What does this vent damper do and should I use it. I have it on hold open
acl10
Member Posts: 349
0
Comments
-
-
What on earth is that thing attached to? What it is is a powered damper, which is supposed to close when the appliance to which it is attached isn't operating. The idea is that there will be a call for the appliance to operate, and it is supposed to open and then -- and only then -- is the appliance allowed to fire up.
The idea is to reduce or eliminate heat loss up the stack when the appliance isn't operating. If it is operating properly, it will do just that. If it isn't, the appliance won't operate -- and they have proven to be somewhat problematic contraptions.
It should do no harm if it is locked open so the appliance can operate -- except for the loss of some warmer air up the stack.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Common for them to fail. No harm in manually wedging it open.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Thats the chimney pipe going to the brick chimney0
-
They've gotten better over the years. We stock replacement motors for them.
On older chimneys, say pre- World War 2, they can make a significant difference. These older chimneys were built to pull air through coal beds in the original boilers, so they can almost pull pets and small children up to the roof. Such a draft can cool a boiler down quickly, but with the damper closed that can't happen.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting3 -
-
Can they be used on an oil fired steam system?
Also I have an electronic LWC that shuts the boiler down for 1 min every 20 min during operation to check the level. Could the motorized damper be put on a 2 min delay so it does not get unnecessarily abused?0 -
That model is designed for gas. But Field does make one for oil-fired units- the OVD series. Go here:
http://www.fieldcontrols.com/oil-vent-damper?page_id=409
Not sure what boiler you have, but if the stack damper is wired after the low-water cutoff it'll do that as a matter of course.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Your not kidding. I’ve been measuring the draft and I’ve added a manual damper and have it more than 1/2 closed. Still have 0.03”. Before I added the draft damper even with the boiler off if the sun was heating the exposed section of chimney in summe it had a hell of a draft. Traps in the basement were almost sucking dry.Steamhead said:They've gotten better over the years. We stock replacement motors for them.
On older chimneys, say pre- World War 2, they can make a significant difference. These older chimneys were built to pull air through coal beds in the original boilers, so they can almost pull pets and small children up to the roof. Such a draft can cool a boiler down quickly, but with the damper closed that can't happen.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements