Adding an indicator light to a circulator.
Two btu per sq ft for degree difference for a slab
Comments
-
You can wire in a 24-V led indicator lamp in parallel with the 24-V control circuit that supplies the relay for the pump. Here is an example: https://www.amazon.com/Baomain-AD16-22D-Energy-Saving-Indicator/dp/B01MEEIYAM/ref=sr_1_5?hvadid=4966898259&hvbmt=be&hvdev=c&hvqmt=e&keywords=24v+led+light&qid=1561834418&s=gateway&sr=8-5
Otherwise, you can connect a 120-V pilot lamp in parallel with the power feed to the pump. Either way, no ballast resistor is required.
Don't mess with 120-V wiring unless you have the experience and knowledge to do it safely.0 -
I've been considering switching the disconnect (toggle) switches on my circulators to pilot lit (NB: not lighted/lit handle) switches for just that purpose. You can also get a manual motor starter with a pilot light, but IIRC that was a lot more expensive.
What I'd really like is a super cheap single-phase HOA motor starter, but that's pie-in-the-sky.
0 -
Tacos 00-R (radiant) pump has an indicator light built in.0
-
Hello, This may be misguided thinking, but could you simply wrap some wire around the power supply to the pump and hook up a LED to it? Would the induced power be enough to light up the LED? Hmmm
Yours, Larry0 -
I was going to suggest a CT switch. This way would be more funLarry Weingarten said:Hello, This may be misguided thinking, but could you simply wrap some wire around the power supply to the pump and hook up a LED to it? Would the induced power be enough to light up the LED? Hmmm
Yours, Larry"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
For your own use? On non ECM style?
I buy these lights from Radio Shack, a few bucks for a pair. a Unibit to drill a hole in the terminal box.
Probably voids any UL listing.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I’ve done that quite a bit with commercial pumps. Not so much with residential because the pump relays or the pumps themselves usually have them.Steve Minnich0
-
RIB. Relay in a box has relays with lights built in. OPPS I see it’s has already been posted.0
-
I used to use a 120v led and mount it directly to the circ electrical box.
But then I found out that you are modifying an UL approved electrical box that way.
You could however use this !!
Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0 -
I'm with Alan, it's nice to have a light right on on the circulator.
I'd rather manufacturers give us an indicator light instead of a lying GPM readout on ECM circs Or a temperature read-out even.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Likely can wrap an insulated wire around only the single hot lead ( 120V ) that powers circulator ( can't also wrap around the neutral or ground wire). Then connect a NEON bulb (no series resistor) between that wire and neutral.
Takes extremely little current to light a 120V neon light, capacitive coupling transfers energy across the gap. Might not be super bright, unless length of parelle wire wrapping is longer.
Not sure what electrical code has to say about this.0 -
Not only for hot water systems, we need lights on the pressure controls, LWCO, and any other safeties on steam systems. They would be so inexpensive to make, and so useful for the homeowner to refer to when diagnosing his system.—NBC0
-
I use these, but with the capacitor under the cover (non ECM) there is little room.
It is a standard 120v neon indicator, this one is an LED version of the same thing.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Funny I’m not hte only one that thinks this. I was going ot build my own little indicator panel for my boiler at home. But decided thewiring was too much work and had no clean place ot mount it without adding even more wiring. I’m at least going to add a single light for a call for heating, hi stage call, and probably one for 24VAC off the transformer secondary.nicholas bonham-carter said:Not only for hot water systems, we need lights on the pressure controls, LWCO, and any other safeties on steam systems. They would be so inexpensive to make, and so useful for the homeowner to refer to when diagnosing his system.—NBC
0 -
-
Reminds of when I was a kid and we used to make our own boards for our model train layouts.mikeg2015 said:
Funny I’m not hte only one that thinks this. I was going ot build my own little indicator panel for my boiler at home. But decided thewiring was too much work and had no clean place ot mount it without adding even more wiring. I’m at least going to add a single light for a call for heating, hi stage call, and probably one for 24VAC off the transformer secondary.
There was an error rendering this rich post.
0 -
Reminds of when I was a kid and I used to build my own TVs.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements