Is this a normal operating condition

hot_rod
hot_rod Member Posts: 23,398
?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
Solid_Fuel_Man
«1

Comments

  • Canucker
    Canucker Member Posts: 722
    Dry fire? That's scary looking
    You can have it good, fast or cheap. Pick two
    Gordy1Matthias
  • Gordy
    Gordy Member Posts: 9,546
    As with any hydronic heating question depends :D I’ll bet the radiant heat effect is wonderful on a cold winters day B)

    So what gives? Looks like dry fire.
  • JUGHNE
    JUGHNE Member Posts: 11,279
    It is pretty awesome if you are a 1000 miles away. :o
    1Matthias
  • Rich_49
    Rich_49 Member Posts: 2,769
    >:)
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • Gordy
    Gordy Member Posts: 9,546
    The gas line is a scary proximity to the event. I see the paint isn’t brown yet.
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Ah, the large barrel stove with pipes coming out of it! Looks like a nice toasty fire you have sirs! Keep up the good work.
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Grallert
    Grallert Member Posts: 780
    oh jeez that's scary.
    Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker
    ratio
  • Jamie Hall
    Jamie Hall Member Posts: 24,862
    I hope you were using a very long telephoto lens...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Erin Holohan HaskellCanuckerSolid_Fuel_Man1Matthias
  • 1Matthias
    1Matthias Member Posts: 148
    edited November 2018

    I hope you were using a very long telephoto lens...

    You couldn't get me in that building for any sum, much less close enough to take a photo...

    Solid_Fuel_Man
  • Tinman
    Tinman Member Posts: 2,808
    If I saw that I’d do a 180 and run like hell.
    Steve Minnich
    1MatthiasCanuckerSuperTech
  • Tinman
    Tinman Member Posts: 2,808
    Imaging camera with a small target?
    Steve Minnich
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    I agree, in all seriousness that's one of the scariest things i've ever seen. That has the potential to level that place and possibly more.....
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Gordy
    Gordy Member Posts: 9,546
    edited November 2018
    The more I look at the photo, I’m starting to think photoshopped. With the flammable items in the foreground, coupled with the fact there should be heat waves distorting objects in the background above the boiler. Also there should be some smoke from the paint burning off.
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    I thought the same thing, but there seems to be a red reflection off the gas piping. There also looks to be burnt paint, or possibly just the photoshop image overlay too...
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Gordy
    Gordy Member Posts: 9,546
    I think the paint is the overlay of the photoshop attempt. Red hot like that the paint should be scorched on the sides to, and above. Most people would be looking to shut that beast down verses getting a picture :D
  • Gordy
    Gordy Member Posts: 9,546
    edited November 2018
    However there are some real photographers that just make it a priority over 1st steps. Clean your dryer lint.........

    Honey do you have time to call 911? I gotta get a picture of this!
    Canucker
  • HomerJSmith
    HomerJSmith Member Posts: 2,635
    I'll bring the hot dogs if you bring the beer!
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    I've seen a dryer fire happen, and it ain't pretty! Never ever ever, would I ever put any plastic hose on a dryer either. All hard metal pipe for me after seeing that!
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    Gordy
  • ratio
    ratio Member Posts: 3,791
    Unless the camera has good IR filtering, it'll overexpose very hot surfaces. I expect that it wasn't quite so ...visible... to the naked eye.

    That said, with the oxidation that's showing on the very hottest parts, I'd've pulled the fire alarm & called the fire dept as soon as I saw it.

    CLamb
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    Dryback boiler with refractory damage
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,656
    wow thats scary
    Ray Wohlfarth
    Boiler Lessons
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    @EBEBRATT-Ed I wondered that as well. If that were the case, it wouldn't present an explosion hazard.
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Zman
    Zman Member Posts: 7,611
    @hot rod
    You can't just post a pic like that and walk away.
    Did you see this boiler or was it a picture from the internet?
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • hot_rod
    hot_rod Member Posts: 23,398
    I got the pic 3rd hand from a wholesaler that knew the service tech on the call. The building was evacuated, seems the fire marshal and boiler operator had different opinions on how to cool the boiler.

    Another tech that saw the pic recognized the boiler as one his company used to service, years back. He has a high pressure boiler operators license in the State and he indicated there is a protocol for cooling down a boiler that has run away like that.

    Must have been 3 safeties failed for that condition, LWC, operating stat and high limit?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    How to cool the boiler? Just shut it off and leave it connected to the system, the load will cool it down. When it has "cooled" as much as possible isolate it.
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Is an HRT type boiler a dryback like a scotch-marine? At least all that I've seen are.

    How did they cool the boiler? I'd think simply turning off the burner could allow water to return to the boiler which could still be red hot and end up catastrophic. I'd suspect isolating the boiler and turning off burner would be the safest way. I wouldn't want to be the guy turning those valves, let alone the guy taking the picture. Wow....
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    edited November 2018
    EDIT: I was given inaccurate information.

    We had a hotel in Maryland where this happened and it was even worse. The boiler didn't blow but the tubes got so hot they started to melt and were "U" shaped. Boiler was a total loss.
    Never stop learning.
    Solid_Fuel_Man
  • kevinj_4
    kevinj_4 Member Posts: 91

    Yes this one was a dry back. The boiler was a steam boiler and it was empty. They shut it off. The feedwater line broke and no water could enter the boiler. The safeties were probably bypasses or failed long before the feedwater line broke.

    There are dryback and wetback scotch marine boilers.

    I was told it was a maintenance guy who shut the boiler off.

    We had a hotel in Maryland where this happened and it was even worse. The boiler didn't blow but the tubes got so hot they started to melt and were "U" shaped. Boiler was a total loss.

    Mike,

    You do not have your facts straight at all on this job. The feed did not break, the pump coupler stripped.

    The controls are not full of mud. In fact the LWCO tested open.
    The backup warrick relay base is melted in the cabinet so it cannot be tested at this time.

    And last a Michigan state trooper at the site shut it down.
  • kevinj_4
    kevinj_4 Member Posts: 91

    It was an HRT boiler. I talked to the contractor on facebook who is dealing with it. It was a government facility and apparently the insurance and inspectors didn't care about finding out what caused it to happen. I have more pictures of the boiler opened up that I can share later.

    The contractor told me they found nothing jumped out but I'm not sure if I believe that. It had a Warrick probe style low water cut off as well as a McDonnell Miller 150. The only way I see a probe style LWCO not shutting the boiler down is jumping it out. I had a customer that had their LWCO go bad so they had an "electrical engineer" who lived in the building come fix it. He grounded the probe with a jumper. My bet is probe was bypassed and 150 was full of mud.

    hot rod said:

    I got the pic 3rd hand from a wholesaler that knew the service tech on the call. The building was evacuated, seems the fire marshal and boiler operator had different opinions on how to cool the boiler.

    Another tech that saw the pic recognized the boiler as one his company used to service, years back. He has a high pressure boiler operators license in the State and he indicated there is a protocol for cooling down a boiler that has run away like that.

    Must have been 3 safeties failed for that condition, LWC, operating stat and high limit?

    Hotrod, you must have got this from Chris.

    Low pressure steam, 2 LWCO. one manual reset.

    Pressure controls mean nothing when you dry fire.

    A lot of wrong information on here!!!!

    The state boiler inspector spent a half day with me, the insurance inspector is coming in this week for second visit.

    We have meetings coming up with the customer, priority was securing the dead boiler and bringing second boiler and heating plant back on line. Then thoroughly testing all the equipment in the plant.

    The state has their own HVAC people and we only go in when.there are issues,

    There is plenty of time to inspect this thing now.
  • kevinj_4
    kevinj_4 Member Posts: 91

    It was an HRT boiler. I talked to the contractor on facebook who is dealing with it. It was a government facility and apparently the insurance and inspectors didn't care about finding out what caused it to happen. I have more pictures of the boiler opened up that I can share later.

    The contractor told me they found nothing jumped out but I'm not sure if I believe that. It had a Warrick probe style low water cut off as well as a McDonnell Miller 150. The only way I see a probe style LWCO not shutting the boiler down is jumping it out. I had a customer that had their LWCO go bad so they had an "electrical engineer" who lived in the building come fix it. He grounded the probe with a jumper. My bet is probe was bypassed and 150 was full of mud.

    Mike,

    I am the contractor and I do not do facebook so I do not know where you got this info.

    Your bets are all wrong here, CNA done an internal & the boiler was CSD-1 tested by the state HVAC group in August 2018.

    Float is clean & LWCO was open, warrick base is melted.

    Again this equipment is serviced by the state HVAC people, contractors are only brought in when needed.
  • kevinj_4
    kevinj_4 Member Posts: 91
    Gordy said:

    The more I look at the photo, I’m starting to think photoshopped. With the flammable items in the foreground, coupled with the fact there should be heat waves distorting objects in the background above the boiler. Also there should be some smoke from the paint burning off.

    NOT Photoshop, this is real, photo taken by the trooper that shut it down.
  • kevinj_4
    kevinj_4 Member Posts: 91

    How to cool the boiler? Just shut it off and leave it connected to the system, the load will cool it down. When it has "cooled" as much as possible isolate it.

    Yep, dump the e-stops and let it cool.
    RPK
  • hot_rod
    hot_rod Member Posts: 23,398
    kevinj said:

    It was an HRT boiler. I talked to the contractor on facebook who is dealing with it. It was a government facility and apparently the insurance and inspectors didn't care about finding out what caused it to happen. I have more pictures of the boiler opened up that I can share later.

    The contractor told me they found nothing jumped out but I'm not sure if I believe that. It had a Warrick probe style low water cut off as well as a McDonnell Miller 150. The only way I see a probe style LWCO not shutting the boiler down is jumping it out. I had a customer that had their LWCO go bad so they had an "electrical engineer" who lived in the building come fix it. He grounded the probe with a jumper. My bet is probe was bypassed and 150 was full of mud.

    hot rod said:

    I got the pic 3rd hand from a wholesaler that knew the service tech on the call. The building was evacuated, seems the fire marshal and boiler operator had different opinions on how to cool the boiler.

    Another tech that saw the pic recognized the boiler as one his company used to service, years back. He has a high pressure boiler operators license in the State and he indicated there is a protocol for cooling down a boiler that has run away like that.

    Must have been 3 safeties failed for that condition, LWC, operating stat and high limit?

    Hotrod, you must have got this from Chris.

    Low pressure steam, 2 LWCO. one manual reset.

    Pressure controls mean nothing when you dry fire.

    A lot of wrong information on here!!!!

    The state boiler inspector spent a half day with me, the insurance inspector is coming in this week for second visit.

    We have meetings coming up with the customer, priority was securing the dead boiler and bringing second boiler and heating plant back on line. Then thoroughly testing all the equipment in the plant.

    The state has their own HVAC people and we only go in when.there are issues,

    There is plenty of time to inspect this thing now.
    I did get it from Chris, saw him at a training I was doing at Local hall last week.

    I did not get many details, don't want to speculate on the cause, just wanted to share how serious a runaway boiler can be, and look :)

    Hope you get it all worked out, glad it wasn't a more serious event.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • kevinj_4
    kevinj_4 Member Posts: 91
    hot rod said:

    kevinj said:

    It was an HRT boiler. I talked to the contractor on facebook who is dealing with it. It was a government facility and apparently the insurance and inspectors didn't care about finding out what caused it to happen. I have more pictures of the boiler opened up that I can share later.

    The contractor told me they found nothing jumped out but I'm not sure if I believe that. It had a Warrick probe style low water cut off as well as a McDonnell Miller 150. The only way I see a probe style LWCO not shutting the boiler down is jumping it out. I had a customer that had their LWCO go bad so they had an "electrical engineer" who lived in the building come fix it. He grounded the probe with a jumper. My bet is probe was bypassed and 150 was full of mud.

    hot rod said:

    I got the pic 3rd hand from a wholesaler that knew the service tech on the call. The building was evacuated, seems the fire marshal and boiler operator had different opinions on how to cool the boiler.

    Another tech that saw the pic recognized the boiler as one his company used to service, years back. He has a high pressure boiler operators license in the State and he indicated there is a protocol for cooling down a boiler that has run away like that.

    Must have been 3 safeties failed for that condition, LWC, operating stat and high limit?

    Hotrod, you must have got this from Chris.

    Low pressure steam, 2 LWCO. one manual reset.

    Pressure controls mean nothing when you dry fire.

    A lot of wrong information on here!!!!

    The state boiler inspector spent a half day with me, the insurance inspector is coming in this week for second visit.

    We have meetings coming up with the customer, priority was securing the dead boiler and bringing second boiler and heating plant back on line. Then thoroughly testing all the equipment in the plant.

    The state has their own HVAC people and we only go in when.there are issues,

    There is plenty of time to inspect this thing now.
    I did get it from Chris, saw him at a training I was doing at Local hall last week.

    I did not get many details, don't want to speculate on the cause, just wanted to share how serious a runaway boiler can be, and look :)

    Hope you get it all worked out, glad it wasn't a more serious event.

    Well, they were very close to a serious event!!!!!!!!

    Some of that computer stuff is melted and the insulation on the back door is completely melted, another hour it may have been real bad.

    The trooper that was onsite noticed the odd smell and went looking for it.

    The boiler is junk. We hope they let us dig in a bit more.

    We had to wait for the state inspector before it could opened.

    Then disconnect it and work on bringing the plant up, now insurance can come in.

    Since the e-stops killed it the gas valves are working, as I said the 150 LWCO tested open and the bowl is clean.

    There was a valid CSD-1 from august & an internal inspection by the insurance inspector so this thing should have been in good shape.

    Nothing is real obvious and nothing is jumped out.

    Did the flame safegard fail?????? It is one item not yet tested due to the process here.
  • kevinj_4
    kevinj_4 Member Posts: 91
    Gordy said:

    The gas line is a scary proximity to the event. I see the paint isn’t brown yet.

    The gas pipe is brown.

    But they weld on live lines. That is the least on my worries.

    If this boiler would have got a gallon of water it would have been all over.
    Solid_Fuel_Man
  • kevinj_4
    kevinj_4 Member Posts: 91
    Gordy said:

    I think the paint is the overlay of the photoshop attempt. Red hot like that the paint should be scorched on the sides to, and above. Most people would be looking to shut that beast down verses getting a picture :D

    Does this help with your ideas of photoshop???

    Insulation completely melted out.




    Solid_Fuel_ManSuperTech
  • Gordy
    Gordy Member Posts: 9,546
    edited November 2018
    Take it easy. This is the Internet. I don’t believe everything posted until I see proof, especially pictures. Thanks for the proof, and I hope all goes well.
    kcoppDan Foley
  • kevinj_4
    kevinj_4 Member Posts: 91
    Hey Gord,

    This really ain't take it easy territory. A lot of you are out there throwing stones and the boiler ain't even cooled off yet.

    There are procedures here which I have put above.

    This is a real life-safety event we can all learn from but until we are asked to find the cause it is up to others at this time.

    This is my 4th dry fire and I hope to retire in a few months, the other 3 were cast iron without all safety's built into this boiler.

    Fortunately these things do not happen often.

    This should not have happened since it was tested and & inspected recently & it has 2 LWCO on it.

    The other boiler checked out fine and has the same controls.

    Oh & the plant is online & running fine. Just short 1 boiler.


    GordySolid_Fuel_ManCLamb
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    @Kevinj thank you for all the info. I'm very interested in the results of the/your investigation.

    I have wired hundreds of burner and boiler controls, would like to learn how this can happen. Welded contacts is the first thing that comes to mind.

    Very scary!
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • kevinj_4
    kevinj_4 Member Posts: 91

    @Kevinj thank you for all the info. I'm very interested in the results of the/your investigation.



    Welded contacts is the first thing that comes to mind.



    Very scary!

    No welded contacts found at this point, the 150 ohms open (will not close tho it makes all 3 clicks up & down)

    No shorted wires found so far either.

    You can see in the Warrick (clear case)

    So about the only other thing in the circuit is the flame safegard control. Maybe burner contactor???? But gas should be stopped from safety circuit, e-stop killed it so gas valves were working.

    Lwco should stop power from all of the controls in theory.

    We have to remember this thing was around 2000° so by the time any investigation was started a lot of metal was moving around. We may never see the condition that caused it.

    Just the expansion & contraction may have broke a welded contact.
    Solid_Fuel_Man