Question for the engineers re makeup air units
Or am I wrong in my assumption of the purpose of the stats, or my analysis of what will happen?
Comments
-
This is my take on make-up air systems and I am sure others will take issue with it. And I realize many are not installed this way
I don't look at make-up air units to "heat a space" To me a space should have it's "own " heating system that will heat the space based on it's heat loss.
The MU air unit supplies only "replacement" air.= the amount of air being exhausted.
For instance a kitchen could have it's own heating system used to heat the kitchen during off hours when the kitchen equipment and exhaust hood is not used. When the kitchen hood is turned on to exhaust the MU air units starts and brings in the amount of outside air that pretty much matches the exhaust air. You might run the discharge air at 70 deg
The 80/20 units are called that because these are direct fired to limit the CO in the air the outside air used cannot fall below 80% of the units capacity...they want to make sure the have enough dilution air for the CO. So your allowed to use up to 20% return air to save fuel.
Not sure how the controls are set up I have not seen one in a while but I would think if the OA is cold and the gas is on Hi Fire and the discharge temp drops the OA damper could close down to 80% and take20% return.0 -
Right, they're not for space heating. (The general on this latest job is going to be sad, he wants the space warmed up & the humidity lowered…)
All that makes sense re outside air and everything. What I can't wrap my head around is why drive to 100% outside air when the return &| outside air temp is low. Every one (that I've come across) that has a return or outside air thermostat does the same thing. I've got a hard time believing that the Old Guys who though up these units got it wrong but for the life of me I can't come up with a reason for it.
0 -
All 100% MU air units drive to 100% OA whenever they run. The CFM they move is supposed to be matched with the proper btu input to "keep up" Amount of air they bring in is not based on OA temp
80/20 can take a maximum of 20% return air for dilution air yada yada.
Not 100% sure how they control those.0 -
These are 80/20 for building pressurization control, as building pressure rises bring in less outside air, up to 80% return air. That part makes sense. But I can't understand the reasoning for driving to 100% outside if it's cold out—it's more likely that the discharge air temp will drop due to the inability to heat the (presumably sub zero) outside air as warm as trying to reheat 20% outside air + 80% return air that will probably be somewhat to significantly warmer than the outside air.0
-
@ratio,
I apologize I was wrong and your right. 80/20 is minimum of 20% outside air I had it backwards.
Well for building pressurization I think the controls look at building pressure and bring it whatever OA is needed to maintain the pressure. The MU air unit should be set up to be able to heat the replacement air up to a minimum of 55-60 deg I would thing and the building system can do the rest0 -
Keep firmly in mind when you are looking at these things that they are not there for heating and, unless they are coupled with a sensible heat heat exchanger, don't even pretend to be efficient in that regard. They are there to maintain indoor air quality.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I'm not explaining my question correctly. What are the benefits of firing at 100% outside air when the outside air temperature is below (say) 58° when you are guaranteed not higher than 90° discharge air? (real numbers from current job) My opinion is that you are only guaranteed to increase fuel consumption & that net heat to the building will suffer once the firing rate of the unit can not meed the DAT setpoint due to a depressed inlet air temperatures, because you will be relieving warm air that could be recirculated.0
-
I suppose I am getting hung up on discharge air temperature, but even with that in mind, how would air quality be better served by going to 100% outside air just because it's cold, either in the space or outside?0
-
Can't answer that one, @ratio -- unless for some reason someone thinks they need that much makeup air when it's real cold And I can't think why...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Make up air is replacement air heater only and in most cases is not to provide building heat only to heat air brought in to replace what is exhausted or to pressurize building depending on the controls.
This is an "engineered design" and as such most of us service/installation guys are rendered stupid. We are on a need to know basis and we don't need to know.
But seriously I would need the original building drawings or design to get into the engineers brain and figure it out.
usually MU air is used for kitchens, factories (fumes, smelly stuff etc being exhausted) process or something like that. Building pressurization to prevent negative pressure (doors won't open) (smelly elevator shafts) Sometimes building are sold or change of use and then their are issues.0 -
So it's not just me then!
Ok, guess I'll go back to wondering about it. I kinda think it might be some kind of mistake to have it respond that way, but without some confirmation I'm not gonna say 'That's dumb!'
0 -
@EBEBRATT-Ed, this is a factory control feature, not a building design decision. It appears to be a response to a concern that the building is (or is about to become) cold. I think it is based on a mistaken belief that burning the most fuel will keep the place the warmest, but I don't think that's the case if we are discharging air that is cooler than would be if we were recirculating some.
It just bugs me to not know.
0 -
Ratio, I’ve never seen one with the control you’re describing. I’ve seen them with space sensors that reset the DAT to accomplish some space heating. The only thing I’ve ever seen controlling the OA/RA ratio is building pressure. What is the make/model of the unit you’re taking about? Or have you seen this from more than one manufacturer?0
-
It's a Rupp RAM-M 27 w/ 80/20 return for building pressurization control. Here's the schematic, TS-09 factory setting is IIRC -25° & TS-10 factory setting is 58°. While they have a design max of 90° DAT, they have a max ΔT of 115° so we can do that 90° for quite a while, but if the ambient drops below -25° our DAT will drop & I believe at that point, we're likely going to be relieving heated air that we could have kept in the space by recirculating & the net heat input to the space will be less than it could have, even though we'll be burning more fuel.
NB: This unit has a larger ΔT than some of the others I've come across with a similar configuration.
0 -
Does the return air flow through the burner of this unit? And is the return air actually being directly exchanged for outside air? If the answer is no to these questions, then it would make sense that the OA damper opens to 100% when the return air temp drops, since this will provide maximum output from the burner. Presumably the unit would be designed/spec'd such that the outlet temperature would be greater than the indoor space under worst case conditions.0
-
PS-0 runs the damper motor and is running the show to control building static. The gas follows to keep up. @-25 discharge of 90 should be fine. Even if you drop to -45 you could still discharge 70 degree air.
the way I see it the unit is first & formost designed to control building static and heat replacement air. No for heating the building, not for comfort not for energy savings.
What I can never understand is why they don't use a heat recovery ventilator in conjunction with a MU air unit. A heat recovery wheel will recover 80% of the exhausted heat0 -
The units might be direct fired. So they need to bring in fresh air when firing above a certain rate.
Also might have a maximum temp rise value.
OF the programmers, general and engineers failed to communicate the function or wrote the specs wrong. This is how EVERY project I’ve worked on has been. There little common sens among designers because it all about meeting some building code, misinterpreting or not completely following the full code with it’s exceptions, or just being cheap or lazy.
I left my last job because I got tired of arguing with my boss who believed the engineers were smart and there fore knew all and were infallible. I showed him hard data why they were wrong. Oh well. His problem now.0 -
Right. Now, I'm pretty smart, so when I come across something that doesn't make sense my first impulse is to assume that I'm right; but I also know that there are lots of people smarter than me (including some engineers ) so my second impulse is to try and figure out if I'm wrong or not. I'm at that stage right now. I can't see a benefit to driving to 100% outside air as determined solely by return/outside air temp other than consuming more fuel.0
-
It occurred to me the other day that this function (driving to 100% outside air [as opposed to up to 80% return air] based on outside &| return air temp) might not be a heating response but rather a building pressurization response. Certainly any chance of negative building pressure is to be avoided in freezing conditions due to the possibility of infiltrated air freezing pipes, etc. This is at least a plausible explanation.0
-
Commercial kitchens and factories are different. Most use direct fired units and move so much air that the CO could not possible be an issue.
Natatoriums ,ice rinks and surgical centers are also different animals. Humidity, air change rates and space pressure are super critical.
For most other spaces, the engineer is just using the Ashrea or IMC requirement for the occupancy type and designing a system that makes those air change rates during occupied periods. In most systems, they just bring in OA at a fixed rate unless in economizer mode where they are using additional OA to cool. I have seen some systems that have supplemental baseboard heaters for additional heat, some use the AHU, recircing some of the air.
The world would use much less energy if the OA requirement was actually controlled by indoor air quality. I always recommend that customers consider controlling OA using CO2 sensors. That way you only bring in and heat what you need. For commercial kitchens, they make some great detection systems that ramp everything up and down based on what is being cooked."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Yes, the 80/20 units are just there to match the CFM of air being exhausted from the building. Technically they are near 100% efficient as that are direct fired..... But the burner is just there as to not discharge -20F air.
I've installed several for a national pizza chain, where we used a differential pressure sensor (outdoor/indoor) to generate a 4-20ma control signal which drove a VFD on the fan. The burner was modulated via discharge air temp. This would be a 100% OA setup.
There are also some which are more like air handlers. They have fixed speed blowers and use the OA damper to maintain indoor air pressure or quality. There are also condensing furnaces so as to avoid direct fired units.
I use/see the direct fired units in industrial settings. Remember that OA is required and yes it burns a ton of fuel to heat it up, but air is being pulled out of the building somewhere for a specific reason as well, so fuel consumption is not the concern here. Most places with a setup like this couldnt make used of an economizer HX due to major contamination of the HX.
Different altogether than a commercial building with just people causing poor IAQ.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Categories
- All Categories
- 85.9K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 78 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 94 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 59 Pipe Deterioration
- 886 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements