What's Wrong With This Picture
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
Comments
-
Only one takeoff?
Rusty sections?
Not on a concrete pad?—NBC0 -
Weil-McLain flipped us the bird!!! More maybe coming on that!!!!DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
Went to the 63 series myself.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
We love our Weil distributor. But not enough...
On to Peerless 63 series.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com1 -
They missed a hole0
-
-
-
That seems a bit much to me.
My argument was EG-30 - 55 is fine with one 3" tapping.
But EG-75...........I don't think I'd want one like that. I thought they were only doing this on the smaller ones? Didn't they previously require two risers on one of these in the manual?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
pfft, a real tech would just drill and tap another one...
JK!.......0 -
I work in a machine shop and we could easily do that here without buying a $500 tap + a several hundred dollar drill.ch4man said:pfft, a real tech would just drill and tap another one...
JK!.......
However, I'm sure it'll still void the warranty on the block.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Was this one a surprise to you like what happened to Dave? Did you pack it back up and return it?
If they did testing and found that one performed fine compared to two it still seems like they’d want to let installers pick the side!! Of course they wouldn’t want to have to stock/track two different models for that so the answer would be to have two holes! This story writes itself!NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
So they bolted and sealed it before they realized somethings wrong?0
-
Side question: is this a 5-section or do you count the end units also?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I have a question, and I’m not fluent with steam, but I’ve been following the bird thread
If WM did this to save money. How much did they spend changing the installation manuals?.........
I’m not sure how the manufacturing process worked from casting section to drilling, and tapping the section. Same people? Shipped to another facility to do the machining ?
That’s a large chunk of cabbage they are saving by shipping only half as many of that casting for machining,? Let alone the cost of the process.0 -
What kind of plugs/caps are you using on that boiler? They look smooth? @New England SteamWorks0
-
7 sectionethicalpaul said:Side question: is this a 5-section or do you count the end units also?
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com-1 -
Is that a HW boiler?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
> @ChrisJ said:
> Is that a HW boiler?
It could be with hot water trim. But this one has the steam trim.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
What are you gonna do with it, install it or return it?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I actually don't think the water line will slope that much in that boiler. EG-75 according to W-M puts out 249,000 btu/hr steam. At 970 btu/lb to evaporate water that is 256 lb/hour of water which at 8.33 lb/gallon is 30.8 gallons per hour or 1/2 gallon per minute, roughly. Without measuring or looking up the specs the steam chest (circular section running front to back) looks to be about 2 times the 3" outlet opening or about 6" in diameter. When steaming, the roughly circular boiler sections would be about 1/2 full or a water flow area of about 0.2 square feet. If all the water flowed in at the front of the boiler, was heated to steam and only exited the boiler at the back in one 3" steam outlet the water line would be depressed much less than 1/4" from front to back, just using pretty common Manning (gravity flow) equation formula for flow in a half pipe section. Think of it in common terms how much would the water line in a half 6" diameter pipe drop in the roughly 30" length front to back of the boiler if only 1/2 gallon per minute were running in that 1/2 pipe (common garden hose is about 5 gallons per minute, common faucet about 2 gallons per minute). But it is probably much less slope than that as the condensate return comes in about half way back the boiler not at the extreme opposite side to the outlet. The W-M engineers probably calculated this water line slope and found it was a very small fraction of an inch so decided to use only one outlet. Of course that doesn't eliminate the problems of piping flexibility which is eliminated with just one outlet, a valid point for installers.
Another way to think about it is: if the steam velocity for this boiler is acceptable in one 3" outlet (as far as producing dry steam--I haven't checked the tables on that as LAOSH is at home) then the steam velocity in the steam area above the water line is one half the velocity in the 3" steam outlet (if the steam chest circular area is in fact about the equivalent of a 6" diameter pipe--eyeball-o-metric measurement from the photo).
I'm not a boiler designer but have some facility with hydraulic calculations.
Maybe @Jamie Hall would like to weigh in on this.1 -
> @Ironman said:
> What are you gonna do with it, install it or return it?New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com1 -
No choice. The old boiler had asbestos, so the abatement company removed it the prior day. So no heat when the surprise showed up.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com1 -
Of some interest: this counterflow has no drips. Instead the supplies where upsized by a factor of two. The largest main is 4”.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com2 -
They still have the second return tapping. 34 fps @ 1psi0
-
So.
How did it seem to run with clean water?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
-1 -
Beautiful, as always. Shouldn't the smaller flue pipe from the water heater be above the larger flue pipe?...just wondering.
There was an error rendering this rich post.
0 -
-
Keep your ears open for more information on this. Reason may prevail.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements