going to work.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Thanks for the comments all.
I am in a net metering situation. So from late march through June, I'm getting 90-100kwh/day and then around 80kwh/day through September when it drops down to around 50.
In MA we also have buyback credits. On average I see checks per month around $300. In the winter months, I use more electricity than I produce but I have excess in the bank. It's also keeping the wife's Hyundai EV charged.
My thinking was around consuming some of that excess electricity to power the HP. I'd interface that to a water2water heat exchanger for the radiant loops and maybe the domestice HW. I have the interface plumbed in on the manifold as I had originally planned on putting evac tubes in place. But the MA solar deal was way better. I paid 42k for 15kw of solar and got $17k rebate so I'm currently projected to pay back the cost of it in year 4 based on reduction cost and credits.
ethicalpauls experience is interesting. Hard and costly to get work done here on the Cape but I might look into seeing what I could get for a price on the drilling, sealin and running the tubes into the house. I can handle the rest of the install from there.
george_42s figures looks like around 75kwh/day average to run the HP which is fairly minimal given my situation.0 -
I have a very similar situation to yours. I have a 15 kW solar array net-metered (started out as 5 kW, then I added 10 kW to it). I installed a 3 ton geothermal system (Geostar) sourced by two 225 foot deep vertical grouted wells, closed-loop. I have underfloor radiant heat with 1/2" pex and thick aluminum plates. The system works great. I estimate I am using about 4 MWh/year to heat a 1750 square foot house in Central NY (7500 degree day climate). My water temperature at 0 degree outside is 120 degrees F (system uses outdoor reset). I have a 180 gallon Stiebel Eltron water storage tank with a heat exchanger and I plumbed the cold water supply to the DHW tank through the heat exchanger to preheat the cold supply to the DHW. I'm going to plumb a line to a heat exchanger and have it pre-heat the return air from the HRV that is getting installed. Then, I can also use it to chill air and provide some small amount of AC and dehumidification in the summer. Everything is powered by a single Grundfos Alpha pump that uses about 14 W of electricity on average. Thanks to many on this forum for getting me to such a great system.
It's been heating an empty house for two years now as the renovation was underway. I expect to move in this December.
I'd estimate my total costs were around $35k after tax, but I used my own labor for system design and helped run the PEX loops with a crew of two guys I hired to help out. I'm also in a lower cost of living area. These systems are not cheap to install but the running cost is pretty low (about $500/year or less if I paid for the electricity from the utility).
My 15 kW system supplies about 18 MWh/year - 4 MWh for the heating system, 6 MWh for the all-electric house (non-heating), 3-4 MWh for the electric vehicle, and some room to grow into a 2nd electric vehicle.0 -
Back in the 70's i did a few water to water Vanguard HP's. They are long gone and good riddance, but we used a glazed solar array to heat a swimming pool and used the swimming pool to drive the hp. It worked great in heat. Cooling could be a problem as on a couple of the pools we had to install small cooling towers to get rid of the rejection heat from the cooling mode. The solar also heated the dhw and hot tub, etc.0
-
Not to crack the egg shell but the rebates and incentives that are given I kinda wonder how many would still go the route w zero rebates ? Another always on my mind is after all the money shuffling exactly who’s the ones giving it away the money and really footing it I wonder the general public ? Last but not least if you had to foot the whole bill w out any rebates and free money give aways at all would you still go for it ? I hate to get reality confused w negativity . Things have come a long way but I yet to see a inverter based geo or multi staged one . The ones I have seen had simple tube in tube heat exchanger same as used 50 years ago . The last point is when the ground well or geo unit goes will the same incentives be given for replacement or will you be footing that bill on your own . To be reality based without any rebate or incentives would the geo therm industry thrive without tax payers helping. I know they where screaming when they wanted to cut the funding and incentives Year’s back . I know I ve never received and free lunches from the government and I feel if a industry cannot make it on there own 2 feet then why should tax payers foot the bill the ceo is taking a pay check ?
Never confuse negativity w reality
Peace and good luck luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements