Were the Dead Men Wrong?
Alan (California Radiant) Forbes Member Posts: 4,006
edited June 2019 in THE MAIN WALL
This is a continuation of a thread about a Bell & Gossett replacement circulator.
Based on everyone's great advice, I replaced a 79-year-old B & G circulator that was leaking with a Grundfos 15-58 because I wanted a choice of speeds in case low or medium didn't work (see performance curves below). I added 30# gauges on the suction and discharge sides of the pump to determine pressure drop and the results were surprising.
I added the gauges out of curiosity. I didn't know the actual pressure drop of the system. Three-eighths tubing in the plaster ceiling was known, but was it 3/8" o.d. or i.d.? And how long were the loops?
As I said, the results were surprising. The pressure drops were:
Low speed: 7 feet
Medium speed: 9.3 feet
High speed: 11.7 feet
At low speed, the Grundfos satisfies the heating requirement of 3 gpm. I shot the ceiling with my infrared camera and it was all aglow.
The owner saw the replacement of his massive B & G circulator with the much smaller Grundfos and told me he wanted to keep the B & G "just in case".
If the installer had known what I know now, he could have used a B & G Series 100 circulator to satisfy the system requirements and reduced the owner's utility bill. But he probably wanted to make sure his system worked properly and erred on the side of expediency although the B & G "1½ HV" is really a high volume pump, able to flow over 35 gpm.
  • gerry gill
    gerry gill Member Posts: 3,078
    My guess is that the dead men did just that...guess
    gwgillplumbingandheating.com
    Zman
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    I'll take a stab that 90% of residential jobs are massively over pumped. The math doesn't lie, but it doesn't take much flow to move heat. The emitters only care what the average water temperature is, more pump and all you get it higher return temps.
    Dont you just love hydronics? So much heat can be moved through such small pipes (3/8")!
  • Tinman
    Tinman Member Posts: 2,808
    Pressure diff x 2.31 = ft of head
    7 x 2.31 = 16.17 ft of head
    Steve Minnich
    That's the formula that I used, Steve. The pressure differentials were 3, 4 and 5 pounds respectively.
    hot_rod Member Posts: 22,158
    Nice use of those ported iso-valves :)
    Maybe they were designing for a 3- 5° ∆ with that large circulator.
    edited June 2019
    Thanks for turning me on to them, HR. I just wish they were ¼" tappings instead of ⅛".
  • Danny Scully
    Danny Scully Member Posts: 1,425
    They make 1/8” gauges @Alan (California Radiant) Forbes :wink:
    Alan (California Radiant) ForbesSeanBeans
  • STEVEusaPA
    Good work you mad hydronic scientist!
  • Tinman
    F you want to be even more accurate, use a single gauge piped in parallel to the pump with a ball valve on each side. It lessens the margin of error.
    Steve Minnich
    Alan (California Radiant) ForbesSolid_Fuel_Mandelta T
    It's great. It was the first time I could draw a system curve on a pump performance curve.
    Oh, the things I get excited about!
  • Tinman
    For the performance curve, did you use B&G's System Syzer?
    Steve Minnich
    edited June 2019
    The pump performance curves are shown on the lower image above.
    I used the pressure drops to plot the duty points on each curve and ran a line through them to give me the system curve.
  • jumper
    jumper Member Posts: 2,260
    Not that difficult to determine a system curve and then select pump. But this obvious method is rare even on million dollar projects. Hope that Henry from Montreal sees this post.
    And most important the system curve over the pump curve defines the OP operating point of the circ.
    Notice 5.5 where two circs would give you the correct flow, a high head and a flat curve, which would you select?
  • STEVEusaPA
    #2?
    #2 as well. Circulators with flat curves are more desirable when using zone valves . Flow will not change drastically as a function of opening and closing zone valves.
  • jumper
    For main circulator. Opposite situation for coil circ.
  • JohnNY
    JohnNY Member Posts: 3,231
    Great post/thread.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • bob eck
    bob eck Member Posts: 930
    Where did you buy the flange with 1/8” tapping.
    Steamhead Member Posts: 16,843
    I'd say you're right. Check this one out:
    https://heatinghelp.com/systems-help-center/adjusting-the-flow-rate-for-an-old-gravity-hot-water-system/
    which led to this:
    https://heatinghelp.com/systems-help-center/sizing-circulators-for-old-gravity-hot-water-heating-systems/
    Consulting
    Solid_Fuel_Man
    edited June 2019
    Calefactio (means "warming" in Latin) is in Montreal and I couldn't find any out West, but finally scored in Salt Lake City. Hajoca at (855)982-1408. Ask for Vern.