heat not reaching one radiator

Pegret
Pegret Member Posts: 37
Had a new Weil-McClain steam boiler installed in my 1928 house. It's been a huge struggle. Voilent banging pipes and water gushing all over floor. Plumber tried many things and finally repiped correctly (according to manual) and it's now working fine except...one radiator comes on only if I turn the thermostat up 3 or more degrees at once. Even then it's the last one to come on and sometimes only warms 3 or 4 columns. But sometimes it heats completely. When maintaining the same temp., it never works at all. Of course most of the time I keep it at one temp so this means most of the time it's cold! There's no problem with the radiator itself- plumber confirmed today that the radiator and vent are fine.
The radiator is located in an addition on the first floor, surrounded by windows and is my favorite room. Today plumber turned vents to 1/2 positions on other radiators on first floor thinking the thermostat reads warmth from them before this rad has a chance to come on. Interesting theory but, once again, when I kept temp set and a new cycle came on, the rad didn't come on. I've been on the phone with Weil-Mclain technical services several times and they can't figure this out, either.
efb203

Comments

  • JohnNY
    JohnNY Member Posts: 3,294
    edited January 2019
    It can really only be a venting issue. The radiator needs to be vented more quickly with the largest vent(s) available and the radiator closest to the thermostat should have a restricted air vent, i.e. a smaller, slower vent.
    It is usually possible to add a second vent to a slow heating radiator.

    Weil-McLain can't help you with this because it's likely not a boiler problem. It's a system problem. A good steam guy will knock this out right away.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    kcoppethicalpaul
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Your problem radiator is in an addition to the house?
    The rest of the system works?

    The addition may be under piped.
    There is a limit to the length of runout pipe without increasing to the next larger pipe size. Easy to exceed that point.
    wcs5050
  • Jamie Hall
    Jamie Hall Member Posts: 24,878
    And any chance of water trapped in the feed to the radiator? All your slopes are good?

    As @JohnNY said, this has nothing to do with the boiler.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • JUGHNE
    JUGHNE Member Posts: 11,279
    One church I service has mirror image of piping and radiation on the east and west sides.
    One difference is the last rad on the east has a 2" runout of about 15'. That rad is last to heat, then only part way and only if call for heat is longer as in coming out of setback. It also has a little water hammer the longer it heats.
    By the book it should have a 2 1/2" runout.

    The last rad on the west, same size, has a 2" runout of only about 8'. It heats fully without problems.

    When you mentioned addition to the house how far is it from the
    problem rad to the main in the basement?

    Three things helped with the problem rad;
    Adding about 12 G2 steam main air vents, (a lot of large pipe) Putting a slow Hoffman air vent on problem rad.
    Insulating piping with 1" fiberglass.
  • Pegret
    Pegret Member Posts: 37
    Wow thanks for all the ideas. Can anyone explain why this radiator works fine when I increase the thermostat by approx 3 or more degrees, but doesn't work when simply maintaining the same heat?
  • JUGHNE
    JUGHNE Member Posts: 11,279
    In my case I believe that happens because the longer run time heats the run out pipe enough to get the steam to that rad.
    The pipe has to "become a radiator" first.
    It is counterflow, in that the steam has to meet the returning condensate water. It gives up some heat as the two meet inside the pipe. The longer the pipe, the more time needed.

    Could you move your thermostat to the cold room?
    What do you have for main air vents in the basement?

    wcs5050ethicalpaul
  • KC_Jones
    KC_Jones Member Posts: 5,840
    Main venting, need to start there and go up. @JohnNY said it right, a good steam guy fixes this easily.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Jamie Hall
    Jamie Hall Member Posts: 24,878
    Time. Pure time. It just takes that much longer for the steam to get to the radiator.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Pegret
    Pegret Member Posts: 37
    Mystery is when I had the old 1928 "snowman" boiler, which was replaced this summer with this new Weil-Mclain, there was never a problem with heat getting to this radiator. Now I have a brand new boiler but my livingroom is cold because of this one radiator
  • KC_Jones
    KC_Jones Member Posts: 5,840
    How did they size the new boiler?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • KC_Jones
    KC_Jones Member Posts: 5,840
    Also what is the pressure set to on the pressurtrol?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • coelcanth
    coelcanth Member Posts: 89
    jughne touched on one problem i experienced, which was that boiler run time was too short to get steam to my furthest radiators, even after my main venting was upgraded.. might be related or at least part of the issues you are seeing..

    so i would check the length of the normal heat cycle when you are not getting satisfactory heat and determine what is signalling for boiler to cut out. might be as simple as the thermostat being satisfied because the vents in that room are too quick or might be something like an anticipator or CPH setting keeping the boiler run time too short.
    that could be why the steam reaches the trouble radiator when the heating cycle is long (recovering from your 3 degree setback).

    other things could cause the boiler to cut out too early, like a LWC triggered by a surging waterline or an actual low water condition.. or a pressuretrol set wrong or triggered by an oversize boiler. these less likely since it sounds like you and your plumber have been investigating
  • Pegret
    Pegret Member Posts: 37
    pressure is 1/4 cut in and 1 cut out. Its a 98,000btu for an 800 square ft house. Water level has be right. Plumber thought of the other vents in area being too quick for the slower radfiator so we turned thme 1/2 closed. Didn't work. Thankful for all these thougths which I will bring to my plumber. I'm going to time a normal heat cycle.
  • BobC
    BobC Member Posts: 5,502
    It's best to vent the steam mains fast and the radiators slowly. What kind of radiator vents do you have? If they are heatimer's you may be in trouble because they are very fast and hard to adjust at the low end.
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • pecmsg
    pecmsg Member Posts: 5,298
    Pegret said:

    pressure is 1/4 cut in and 1 cut out. Its a 98,000btu for an 800 square ft house.

    Thats a lot of BTU's for a little Sq Ft

    How long from cold start to shut down?
    KC_Jonesethicalpaul
  • Pegret
    Pegret Member Posts: 37
    I think 17 min. cycle for cold start to shut down. Haven't timed recently, but last I checked it was 17 min. which seemed long to me but I don't know what it should be.
  • pecmsg
    pecmsg Member Posts: 5,298
    At design condition 0 cycles.
  • KC_Jones
    KC_Jones Member Posts: 5,840
    I asked earlier how the new boiler was sized, I’m guessing it’s oversized.

    My guess, lack of main venting and too big of a boiler.

    Old boiler worked “fine”. New boiler does not. New boiler is oversized, producing steam at a faster rate. This is running the pressure up higher faster than the old one. The steam is looking for a place to go so it fills the closer rads quickly, satisfies the thermostat, shuts off boiler and the last rad never gets steam.

    Need to find out if they sized the boiler properly, they will say yes so the only way IMHO is for you to run the numbers which isn’t hard. After that need to look at main venting, ignore the rad vents for now they don’t do you any good until the main venting in the basement is correct.

    Also please post pics of the new boiler and it’s piping so we can verify it was properly installed.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Dave0176
    Dave0176 Member Posts: 1,178
    @Pegret what model Weil-McLain boiler do you have ?
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Pegret
    Pegret Member Posts: 37
    my house is 800 sq ft w 3 radiators upstairs and 4 rads downstairs - it's a wiel-mclain peg45 series 5. with150,000 btu. wiel-mclain technical services said all I needed was 98,000btu but the 150 wasn't exorbitantly too big to function properly.
    (Can't do pictures til I can use my own laptop which is being fixed.)
  • Pegret
    Pegret Member Posts: 37
    There is a main vent near the boiler that is new and appears to be working
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Is it on the smaller return piping?
    You should maybe hear it passing air for a few minutes after boiler fires until steam gets all the way around the piping.

    I ask because sometimes they are wrongly put on the steam main right at the boiler....it has happened.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Not only should the main vent work, but it should be the right size. Bicycle tires are round, made of rubber, and filled with air; but won’t work on a car.—NBC
  • KC_Jones
    KC_Jones Member Posts: 5,840
    > @Pegret said:
    > my house is 800 sq ft w 3 radiators upstairs and 4 rads downstairs - it's a wiel-mclain peg45 series 5. with150,000 btu. wiel-mclain technical services said all I needed was 98,000btu but the 150 wasn't exorbitantly too big to function properly.
    > (Can't do pictures til I can use my own laptop which is being fixed.)

    To size the boiler all the rads in the house are to be measured, the total EDR of the radiation is then compared to the boiler rating. This is the proper way, I’m not following what your stating exactly. If you needed 98 and put in 150 I would call that massively over sized.

    Again all the rads need measured to do it properly, I’m guessing that wasn’t done?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Pegret
    Pegret Member Posts: 37
    Radiators were not measured. The plumber who gave the first estimate for the job measured every radiator. He dissappeared when he saw aesbestos pipes, didn't return calls. So second plumber came out and did not measure radiators and I asked him why and he said not necessary and I think he said he goes by house sq footage. So frustrating - it would be nice to be able to trust the pros since I know zero about plumbering.
    Now I'm worried that no matter how well all problems are resolved it will never run at highest efficiency.
  • Dave0176
    Dave0176 Member Posts: 1,178
    edited January 2019
    Your radiators need to be measured to come up with an EDR. Then you can compare to the boilers output of 392 EDR, that particular WM boiler is 150,000 input, with 125,000 output and 392 sq ft of steam. When we size a boiler for replacement we never use BTU, it’s always sq ft of steam or (EDR)
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • KC_Jones
    KC_Jones Member Posts: 5,840
    Pegret said:

    Radiators were not measured. The plumber who gave the first estimate for the job measured every radiator. He dissappeared when he saw aesbestos pipes, didn't return calls. So second plumber came out and did not measure radiators and I asked him why and he said not necessary and I think he said he goes by house sq footage. So frustrating - it would be nice to be able to trust the pros since I know zero about plumbering.
    Now I'm worried that no matter how well all problems are resolved it will never run at highest efficiency.

    It doesn't go by square footage for any heating system, so he is 100% wrong every day of the week. Hack's are among us.

    If you want to calculate your radiator EDR we can easily help with that exercise so you can get an idea of where you are at. I'm betting it's over sized.

    You are correct you will only get it so good if it is over sized.

    Honestly, I'd take the measurements, then put the contractor to task and show him with numbers how he did it wrong. Then see what he does, it should be fixed on his dime as it's his mistake. Weil Mclain actually has a boiler sizing sheet available on their website, you could fill that out then show it to him. I'd really love to hear how he would argue with the manufacturer about it.

    Have you made final payment?

    When you are able to post pictures please do so.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    ethicalpauladasilva
  • ethicalpaul
    ethicalpaul Member Posts: 6,672
    edited January 2019
    This doesn't sound good. Sq feet isn't a good comparator, but I have a two storey wood frame house that is about 1400 sq ft and my boiler is 112k btu and is oversized by 20-30%.

    I bet 98K BTU is oversized, but probably OK (as in, it was typical oversized that is in a majority of houses). But 150k BTU in an 800 sq ft house sounds insane, like WAY off the charts.

    Edit: I am still slightly confused at the size...I think @Pegret said it was 98k and then later said it was 150k. So to me, 98k = too big but could work and 150k = !!! danger Will Robinson

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Dave0176
    Dave0176 Member Posts: 1,178
    You can size the radiators yourself here is a chart I use and it includes basically the most popular radiators.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Pegret
    Pegret Member Posts: 37
    Don't know what all this btu information is but this is what catalog says for Model 45

    Max Input BTU=150,000 BTU
    DOE Heating Capacity=125,000 BTU
    Net I=B=R= 94,000 BTU
    AFUE 82.9%

    so is bottom line that the BTU is 94,000?
  • Fred
    Fred Member Posts: 8,542
    The 94,000 BTU is the amount of BTU's available for the Sq. Ft. of steam, not counting the 33% pipe and Pick-up factor. 94000 divided by 240 BTU's per EDR = 392 Sq. Ft. or 392 EDR
  • KC_Jones
    KC_Jones Member Posts: 5,840
    The only way to know where you are at is to measure the radiators using the chart that Dave posted.

    For anecdotal information, I have a 1500 sq ft house and a smaller boiler than you, and honestly I could have used a smaller one and still been ok.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    ethicalpaul