Based on everyone's great advice, I replaced a 79-year-old B & G circulator that was leaking with a Grundfos 15-58 because I wanted a choice of speeds in case low or medium didn't work (see performance curves below). I added 30# gauges on the suction and discharge sides of the pump to determine pressure drop and the results were surprising.
I added the gauges out of curiosity. I didn't know the actual pressure drop of the system. Three-eighths tubing in the plaster ceiling was known, but was it 3/8" o.d. or i.d.? And how long were the loops?
As I said, the results were surprising. The pressure drops were:
Low speed: 7 feet
Medium speed: 9.3 feet
High speed: 11.7 feet
At low speed, the Grundfos satisfies the heating requirement of 3 gpm. I shot the ceiling with my infrared camera and it was all aglow.
The owner saw the replacement of his massive B & G circulator with the much smaller Grundfos and told me he wanted to keep the B & G "just in case".
If the installer had known what I know now, he could have used a B & G Series 100 circulator to satisfy the system requirements and reduced the owner's utility bill. But he probably wanted to make sure his system worked properly and erred on the side of expediency although the B & G "1½ HV" is really a high volume pump, able to flow over 35 gpm.
Two btu per sq ft for degree difference for a slab
Comments
-
My guess is that the dead men did just that...guessgwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.1 -
I'll take a stab that 90% of residential jobs are massively over pumped. The math doesn't lie, but it doesn't take much flow to move heat. The emitters only care what the average water temperature is, more pump and all you get it higher return temps.
Dont you just love hydronics? So much heat can be moved through such small pipes (3/8")!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Pressure diff x 2.31 = ft of head
7 x 2.31 = 16.17 ft of head
👍Steve Minnich0 -
That's the formula that I used, Steve. The pressure differentials were 3, 4 and 5 pounds respectively.Steve Minnich said:Pressure diff x 2.31 = ft of head
7 x 2.31 = 16.17 ft of head
👍8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Nice use of those ported iso-valves
Maybe they were designing for a 3- 5° ∆ with that large circulator.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks for turning me on to them, HR. I just wish they were ¼" tappings instead of ⅛".hot_rod said:Nice use of those ported iso-valves
Maybe they were designing for a 3- 5° ∆ with that large circulator.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
Good work you mad hydronic scientist!
There was an error rendering this rich post.
0 -
-
-
For the performance curve, did you use B&G's System Syzer?Steve Minnich0
-
The pump performance curves are shown on the lower image above.
I used the pressure drops to plot the duty points on each curve and ran a line through them to give me the system curve.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Not that difficult to determine a system curve and then select pump. But this obvious method is rare even on million dollar projects. Hope that Henry from Montreal sees this post.0
-
And most important the system curve over the pump curve defines the OP operating point of the circ.
Notice 5.5 where two circs would give you the correct flow, a high head and a flat curve, which would you select?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
#2?hot_rod said:And most important the system curve over the pump curve defines the OP operating point of the circ.
Notice 5.5 where two circs would give you the correct flow, a high head and a flat curve, which would you select?There was an error rendering this rich post.
0 -
#2 as well. Circulators with flat curves are more desirable when using zone valves . Flow will not change drastically as a function of opening and closing zone valves.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
For main circulator. Opposite situation for coil circ.#2 as well. Circulators with flat curves are more desirable when using zone valves . Flow will not change drastically as a function of opening and closing zone valves.
0 -
Great post/thread.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Where did you buy the flange with 1/8” tapping.0
-
I'd say you're right. Check this one out:Solid_Fuel_Man said:I'll take a stab that 90% of residential jobs are massively over pumped. The math doesn't lie, but it doesn't take much flow to move heat. The emitters only care what the average water temperature is, more pump and all you get it higher return temps.
https://heatinghelp.com/systems-help-center/adjusting-the-flow-rate-for-an-old-gravity-hot-water-system/
which led to this:
https://heatinghelp.com/systems-help-center/sizing-circulators-for-old-gravity-hot-water-heating-systems/All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Calefactio (means "warming" in Latin) is in Montreal and I couldn't find any out West, but finally scored in Salt Lake City. Hajoca at (855)982-1408. Ask for Vern.bob eck said:Where did you buy the flange with 1/8” tapping.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements