Weil-McLain flipped us the bird
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
Comments
-
Will they let you order it differently? They have to be tapping that section for some of the boilers.
I am guessing due to high demand of lower quality work they made this change. But hey it's cheaper which is what most people want right? They need the money for useless granite counter tops.1 -
Any chance it was a mistake and somehow that section got shipped?
I guess they will be making a limited amount of tapped versions just for the larger boilers?
@Dave0176 Out of curiosity, have you piped an EG-45 with just a single 3" riser? I think that was the largest that allowed a single, no?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Wow, that is a big mistake, on their part. It won't take long for them to realize that. Did they also reduce the price of those units or are they saying it helped them to not have to raise the pricing? Lower product cost by these kinds of design changes rarely make up for lost sales volume or lesser market acceptance.0
-
Why?Fred said:Wow, that is a big mistake, on their part. It won't take long for them to realize that. Did they also reduce the price of those units or are they saying it helped them to not have to raise the pricing? Lower product cost by these kinds of design changes rarely make up for lost sales volume or lesser market acceptance.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
> @ChrisJ said:
> Any chance it was a mistake and somehow that section got shipped?
>
> I guess they will be making a limited amount of tapped versions just for the larger boilers?
>
> @Dave0176 Out of curiosity, have you piped an EG-45 with just a single 3" riser? I think that was the largest that allowed a single, no?
I kinda thought it was a mistake myself, that is until I called the supply house and they said they found that out yesterday on a Williamson. They then called the Rep and he said it’s no mistake.
This is per the manual minimum
The EG30/35 uses one 2” riser and header.
The EG40/45/50 uses one 2-1/2 riser and header
The EG55/65/75 use one 3” riser and header
Obviously the right end sections have to be tapped for the EGH series so I suppose there going to have two different part numbers now.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
> @Fred said:
> Wow, that is a big mistake, on their part. It won't take long for them to realize that. Did they also reduce the price of those units or are they saying it helped them to not have to raise the pricing? Lower product cost by these kinds of design changes rarely make up for lost sales volume or lesser market acceptance.
No all Weil-McLains boiler products rose about 5% this year.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
A prime example of Corporate greed. Lesser product for more cost. Maybe this is a phase out strategy for the EG series products? Diminish demand while selling what you can to those who will still buy??Dave0176 said:> @Fred said:
> Wow, that is a big mistake, on their part. It won't take long for them to realize that. Did they also reduce the price of those units or are they saying it helped them to not have to raise the pricing? Lower product cost by these kinds of design changes rarely make up for lost sales volume or lesser market acceptance.
No all Weil-McLains boiler products rose about 5% this year.0 -
Dave I just did a eg35 bout 2 weeks ago n was surprised to also find only one 3 inch tapping I really don’t use Weil much so it had been a while n I was sadden to only see one tapping. I was doing the install for a buddies company I usually use peerless I did like the weight difference I was tossing that 35 around it felt very light in comparison peace n good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
Is it possible their engineers found that there was no benefit to dual ports for those sizes?
OR
Their research showed them that 95% of units were getting plumbed only using one port anyway (and in copper, and incorrectly laid-out) so they figured why fight it? (As KC basically said)NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
> @ethicalpaul said:
> Is it possible their engineers found that there was no benefit to dual ports for those sizes?
>
> OR
>
> Their research showed them that 95% of units were getting plumbed only using one port anyway (and in copper, and incorrectly laid-out) so they figured why fight it? (As KC basically said)
Paul, yes from its inception in 1976 the EG35-75 series only had a recommended minimum of one riser. But it was nice having those two 3” tappings there.
This more than likely was a money saving effort, they don’t have drill, tap, or purchase and install the 3” Ward plug any longer.
They’ve been doing this all along on the SGO oil series of boilers, only one 2-1/2 tapping from the SGO3-5 series then on the 6-9 it’s tapped.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......-1 -
-
-
> @STEAM DOCTOR said:
> O wow. Not good. Williamson has been my go to steam boiler. Guess that I will also be switching to Peerless. I guess now they are truly peerless. For what it's worth, the Weil Mclain brochure still lists both supply trappings. Do they still have the return tapping on the right side?
You know I wanted to see but I didn’t feel like taking the side jacket off the boiler off.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
Wonder how many EG's sold were steam vs water and if this had anything to do with it.
0 -
I assume your supplier was OK with taking it back?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
> @ethicalpaul said:
> I assume your supplier was OK with taking it back?
Yep they took it back, I never took it off the crate. Just opened it.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
> @Phil53 said:
> Wonder how many EG's sold were steam vs water and if this had anything to do with it.
I don’t really see EG boilers being used for hot water anymore, some instances, however Weil-McLain has the CGa water boiler that’s a third of the size and cost a lot less.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Apparently the right side return is no longer tapped either. SmhDL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
@Dave0176. I could be wrong but I don't think the right side return tapping was ever listed in the brochure or installation manual.0
-
My local supplier stocks Peerless boilers so I am okay. Of course my estimates will need to go up and I am a greater risk of being out bid. Maybe someone can convince peerless to get rid of that stupid Cyclegaurd and to use a 24v LWCO instead of 120V. One thing that I like about Peerless is that they do not plug their tappings and they have 1" tappings towards the bottom of the block. I also find their jacket to be easier to get on and off.0
-
The cyclegaurd is the only drawback, however that'll be replaced before the first fireup...........STEAM DOCTOR said:My local supplier stocks Peerless boilers so I am okay. Of course my estimates will need to go up and I am a greater risk of being out bid. Maybe someone can convince peerless to get rid of that stupid Cyclegaurd and to use a 24v LWCO instead of 120V. One thing that I like about Peerless is that they do not plug their tappings and they have 1" tappings towards the bottom of the block. I also find their jacket to be easier to get on and off.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Weil-McLain's Head of Training and Technical Dept called me on this a few weeks ago and asked if I thought WM would have a problem with this change on the smaller boilers. My answer was simply "Only with the people to whom the dual-riser drop header has become a religion. But there are a lot of them out there. Watch HeatingHelp.com for blowback because you're going to get it."
He replied, "I didn't think of that. There's no reason whatsoever to use a second tapping on boilers this size but I guess I'll watch what happens online."
And that was that.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
-
Looks like that few cents that they saved on a second tap is going to cost them much more...…. How much really is a bushing plug, compared to lost sale of an entire boiler.....
I don't know, I'm just a heating guy.0 -
Well now I know I won’t be installing any of there smaller EG boilers.0
-
> @EzzyT said:
> Well now I know I won’t be installing any of there smaller EG boilers.
>
Do you feel a single 3" will impact the performance of an EG-35?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
That small of a boiler not really but that both the supply and return on the same side of the boiler yes0
-
The amount of water coming back even on EG-55 is awfully small. No?EzzyT said:That small of a boiler not really but that both the supply and return on the same side of the boiler yes
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
@ChrisJ. Issue is not the amount of water. Issue is piping convenience. Either header needs to run front to back or you need to make U-turn to get equalizer back to left side of boiler0
-
So I have to adjust my standards of operation of installs because a manufacturer wants to be cheap because some pencil pushing numbers guy figured a way to save the company I’ll pass on that.1
-
You guys and gals already know from my install pictures that I post that I don’t stick with just one manufacturer, I go with the boiler size that is best suitable to the application. So if a manufacturer is gonna pull this kinda crap then I’ll just move on to the next one.0
-
> @STEAM DOCTOR said:
> Not just a matter of using two tappings. There are many times where piping right to left is much more convenient then piping left to right. Also, whenever the header is running side to side(as opposed to front to back) it is always more convenient to have a return tapping on the opposite side.
That’s the thing, even people using one tapping had the option to move to the right should the job require that, and in Weil-McLains older I&O manual they always stated the return must be on the same side as the supply tapping. Now there is no choice other then the left.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
> @JohnNY said:
> Weil-McLain's Head of Training and Technical Dept called me on this a few weeks ago and asked if I thought WM would have a problem with this change on the smaller boilers. My answer was simply "Only with the people to whom the dual-riser drop header has become a religion. But there are a lot of them out there. Watch HeatingHelp.com for blowback because you're going to get it."
>
> He replied, "I didn't think of that. There's no reason whatsoever to use a second tapping on boilers this size but I guess I'll watch what happens online."
>
> And that was that.
I do hope they read this @JohnNY
Tomorrow morning I will call our local WM rep and let him know my displeasure, and that I’ll be moving to another manufacturer. Weather he cares or not is not my problem. I have other options and my supply house carries other boiler brands.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Is Peerless the one that has a heavier block and no pins above the water line?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
-
-
Steam velocity numbers before we form a lynch mob please. Excessive pipe size means extra air to purge on a cycle and more heat loss from surface area even with insulation in place. Bigger is not better, we learned that with boiler sizing. Why are we forgetting that with pipe sizing?Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating1 -
Yes, I'm definitely with Charlie on this one. Running 2- 3inch risers on a tiny boiler doesn't make sense to me. I say, put that money into the system or TRV's. A 3 inch riser will allow water to drop back down up to about 200,000 btu/hr boiler input. With dirty water there may be a little carryover, but a good header will take care of that. We run 3 inch risers up to 350,000 with a good header ( 4 inch if possible) and don't have problems on Peerless 64's. I think you're better off with the Peerless with push nipples and heavier sections anyway. It seems the plastic gasket life is only about 25 years on the LGB's, not sure how well they hold up on EGH's. On the EGH's we tend to see cracks at the top of the legs going into the water jacket and eventully bad gaskets or rot out.To learn more about this professional, click here to visit their ad in Find A Contractor.1
-
It's not only a matter of using the second riser. It's a matter of being limited to supply and return tappings on the left side of the boiler. Makes the piping significantly more difficult. Especially in small boiler rooms. I typically use one riser on smaller boilers but almost always Supply from one side and return on the other side.3
-
25 years is good to me considering the other sludge and scale build up in a steam boilers. As far it limiting piping options this is hardly an issue even in the tightest boiler room. Guys there are bigger problems in the universe of steam heating. Time to fix so heat and I choose wm because it is a good middle ground but also I have successfully installed my long disliked Utica boiler to great success. Quit nitpicking. Steam on.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating3
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements