75 PSI relief too high?
Jopom
Member Posts: 1
in Gas Heating
Home Inspector mentioned this, I don't want to bring it up to the association without some merit.
3-story building, 12 units, 1 weil-mclain boiler that heats all units and a large water heater...
Inspector said the relief valve was rated for 75 psi, yet the "MAWP" for the boiler is 50psi.
Is this worth mentioning to the association? I'm moving in and don't want any bad first impressions, although it'd help if I was a hero
Thanks!!!
3-story building, 12 units, 1 weil-mclain boiler that heats all units and a large water heater...
Inspector said the relief valve was rated for 75 psi, yet the "MAWP" for the boiler is 50psi.
Is this worth mentioning to the association? I'm moving in and don't want any bad first impressions, although it'd help if I was a hero
Thanks!!!
0
Comments
-
yup0
-
-
It’s perfectly fine if they want to take a chance of blowing up the building. Seen those stories on the news of boilers blowing through the roof? These are the types of things that lead to that.
You may also want to mention to them whoever is working on their system is incompetent.1 -
If indeed the boiler is rated 50 and it's a 75lb valve it must be changed. Not impossible for a contractor to make that mistake but it is a stupid and dangerous mistake. relief and safety valves are the most important valves on any boiler....the last line of defense
Do yourself a favor and take pictures of the relief valve tag on the valve and the boiler name plate and compare the two and you can show the other association members
It is also not impossible that the inspector read the tag and nameplate wrong so double check it0 -
What model Weil McLain is it?Never stop learning.0
-
50# boiler is commercial..........
Why is a Home Inspector even looking at that? Well out of his field!
Shouldn't it be inspected by a licensed and insured contractor before being inspected by the JHA!0 -
If someone put a 75# relief valve on that boiler I'll bet you buckets of money it's because there's been an ongoing problem with controlling the pressure rise of the system when the boiler is operating. I advise the building get someone to evaluate the expansion tank sizing and static fill requirements to start. After that, piping configuration, pump values, and dynamic pressure changes need to be verified.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
And if the boiler won't handle the needed static pressure after evaluation a heat exchanger, another expansion tank, water feeder, and pumps will fix it
$$$$$$0 -
I don't remember the model but I did a new Viessmann commercial boiler installation with a provided and recommended 70psi relief valve.
Inspector did not pass the inspection. Was made to replace the relief valve. I don't remember why the relief valve was rated so high.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements