Liquid Nitrogen Piping

Zman
Member Posts: 7,611
A friend of mine is working on a project that requires a 40' underground delivery pipe for a liquid nitrogen.
They are hearing conflicting information on the type of pipe required. One party is saying Type K hard or soft copper, the other is saying braided stainless steel. The pipe will be exposed to -321 F temp.
Has anyone had experience with this?
@Jamie Hall ?
They are hearing conflicting information on the type of pipe required. One party is saying Type K hard or soft copper, the other is saying braided stainless steel. The pipe will be exposed to -321 F temp.
Has anyone had experience with this?
@Jamie Hall ?
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein
Albert Einstein
0
Comments
-
A quick Google search yielded specialized vacuum insulated stainless steel piping.Zman said:A friend of mine is working on a project that requires a 40' underground delivery pipe for a liquid nitrogen.
They are hearing conflicting information on the type of pipe required. One party is saying Type K hard or soft copper, the other is saying braided stainless steel. The pipe will be exposed to -321 F temp.
Has anyone had experience with this?
@Jamie Hall ?
I highly recommend whoever does it finds out for sure what they need to do. Something actually documented.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
-
We did a project back in the late 1980's with nitrogen. The manufacturer/nitrogen supplier supplied all of the piping. It was copper type K rigid with factory applied 3" rigid foam pipe insulation, covered with a white plastic coating (it was installed mostly outside the building). If I remember correctly, we brazed with silver brazing rod (very expensive) and had to run nitrogen (or was it some other inert gas) through the piping when we brazed it. Fittings were heavy wall if I recall. Special long stem "cryogenic" valves were used, if not user's hand would get instant "freezer burn" when someone touched a valve handle.
Again it was thirty years ago, but I think it was Union Carbide and/or Linde that supplied the roughly sixteen feet tall vertical tank ( I guess about 1000 gallons) and most of the materials mentioned above. I believe they made money off the nitrogen and the tank rental fees. Insulated piping and fittings were a lost leader I guess.
Really nothing tricky, except a twenty foot length of 1" copper type K weighed about 100 pounds (with the insulation) compared to around 10 pounds for plain copper. Pipe was placed on 6x6 treated wood blocks on the roof, with nothing more than galvanized 6" straps to hold the insulated pipe in place. The copper elbows were covered with the 6" plastic shell and then triple expanding foam (or something similar) was injected and left to cure.
I don't recall any special tools or licenses were required, but again that was a long time ago. For the record, the system was in place and used for about ten years without any problems. For the life of me I cannot recall if there was a regulator on the outlet of the tank or was it placed inside near where they "flash froze" the pizza bites. By the way, the were the best pizza bites I've ever eaten!1 -
@ScottSecor 's played with the stuff more recently than I have. Underground or not, you have to have insulation on it and use the correct fittings and braze. Solder won't take it.
You also have to make provision for expansion and contraction -- one end of your 40 foot section can and probably should be fixed, but the other end absolutely has to be free to move, and not just a little. There I would make the connections to whatever this thing is going to with the braided stainless -- either that or cryogenic rated expansion joints. The movement will be on the order of several inches.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
@Jamie Hall has a god point, we put a "U" in the middle of the roughly sixty foot run on the roof for expansion.1
-
I have piped liquid nitrogen from the vacuum jacketed tank to a mixing station for a welding gas supplier.
Did it with regular ACR type L and refrigeration fittings. Sil-Fos 15% with standard nitrogen purge. It should be insulated, if not it ends up with 3" of solid ice on it in about an hour. Any voids in the braze joints show up as its cryogenically frozen and will leak.
Keep in mind wherever the shutoff valve is that any liquid in the lines will boil off and have tramendous pressure. We braze in little bell shaped relief valves between every potential trap point.
The stuff is wicked cold!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 941 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements