Injection pumping?
mattyc
Member Posts: 45
I have a customer with an oil fired cast iron boiler with a two zone fin tube baseboard hydronic system running a tankless coil for HW...for a basic system it works fine except the cx is not used to the expansion/contraction noise of the baseboard when the cold pipe heats up and rubs against every joist in the house.(for me it's a normal sound but in this house it is a bit more extreme then usual) opening up walls to relocate pipe and insulate and clamp properly is not an option. I was thinking about maybe using injection pumping with outdoor reset to hopefully keep the pipe running lower temps for most the year and not have extremes temp changes..thinking maybe keep the zone pump to run constant during design temps and the injection and boiler pump to run on call for heat. Curious if this would solve the noise complaint or if anyone had any other suggestions not including opening sheetrock
0
Comments
-
This almost certainly can be repiped as a primary/secondary system. The secondary would run all the time, with the temperature controlled with a mixing valve or other control, controlled by outdoor reset, and the boiler supplying heat when needed. Lots of ways to do it -- and there is at least one good book on the subject, available from the store on this site.
A very common and normal arrangement...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
Depending on your setup, a mixing valve may be a better option than injection mixing. Injection mixing tends to be a bit of a challenge to get dialed in. If you do injection mixing, tekmar has a good white paper on proper piping. be sure to put a balancing valve on the mixing loop.
The taco I series valve is a good option for a mixing valve."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
it may require some boiler re piping to add an injection mixing system, either primary secondary or a hydraulic separator. It will also require an additional circ pump
Injection mixing is not as popular as other methods, anymore Various mixing valve options are the more common methodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements