  • mattmia2
    mattmia2 Member Posts: 9,646
    Options
    The 2 outlets of a boiler when set up for steam are a result of how the boiler is manufactured and assembled, each section has an interconnection, they connect to each other on the middle sections, they are the steam outlets on the end sections. On modern boilers they need to both be used and sometimes the outlet piping needs to be upsized to slow down the steam, separate the steam from the water, and keep the steam from pulling the water out of the boiler with it. The header needs to be constructed in a specific manner to promote the water to separate and drop in to the return to the boiler, not get trapped in the header, and not be pulled in to the system with the steam. On a boiler set up for hot water frequently only one tapping needs to be used or different trappings can be used for different purposes, but on a boiler set up for steam, both trappings must be used and connected to a common header before splitting out to multiple mains if the system has multiple mains.

    If you do not do this, the water pulled in to the steam mains will cause water hammer, unstable boiler water levels, and may pull water in to radiators where it may be pushed out the vents. The near boiler piping is critical to make the system function properly.
    Ironmanbilly42945Canucker
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options
    mattmia2 said:
    The 2 outlets of a boiler when set up for steam are a result of how the boiler is manufactured and assembled, each section has an interconnection, they connect to each other on the middle sections, they are the steam outlets on the end sections. On modern boilers they need to both be used and sometimes the outlet piping needs to be upsized to slow down the steam, separate the steam from the water, and keep the steam from pulling the water out of the boiler with it. The header needs to be constructed in a specific manner to promote the water to separate and drop in to the return to the boiler, not get trapped in the header, and not be pulled in to the system with the steam. On a boiler set up for hot water frequently only one tapping needs to be used or different trappings can be used for different purposes, but on a boiler set up for steam, both trappings must be used and connected to a common header before splitting out to multiple mains if the system has multiple mains. If you do not do this, the water pulled in to the steam mains will cause water hammer, unstable boiler water levels, and may pull water in to radiators where it may be pushed out the vents. The near boiler piping is critical to make the system function properly.
    IMO the "outlet piping" or risers should never be upsized bigger than the tappings.  It slows the steam after water has already left the boiler and the only thing it could possibly do is trap water in the risers.  That's bad.    

    This is why the header is bigger. It slows the steam down allowing water to separate and not get dragged with the steam and drains.  


    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,525
    Options
    Most don't have a threader to do anything larger than 2" so they do 2" even if the MFG calls for larger pipe.

    If they do size it right it's copper sweat or propress or steel with Megapress
  • billy42945
    billy42945 Member Posts: 47
    Options
    THANKS FOR EVERYONE'S INPUT ON THIS SUBJECT.I DID NOT REALISE I SHOULD HAVE POSTED THIS ON ORIGANIAL POST .
    (NEW TO at ths
    PICTURES OF THE boiler on the first post.

    Burnham IN 8 residential gas boiler pipeing.
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,284
    Options
    @billy42945, we've merged all of your posts about the Burnham together here.
    President
    HeatingHelp.com
    STEVEusaPAmattmia2
  • billy42945
    billy42945 Member Posts: 47
    Options
    Thanks for your help and understanding we are all still learning and when we stop we are uneducated !!
  • billy42945
    billy42945 Member Posts: 47
    Options


    This is a picture of how the general contractor let his sub contractor carpenters cut out the near boiler pipeing.
    Note they did not need a manual it was not in there language.
    They had no idea of a header is and will never know.

    Sorry my dad was a bricklayer and he informed me that they
    Thought they could do any ones work.
    50 years later it still the truth. I have the breasted respect for people who do this type of pipeing.
  • billy42945
    billy42945 Member Posts: 47
    Options


    This is the image of header pipeing of the Burnham IN 8
    That was cut out with a saws all the original person who put this in told me he does not care to to do this work any more
    It brings tears to my eyes. IF A poem buy kipping.
    IF YOU CAN BEAR THE THINGS YOU DONE BROKEN AND BUILD THEM BACK
    UP WITH WITH WORN OUT TOOLS AND START OUT AT THE BEGING AND NEVER BREATH ABOUT YOUR LOSS.

    YOU ARE A MAN MY SON!! (AT LEAST YOU SHOULD CRY)

  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options
    I don't feel you need to be an expert to cut piping out with a Sawzall.


    However whoever puts it back needs to know what they're doing and I don't care what their title is.   There's plenty of heating contractors that have no business touching a steam boiler. And yet, there's at least one carpenter that could pipe one correctly without a book.




    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    billy42945
  • Ironman
    Ironman Member Posts: 7,376
    Options
    The shame of it is that there were unions from which it could have easily been disconnected without cutting anything.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    STEVEusaPAmattmia2ethicalpauldelta T
  • billy42945
    billy42945 Member Posts: 47
    Options



    This is the image of header pipeing of the Burnham IN 8
    That was cut out with a saws all the original person who put this in told me he does not care to to do this work any more
    It brings tears to my eyes. IF A poem buy kipping.
    IF YOU CAN BEAR THE THINGS YOU DONE BROKEN AND BUILD THEM BACK
    UP WITH WITH WORN OUT TOOLS AND START OUT AT THE BEGING AND NEVER BREATH ABOUT YOUR LOSS.

    YOU ARE A MAN MY SON!! (AT LEAST YOU SHOULD CRY)

    DO not Judge !!! For they know not what they Do !!
  • billy42945
    billy42945 Member Posts: 47
    Options
    ChrisJ said:

    I don't feel you need to be an expert to cut piping out with a Sawzall.


    However whoever puts it back needs to know what they're doing and I don't care what their title is.   There's plenty of heating contractors that have no business touching a steam boiler. And yet, there's at least one carpenter that could pipe one correctly without a book.




    Are you referring to Jesus Christ !!
  • billy42945
    billy42945 Member Posts: 47
    Options


  • billy42945
    billy42945 Member Posts: 47
    Options
    Looks like contractor has manual Not done yet but this was done today . Will post finished work thanks for all your Input.
    mattmia2realliveplumberSTEVEusaPA
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options
    I don't feel you need to be an expert to cut piping out with a Sawzall.


    However whoever puts it back needs to know what they're doing and I don't care what their title is.   There's plenty of heating contractors that have no business touching a steam boiler. And yet, there's at least one carpenter that could pipe one correctly without a book.




    Are you referring to Jesus Christ !!


    My old man was a carpenter for 50 years and helped me pipe my boiler.

    He could do it again no problem thanks to Dan's books.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • JohnNY
    JohnNY Member Posts: 3,230
    Options
    This thread is painful.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    mattmia2EdTheHeaterManethicalpaul
  • billy42945
    billy42945 Member Posts: 47
    Options
    Thanks John NY
    In MA. ITS UP TO each TOWN in MA. To have a Mechanical
    Inspector. Our town does not have one . I Informed the home owner of this who was going to wait untill his boiler work was done and wait for Plumbing inspections. I INPLORED HIM THAT HIS BOILER WAS ONLY 4 years and he had a service contractor that I contacted and they told me to have him call for a inspection it would not cost him a anything. Not only did they not like what they seen they called the Burnham Reb . That's when things got better.




  • billy42945
    billy42945 Member Posts: 47
    Options
    ChrisJ said:



    ChrisJ said:

    I don't feel you need to be an expert to cut piping out with a Sawzall.


    However whoever puts it back needs to know what they're doing and I don't care what their title is.   There's plenty of heating contractors that have no business touching a steam boiler. And yet, there's at least one carpenter that could pipe one correctly without a book.




    Are you referring to Jesus Christ !!


    My old man was a carpenter for 50 years and helped me pipe my boiler.

    He could do it again no problem thanks to Dan's books.

    CHRIS THANK YOU , FOR YOUR PASSIONATE REPLAY ABOUT YOUR DAD!!
    HE BELIEVED IN DAN'S BOOKS AND I THINK THATS WHAT MADE HIM AND YOU BETTER PEOPLE.
    My responce to people in my Trade Electrical ( Trouble shooting after 50 Plus years.

    I COULD DO IT QUICKER TOO WHEN I DID NOT KNOW WHAT I WAS DOING.


  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options

    ChrisJ said:



    ChrisJ said:

    I don't feel you need to be an expert to cut piping out with a Sawzall.


    However whoever puts it back needs to know what they're doing and I don't care what their title is.   There's plenty of heating contractors that have no business touching a steam boiler. And yet, there's at least one carpenter that could pipe one correctly without a book.




    Are you referring to Jesus Christ !!


    My old man was a carpenter for 50 years and helped me pipe my boiler.

    He could do it again no problem thanks to Dan's books.
    CHRIS THANK YOU , FOR YOUR PASSIONATE REPLAY ABOUT YOUR DAD!!
    HE BELIEVED IN DAN'S BOOKS AND I THINK THATS WHAT MADE HIM AND YOU BETTER PEOPLE.
    My responce to people in my Trade Electrical ( Trouble shooting after 50 Plus years.

    I COULD DO IT QUICKER TOO WHEN I DID NOT KNOW WHAT I WAS DOING.




    Both of us like Dan's books.
    I'd never do work without knowing what I was doing was correct.

    I wish Dan would do more books. I like how he writes.

    @DanHolohan I need some books on 3D modeling and 5 axis CNC machining please.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    mattmia2
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,526
    Options
    😂. Thanks. 
    Retired and loving it.
  • billy42945
    billy42945 Member Posts: 47
    edited August 2020
    Options
    Thanks but i have a long way to catch up with Dan's posts.
    mattmia2
  • billy42945
    billy42945 Member Posts: 47
    Options



    This hartfood loop looks good but why the
    Copper water feed for make up water in tee below the Hartford loop.what happens if this brakes ???
  • billy42945
    billy42945 Member Posts: 47
    Options

    Top down view of auto/manual water feed below Hartford Loop.
    For boiler make up water !!!
  • billy42945
    billy42945 Member Posts: 47
    Options
    Now if you have a problem pipeing to water feed or the water feeder itself your boiler water could drain bypassing the loop.
    Hope the other trade wired your low water cut out right.
    Been on a lot of miss wired low water cut outs troubles !!
  • billy42945
    billy42945 Member Posts: 47
    Options
    Company empolyie working on job today thought I went to far buy posting this on the internet I told him I would have posted to his company but they only had a web site and no Email to send pictures too they are just to big and I guess why should they look at what I think is wrong they after all are a team who does not need help ??? If you want to be on team work for Walmart!!
  • billy42945
    billy42945 Member Posts: 47
    Options
    IF they think I went to far by posting to the internet on the wall.
    Waite to they see the Movie.
    The **** Show. ****=**** did know if could post this word ??
  • billy42945
    billy42945 Member Posts: 47
    Options
    I can't find a black flow preventer on the automatic water boiler water feeder I guess there excuse will be be they are not finished yet !! Thank *** note ***=GOD HOPE I CAN USE THIS WORD
  • billy42945
    billy42945 Member Posts: 47
    Options
    Check out page 202 of Dan holahan boiler feeder 1992 the lost art lost art of steam heating. In 1969 I took Buhrkhart book
    On oil burners
    1969 book to troubleshoot ..aA jop for a plumber. The owner was upset that I needed a book to solve his problem not many people at this time knew what ZC or ZR TERMINALS WERE FOR ON HOT WATER SYSTEM NOR THEY DO 50 years later at this time .
    The terminal 2 to 3 is a jumper that has to be install depending on what voltage you want to feed the make up water coil.
  • billy42945
    billy42945 Member Posts: 47
    Options


    THIS IMAGE IS NOT BOILER IN QUESTION ON MY IN8 POST.

    NOTE BOILER WATER MAKE UP IN THIS PIC BEFORE HARTFORT LOOP NOT AFTER IN MY POST OF THE BURNHAM IN 8.

  • billy42945
    billy42945 Member Posts: 47
    Options


    The new Hartford loop with the wet returne above the boiler water line . Any comments
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,837
    edited August 2020
    Options
    This looks like a picture we have already viewed above. I see no Hartford loop in this photo?!? There is no equalizer in this photo.

    If this is a correction of previously failed piping, then you need to get someone who knows something before this winter.
    you see in the illustration below, the return water must enter the boiler below the waterline... not above the waterline.

    August 16 post of old piping has a proper Hartford loop. It might be time for a Lawyer.

    This illustration shows the HARTFORD LOOP


    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,837
    Options
    The second picture from Aug 12 looks like someone is getting it right.

    Is the Picture from Aug 17 a mistake?


    @JohnNY said "This thread is painful." on Aug 12
    @EdTheHeaterMan Says: "This thread is painful." on August 18
    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics
    JohnNYJUGHNE
  • billy42945
    billy42945 Member Posts: 47
    Options

    Yes ment to show boiler feed water to boiler after Hartford loop !! Aug 12 picture is getting a lot better will post final when they get things right note no back flow preventer for boiler automatic fed make up water.
  • billy42945
    billy42945 Member Posts: 47
    Options
    in the picture posted the 1/2 inch copper pipe into 2 inch tee is auto feeder make water after the hartford loop into boiler is this ok ??
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options

    in the picture posted the 1/2 inch copper pipe into 2 inch tee is auto feeder make water after the hartford loop into boiler is this ok ??

    Many feed a boiler in this location.
    I did on my own. It allows fresh washer to get to the boiler faster to drive O2 out.

    As far as what if the pipe breaks, the LWCO will take care of it just like it will in any other low water condition.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • billy42945
    billy42945 Member Posts: 47
    Options
    Thanks for your comment . BUT THINK ABOUT WHAT THE HARTFORD LOOP IS FOR ITS TO MAKE SURE THE BOILER WATER DOES DRAIN LOWER THEN THE LOOP . IF YOU DEPEND ON THE LOW WATER CUT OUT WHY DID YOU PUT IN THE HARTFORD LOOP .?? BY FEEDING WATER AFTER IT ?? THANKS .
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 1,968
    Options
    Belt and suspenders. There is always pipe on the boiler side of the loop. That pipe is unprotected by the loop. 
  • ChrisJ
    ChrisJ Member Posts: 15,677
    edited August 2020
    Options
    Thanks for your comment . BUT THINK ABOUT WHAT THE HARTFORD LOOP IS FOR ITS TO MAKE SURE THE BOILER WATER DOES DRAIN LOWER THEN THE LOOP . IF YOU DEPEND ON THE LOW WATER CUT OUT WHY DID YOU PUT IN THE HARTFORD LOOP .?? BY FEEDING WATER AFTER IT ?? THANKS .
    I put a loop in because code required it.
    Otherwise I probably wouldn't care.  There's been long arguments about it on here.

    What happens if the LWCO fails and the pipe breaks after the loop?  The boiler slowly empties and dry fires because people rarely check on it until the house is cold.

    Code requires it as does the manufacturer so you install it.  But anything on the boiler side is fine.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    ethicalpaul
  • JUGHNE
    JUGHNE Member Posts: 11,061
    Options
    Billy, the Hartford Loop idea was set in place just over 100 years ago.
    Many boilers were coal fired, hard to shut down.
    The technology for LWCO and feeders was limited.
    Those boilers contained a lot of water that would give a little more time before the unit dry fired.

    There has been much discussion here concerning the HL because boilers contain so little water. If the return lines are broken then not much time before dry firing. That is why LWCO's are so necessary.

    The HL will probably stay in use forever.
    You do not need one with a boiler feed pump, but you still need an equalizer.
    ethicalpaul
  • billy42945
    billy42945 Member Posts: 47
    Options
    Circulator in picture lasted two weeks