Can someone help me with this pump ID? It's the larger one on top in the picture below. It's not a series 100 pump. It circulates water through 3/8" tubing in the ceiling plaster; maybe 1500 square feet.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
We call it a large B&G in the trade ... What is the problem ? Can we help you
There was an error rendering this rich post.
0 -
-
I thought so too, but I ordered this HV pump, but it's a Series 100.
https://www.supplyhouse.com/Bell-Gossett-102210-1-6-HP-HV-NFI-Circulator-Pump-5601000-p
The motor is the size of the lower circulator in the picture.
The problem is that it's leaking through a hole under the coupling assembly.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
That's a great help, Mike. I'd like to get a new impeller with that. Are there many to choose from?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
-
-
Not certain, but it looks like 1" or 1-1/4" pipe in and out of this HV pump. I agree with others, might be better off replacing pump with new. I'm guessing about ten or fifteen gpm at ten or eleven feet of head. I'd be careful not to choose a pump with less head. We often see HV pumps on systems with monoflow tees, due to the added restriction.0
-
HV pumps are relatively low head (15’ tops) with high flow.Steve Minnich0
-
B&G made a pump called 1-1/2. It's performance curve is on page 38 of their old manual: https://heatinghelp.com/assets/documents/Bell-and-Gossett-Handbook.pdfRetired and loving it.1
-
Work it backwards, how many btus is it moving, the size of the boiler or how much energy could be moved thru 1500' of 3/8 tube? I doubt you are moving 20 gpm, or need to. Follow the curve down to maybe 4-6 gpm. Plenty of small wet rotors will do the jobbed use a lot less energy, be maintenance-free also.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Sorry for the bad information, I somehow missed the 3/8" tubing in the ceiling part....0
-
Yeah, so the GPM is easy. Figuring the pressure drop is more difficult because I don't know how long the longest loop is.
If I go to my B&G System Syzer, scale No. 2:
- 3/8" tubing
- shows 1.7 feet of head at .4 GPM per 100 feet of tubing
Let's say they ran 250' of 3/8" tubing. That gives me 4.25' of head at let's say 6 gpm. So, like Hot Rod says, a small wet rotor pump will do the trick.
What gives me pause is why that smart, dead man who probably watched every nickel and dime he spent would choose such a large circulator.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Probably looking for high head to push it all through the small pipe. B&G came out with ode to deal with multiple Monoflo fittings and their cumulative pressure drop.Retired and loving it.0
-
So do I trust my numbers or his pump?DanHolohan said:Probably looking for high head to push it all through the small pipe. B&G came out with ode to deal with multiple Monoflo fittings and their cumulative pressure drop.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
I’m with Scott.Retired and loving it.0
-
So do I trust my numbers or his pump?DanHolohan said:Probably looking for high head to push it all through the small pipe. B&G came out with ode to deal with multiple Monoflo fittings and their cumulative pressure drop.
I like your number, but, a big but, it assumes 250' or less loops. Could be 500' loops is why they chose that circulator, or booster
Can you see any manifolds to determine the number of loops?
An accurate gauge across the pump could answer the unknown, if you want to go that far.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
A Taco 0012 has the same hydraulic performance as B&G HV. That would be a direct replacement, assuming that the HV was performing satisfactorily. A B&G HV is a heavy, rugged, costly, 3-piece pump that has been around for at least 70 years, but a modern wet-rotor pump such as the Taco 0012 would be a better choice for replacement, I think. The HV is oil lubricated, and has multiple moving parts - the Taco has one moving part, the cartridge, which is easily replaced, and is water lubricated.0
-
Dead men oversized everything. It was a way of life. See what I did there?Steve Minnich0
-
Is the tube 3/8 OD or ID? Typical 3/8" soft copper refrigeration tube is 3/8 OD, 1/4" ID. That would make a big pressure drop difference.
Closer to the old SolaRoll tube 200" loops and it still needed high head circ.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
That's a good questions. I did repairs on the tubing a few years back when the owner forgot to tell the electrician about the tubing in the plaster when he was adding lighting cans in the ceiling. My notes don't say the size and I forgot.
I should presume 3/8" refrigeration.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
If it’s copper radiant though its most likely 3/8” ID, right? That’s all I’ve seen in Chicagoland.Steve Minnich0
-
I had some copper couplings in my garage that I used exclusively for old radiant ceilings and floor repairs. The ID of the coupling is exactly 1/2”. That’s all ever used here.
The last near boiler repipe I did for this type of job was 3 levels, 2400 sf total. 3 zones and I used 007s on each zone. This was 6 years ago. House heats great.Steve Minnich0 -
I'm tending towards a Grundfos 15-58 on high speed.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I tend to stick with B&G around where I’m at. The main reason being all of the bearing assemblies / couplings / motors / impellers are readily available at several different vendors. Every time I need a TACO it’s hit or miss, usually not in stock anywhere.Never stop learning.0
-
Hi Mike
Thanks for expressing your concern when it comes to availability of products, and replacement parts. Taco understands the importance of having product on the shelf at Reps, and wholesalers locations.
I'm not sure where you're located, but please reach out to me so I can look into it, and make sure you find what your looking for in the future.
I'm available anytime at 401-261-4890.
joemat@tacocomfort.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions4 -
Hi @Joe Mattiello
I am in Northern VA. I service from Richmond, VA to Baltimore, MD, and sometimes beyond. Lots of Washington DC.
Commercial service. Residential and commercial sized pumps. I have several go-to vendors for larger B&G pumps, seals, impellers, bearing assemblies, and motors. Haven't had the best of luck finding larger Taco pumps and components in stock.
If you could point me in the right direction that would be awesome.
Never stop learning.0 -
Hi Mike
I'm the North East, commercial Regional Manager that works closely with Taco MFG rep, NH Yates, 117c Church Lane, Cockeysville, MD 21030, 410-667-6300
Matt Cornelius, is the Commercial manager, and works closely with Jim Yates. Collectively they have over 60 years experience with commercial systems, and products. they have been a Taco rep for most, if not all of those years. I would reach out to them with any product needs, and I'm confident they will have it in stock, or will get it within a reasonable time. I provided my contact information too, so I encourage you to call me if you need something ASAP. Thanks again for allowing me the opportunity to serve you.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions3 -
Thank you @Joe Mattiello
I believe I have dealt with NY Yates in the past. They're pretty far north compared to the area I cover most often.
I really appreciate it and will definitely give them a call! Thanks again.
Never stop learning.0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements