Trane - Stuck in the station
PC
Member Posts: 24
I have a Trane hot water boiler (TGBWF090A93AVAA -installed 12/2008 by previous owner) that is getting stuck in lockout on a regular basis.
I get a pilot flame then after a few seconds it kicks off and goes into lockout/service required after the main burner doesn't fire.
Have cleaned the flame sensor and reinstalled (several times) and can get it going again but after the night set-back of only 4-5 degrees it locks out sometime overnight and I wake to a cold house and a locked out boiler control.
Bad flame sensor?
Thanks for any input on this unit
I get a pilot flame then after a few seconds it kicks off and goes into lockout/service required after the main burner doesn't fire.
Have cleaned the flame sensor and reinstalled (several times) and can get it going again but after the night set-back of only 4-5 degrees it locks out sometime overnight and I wake to a cold house and a locked out boiler control.
Bad flame sensor?
Thanks for any input on this unit
0
Comments
-
-
Thanks Ironman...
0 -
After some extensive troubleshooting and installing a new Electronic Ignition Control (CNT05035) we are back in business.
0 -
Is that a modulating atmospheric boiler? I didn’t know they existed. It says 30 min, 90 max.
Efficiency is 80% low, 82 high.0 -
0
-
That a huge turndown ratio for a high low 3:1. Most 2 stage gas valves are only 3:2 at best. But a typical turndown for a gas furnace is 3:1.
Who makes this boiler? Dunkirk?0 -
I have six of these units. I have consumed a few ignitors and it has been impossible to find the parts. The boiler / ignitor is Ferroli. Completely unsupported. In fact, they do not want to speak to anyone in English. It's a great boiler when it works.0
-
actually, atmospherics are modulating ready from the get go. they pull air based on the gas flow working just like the burner on your stove. implementation lags-given that these aren't naturally conducive to a condensing design, so that feature has been less relevant–although if you have partial load could make a little sense although the stack efficiency is pretty similar across the range so the industry has been satisfied with cycling rather than low fire.mikeg2015 said:Is that a modulating atmospheric boiler? I didn’t know they existed. It says 30 min, 90 max.
Efficiency is 80% low, 82 high.
i've been more interested in it from a steam control perspective so you can have high fire to make steam and modulated fire to keep steam.
but what a parts headache for an otherwise useful boiler @turneim.
@PC don't know how much documentation there is or if you have to be able to read italian but you can usually test the flame rod signal. 15 years for a new logic control is within the envelope although it reveals the vaguries introduced by digital control. A good ole fashioned analog 2 stage aquastat could do the same the same thing but, they went digital. what are the connections at the control, if they are screw terminal, non issue but I have had trouble with proprietary multiple lead plug connectors on goodman/honeywell combo. So if it goes back to occasional lockout, that is worth considering, but sounds like you solved it.
brian0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements