Need Help! - 2 Wire Boiler with 3 Zone Valves - WIFI INSTALLATION
jeveritt54
Member Posts: 5
Hi,
I am really hoping someone can help me. I have had zero luck trying to install wifi thermostats at my house. I am trying to install 3 Ecobee 3 lite's. I have a 2 wire boiler, heat only, and 3 zone valves. I have attached a drawing of how my system was wired with battery 2 wire thermostats, which worked fine. After numerous discussions with Ecobee I ran new 18/5 wire so I could have 4 wires at the thermostat for power for the Ecobee. I have also attached a drawing of how I thought it should be based off of what Ecobee is telling me. Long story short, I cannot get this to work. The Ecobee powers up fine, sends a heat signal, but the boiler is not kicking on, or not getting a signal to turn on. I'm sure its somewhere in the wiring, but I can't figure it out and Ecobee hasn't been helpful at all.
Please help!
I am really hoping someone can help me. I have had zero luck trying to install wifi thermostats at my house. I am trying to install 3 Ecobee 3 lite's. I have a 2 wire boiler, heat only, and 3 zone valves. I have attached a drawing of how my system was wired with battery 2 wire thermostats, which worked fine. After numerous discussions with Ecobee I ran new 18/5 wire so I could have 4 wires at the thermostat for power for the Ecobee. I have also attached a drawing of how I thought it should be based off of what Ecobee is telling me. Long story short, I cannot get this to work. The Ecobee powers up fine, sends a heat signal, but the boiler is not kicking on, or not getting a signal to turn on. I'm sure its somewhere in the wiring, but I can't figure it out and Ecobee hasn't been helpful at all.
Please help!
0
Comments
-
Can you post some pics of the zone valves and wiring?
This may be your best solution:
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Taco-ZVC404-4-Brochure.pdfBob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Added a picture of the zone valves. There is also 2 other pictures, 1 working, the other doesn't work with new thermostats.0
-
They seem to recommend an isolation relay for your installation.
A Taco 4 zone panel would make this much easier.
When the thermostat calls for heat, do you get 24V from Rh, and when it's not, no voltage from Rh?
Seems like 24v goes into Rc, does it come out of W or Rh when the tstat calls for heat?
Despite the drawing, and it's not my thermostat to fry, I would put Rc from transformer, W to terminal 1 in the zone valve, C from tstat back to transformer. And terminals 2 & 3 on the zone valve, T-T on the aquastat, and C on the transformer like your first drawing.
Edit: If no one pops on to correct me, I would try one thermostat first, make sure it's working, then the others.There was an error rendering this rich post.
0 -
Attached is what Ecobee sent me or recommends. Supposedly if you take RH and W and wrap them or wire nut them it should manually work. So I am assuming it comes out of RH and back on W, but I am not sure.0
-
Thinking "in" and "out" may be your problem. Think instead of the thermostat as being a switch. If it is turned on -- the switch is closed -- it connects W to either Rh (if heat is wanted) or Rc (if it's cooling you're after). It doesn't matter which way the current flows through the switch -- in fact, it flows both ways, since it's AC -- but it does matter that if you want heat, you want power to flow from your transformer through the heat switch to the zone valve and back to your transformer.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
and to clarify for the OP -- "dry contact" means no voltage applied to either terminal. Just a plain vanilla switch -- which is what the old thermostats were.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements