Is this a normal operating condition
trainer for Caleffi NA
Living the hydronic dream
Comments
-
-
As with any hydronic heating question depends I’ll bet the radiant heat effect is wonderful on a cold winters day
So what gives? Looks like dry fire.0 -
-
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
The gas line is a scary proximity to the event. I see the paint isn’t brown yet.0
-
Ah, the large barrel stove with pipes coming out of it! Looks like a nice toasty fire you have sirs! Keep up the good work.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
-
-
You couldn't get me in that building for any sum, much less close enough to take a photo...Jamie Hall said:I hope you were using a very long telephoto lens...
1 -
-
Imaging camera with a small target?Steve Minnich0
-
I agree, in all seriousness that's one of the scariest things i've ever seen. That has the potential to level that place and possibly more.....Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
The more I look at the photo, I’m starting to think photoshopped. With the flammable items in the foreground, coupled with the fact there should be heat waves distorting objects in the background above the boiler. Also there should be some smoke from the paint burning off.0
-
I thought the same thing, but there seems to be a red reflection off the gas piping. There also looks to be burnt paint, or possibly just the photoshop image overlay too...Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
I think the paint is the overlay of the photoshop attempt. Red hot like that the paint should be scorched on the sides to, and above. Most people would be looking to shut that beast down verses getting a picture0
-
-
I'll bring the hot dogs if you bring the beer!0
-
-
-
Dryback boiler with refractory damage0
-
-
@EBEBRATT-Ed I wondered that as well. If that were the case, it wouldn't present an explosion hazard.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
I got the pic 3rd hand from a wholesaler that knew the service tech on the call. The building was evacuated, seems the fire marshal and boiler operator had different opinions on how to cool the boiler.
Another tech that saw the pic recognized the boiler as one his company used to service, years back. He has a high pressure boiler operators license in the State and he indicated there is a protocol for cooling down a boiler that has run away like that.
Must have been 3 safeties failed for that condition, LWC, operating stat and high limit?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
How to cool the boiler? Just shut it off and leave it connected to the system, the load will cool it down. When it has "cooled" as much as possible isolate it.0
-
Is an HRT type boiler a dryback like a scotch-marine? At least all that I've seen are.
How did they cool the boiler? I'd think simply turning off the burner could allow water to return to the boiler which could still be red hot and end up catastrophic. I'd suspect isolating the boiler and turning off burner would be the safest way. I wouldn't want to be the guy turning those valves, let alone the guy taking the picture. Wow....Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
-
Mike,Mike_Sheppard said:Yes this one was a dry back. The boiler was a steam boiler and it was empty. They shut it off. The feedwater line broke and no water could enter the boiler. The safeties were probably bypasses or failed long before the feedwater line broke.
There are dryback and wetback scotch marine boilers.
I was told it was a maintenance guy who shut the boiler off.
We had a hotel in Maryland where this happened and it was even worse. The boiler didn't blow but the tubes got so hot they started to melt and were "U" shaped. Boiler was a total loss.
You do not have your facts straight at all on this job. The feed did not break, the pump coupler stripped.
The controls are not full of mud. In fact the LWCO tested open.
The backup warrick relay base is melted in the cabinet so it cannot be tested at this time.
And last a Michigan state trooper at the site shut it down.0 -
Mike_Sheppard said:
It was an HRT boiler. I talked to the contractor on facebook who is dealing with it. It was a government facility and apparently the insurance and inspectors didn't care about finding out what caused it to happen. I have more pictures of the boiler opened up that I can share later.
The contractor told me they found nothing jumped out but I'm not sure if I believe that. It had a Warrick probe style low water cut off as well as a McDonnell Miller 150. The only way I see a probe style LWCO not shutting the boiler down is jumping it out. I had a customer that had their LWCO go bad so they had an "electrical engineer" who lived in the building come fix it. He grounded the probe with a jumper. My bet is probe was bypassed and 150 was full of mud.
Hotrod, you must have got this from Chris.hot rod said:I got the pic 3rd hand from a wholesaler that knew the service tech on the call. The building was evacuated, seems the fire marshal and boiler operator had different opinions on how to cool the boiler.
Another tech that saw the pic recognized the boiler as one his company used to service, years back. He has a high pressure boiler operators license in the State and he indicated there is a protocol for cooling down a boiler that has run away like that.
Must have been 3 safeties failed for that condition, LWC, operating stat and high limit?
Low pressure steam, 2 LWCO. one manual reset.
Pressure controls mean nothing when you dry fire.
A lot of wrong information on here!!!!
The state boiler inspector spent a half day with me, the insurance inspector is coming in this week for second visit.
We have meetings coming up with the customer, priority was securing the dead boiler and bringing second boiler and heating plant back on line. Then thoroughly testing all the equipment in the plant.
The state has their own HVAC people and we only go in when.there are issues,
There is plenty of time to inspect this thing now.0 -
Mike,Mike_Sheppard said:It was an HRT boiler. I talked to the contractor on facebook who is dealing with it. It was a government facility and apparently the insurance and inspectors didn't care about finding out what caused it to happen. I have more pictures of the boiler opened up that I can share later.
The contractor told me they found nothing jumped out but I'm not sure if I believe that. It had a Warrick probe style low water cut off as well as a McDonnell Miller 150. The only way I see a probe style LWCO not shutting the boiler down is jumping it out. I had a customer that had their LWCO go bad so they had an "electrical engineer" who lived in the building come fix it. He grounded the probe with a jumper. My bet is probe was bypassed and 150 was full of mud.
I am the contractor and I do not do facebook so I do not know where you got this info.
Your bets are all wrong here, CNA done an internal & the boiler was CSD-1 tested by the state HVAC group in August 2018.
Float is clean & LWCO was open, warrick base is melted.
Again this equipment is serviced by the state HVAC people, contractors are only brought in when needed.
0 -
NOT Photoshop, this is real, photo taken by the trooper that shut it down.Gordy said:The more I look at the photo, I’m starting to think photoshopped. With the flammable items in the foreground, coupled with the fact there should be heat waves distorting objects in the background above the boiler. Also there should be some smoke from the paint burning off.
0 -
Yep, dump the e-stops and let it cool.EBEBRATT-Ed said:How to cool the boiler? Just shut it off and leave it connected to the system, the load will cool it down. When it has "cooled" as much as possible isolate it.
0 -
I did get it from Chris, saw him at a training I was doing at Local hall last week.kevinj said:Mike_Sheppard said:It was an HRT boiler. I talked to the contractor on facebook who is dealing with it. It was a government facility and apparently the insurance and inspectors didn't care about finding out what caused it to happen. I have more pictures of the boiler opened up that I can share later.
The contractor told me they found nothing jumped out but I'm not sure if I believe that. It had a Warrick probe style low water cut off as well as a McDonnell Miller 150. The only way I see a probe style LWCO not shutting the boiler down is jumping it out. I had a customer that had their LWCO go bad so they had an "electrical engineer" who lived in the building come fix it. He grounded the probe with a jumper. My bet is probe was bypassed and 150 was full of mud.
Hotrod, you must have got this from Chris.hot rod said:I got the pic 3rd hand from a wholesaler that knew the service tech on the call. The building was evacuated, seems the fire marshal and boiler operator had different opinions on how to cool the boiler.
Another tech that saw the pic recognized the boiler as one his company used to service, years back. He has a high pressure boiler operators license in the State and he indicated there is a protocol for cooling down a boiler that has run away like that.
Must have been 3 safeties failed for that condition, LWC, operating stat and high limit?
Low pressure steam, 2 LWCO. one manual reset.
Pressure controls mean nothing when you dry fire.
A lot of wrong information on here!!!!
The state boiler inspector spent a half day with me, the insurance inspector is coming in this week for second visit.
We have meetings coming up with the customer, priority was securing the dead boiler and bringing second boiler and heating plant back on line. Then thoroughly testing all the equipment in the plant.
The state has their own HVAC people and we only go in when.there are issues,
There is plenty of time to inspect this thing now.
I did not get many details, don't want to speculate on the cause, just wanted to share how serious a runaway boiler can be, and look
Hope you get it all worked out, glad it wasn't a more serious event.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Well, they were very close to a serious event!!!!!!!!hot rod said:
I did get it from Chris, saw him at a training I was doing at Local hall last week.kevinj said:Mike_Sheppard said:It was an HRT boiler. I talked to the contractor on facebook who is dealing with it. It was a government facility and apparently the insurance and inspectors didn't care about finding out what caused it to happen. I have more pictures of the boiler opened up that I can share later.
The contractor told me they found nothing jumped out but I'm not sure if I believe that. It had a Warrick probe style low water cut off as well as a McDonnell Miller 150. The only way I see a probe style LWCO not shutting the boiler down is jumping it out. I had a customer that had their LWCO go bad so they had an "electrical engineer" who lived in the building come fix it. He grounded the probe with a jumper. My bet is probe was bypassed and 150 was full of mud.
Hotrod, you must have got this from Chris.hot rod said:I got the pic 3rd hand from a wholesaler that knew the service tech on the call. The building was evacuated, seems the fire marshal and boiler operator had different opinions on how to cool the boiler.
Another tech that saw the pic recognized the boiler as one his company used to service, years back. He has a high pressure boiler operators license in the State and he indicated there is a protocol for cooling down a boiler that has run away like that.
Must have been 3 safeties failed for that condition, LWC, operating stat and high limit?
Low pressure steam, 2 LWCO. one manual reset.
Pressure controls mean nothing when you dry fire.
A lot of wrong information on here!!!!
The state boiler inspector spent a half day with me, the insurance inspector is coming in this week for second visit.
We have meetings coming up with the customer, priority was securing the dead boiler and bringing second boiler and heating plant back on line. Then thoroughly testing all the equipment in the plant.
The state has their own HVAC people and we only go in when.there are issues,
There is plenty of time to inspect this thing now.
I did not get many details, don't want to speculate on the cause, just wanted to share how serious a runaway boiler can be, and look
Hope you get it all worked out, glad it wasn't a more serious event.
Some of that computer stuff is melted and the insulation on the back door is completely melted, another hour it may have been real bad.
The trooper that was onsite noticed the odd smell and went looking for it.
The boiler is junk. We hope they let us dig in a bit more.
We had to wait for the state inspector before it could opened.
Then disconnect it and work on bringing the plant up, now insurance can come in.
Since the e-stops killed it the gas valves are working, as I said the 150 LWCO tested open and the bowl is clean.
There was a valid CSD-1 from august & an internal inspection by the insurance inspector so this thing should have been in good shape.
Nothing is real obvious and nothing is jumped out.
Did the flame safegard fail?????? It is one item not yet tested due to the process here.0 -
Does this help with your ideas of photoshop???Gordy said:I think the paint is the overlay of the photoshop attempt. Red hot like that the paint should be scorched on the sides to, and above. Most people would be looking to shut that beast down verses getting a picture
Insulation completely melted out.
2 -
-
Hey Gord,
This really ain't take it easy territory. A lot of you are out there throwing stones and the boiler ain't even cooled off yet.
There are procedures here which I have put above.
This is a real life-safety event we can all learn from but until we are asked to find the cause it is up to others at this time.
This is my 4th dry fire and I hope to retire in a few months, the other 3 were cast iron without all safety's built into this boiler.
Fortunately these things do not happen often.
This should not have happened since it was tested and & inspected recently & it has 2 LWCO on it.
The other boiler checked out fine and has the same controls.
Oh & the plant is online & running fine. Just short 1 boiler.
3 -
@Kevinj thank you for all the info. I'm very interested in the results of the/your investigation.
I have wired hundreds of burner and boiler controls, would like to learn how this can happen. Welded contacts is the first thing that comes to mind.
Very scary!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
No welded contacts found at this point, the 150 ohms open (will not close tho it makes all 3 clicks up & down)Solid_Fuel_Man said:@Kevinj thank you for all the info. I'm very interested in the results of the/your investigation.
Welded contacts is the first thing that comes to mind.
Very scary!
No shorted wires found so far either.
You can see in the Warrick (clear case)
So about the only other thing in the circuit is the flame safegard control. Maybe burner contactor???? But gas should be stopped from safety circuit, e-stop killed it so gas valves were working.
Lwco should stop power from all of the controls in theory.
We have to remember this thing was around 2000° so by the time any investigation was started a lot of metal was moving around. We may never see the condition that caused it.
Just the expansion & contraction may have broke a welded contact.
-1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements