Old lineset
SeanBeans
Member Posts: 520
so I just bought a house in Colorado.. it is part of a condo community and I guess you had the choice to have AC installed at the time the buildings were built.
The Homeowners before me opted to have none.
The refrigerant lines are ran, from my attic to the side of the house.
They capped the lines up in the attic but outside... Nope.
The lines are open and the first few inches are filled with dust, pollen, and whatever else.
I don’t think I have the option to run a new lineset outside exposed so I’m thinking a really great flush?
What would you guys do?
The Homeowners before me opted to have none.
The refrigerant lines are ran, from my attic to the side of the house.
They capped the lines up in the attic but outside... Nope.
The lines are open and the first few inches are filled with dust, pollen, and whatever else.
I don’t think I have the option to run a new lineset outside exposed so I’m thinking a really great flush?
What would you guys do?
0
Comments
-
I'm betting R11 flush.SeanBeans said:so I just bought a house in Colorado.. it is part of a condo community and I guess you had the choice to have AC installed at the time the buildings were built.
The Homeowners before me opted to have none.
The refrigerant lines are ran, from my attic to the side of the house.
They capped the lines up in the attic but outside... Nope.
The lines are open and the first few inches are filled with dust, pollen, and whatever else.
I don’t think I have the option to run a new lineset outside exposed so I’m thinking a really great flush?
What would you guys do?
What sizes are the lines and what size unit do you need?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I wouldn’t chance it. The POE oil used today is a cleaning solvent so anything in there WILL come back to the compressor.
If they insist a filter drier at the air handler and suction filter at the compressor. At least one change of both!0 -
-
-
0
-
Thanks guys!
I kinda figured I would be flushing and blasting with nitro.. probably do it a few times to be safe0 -
I don’t like flushing anything because then you have the flushing agent to deal with, I’ve found blowing the lines out with Nitro works just fine, even on 22 to 410 conversions. Put a suction drier in for a couple weeks and a liquid drier before the txv and you’ll be fine.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements