HELP please on my Lochinvar WHN085
Comments
-
You were pumping through a conventional boiler that had almost no pressure drop. Now your boiler and near boiler piping has considerably more pressure drop.
That, of course is with an assumption of normalcy. I didn't see any pictures of the previous install.0 -
Harvey
things you said is true
I have pictures of the old boiler piping, but i don't know if it's something that needs to be seen, unless you want me too.
somewhat similar to mine, but 1 1/4" and all iron pipe, you see mine is all copper, and 1"0 -
Harvey, it would be great, if that's all it is in changing a pump0
-
Well, from over here it looks like you will be doing extensive manual rad balancing or you'll put in the bigger pump.0
-
Most of us have pumps on hand that we would try in a situation like this.
I seem to have different curves than you do. Here's what I get:Hatterasguy said:15-58: 16 GPM at 2
007: 14.5 GPM at 2
15-58 007 Series 100
2' 15.3 20.4 29
4' 13.7 17 25
6' 12.2 13 18
The unknown here is the new system curve.1 -
I was going to say those curves are the ones I'm familiar with.0
-
Good theatre if nothing else. Good thing it's not cold out.Steve Minnich0
-
just got off the phone with Fred, i asked him if he has a pump laying around, the answer was no0
-
-
Gordy
Help me out to understand what your asking me.
Also, why is the upstairs got good heat, and just the back of the house is colder, and the radiator in the entryway is just warm, and that radiator is close to the living room radiator that is very hot0 -
the living room radiator is closest to the boiler, next i0
-
deleted0
-
Yeah I agree I edited my post in that Marks head will be more.. I think its the perfect selection0
-
is the direction of my pum proper, I'm not talking about flow, this is correct. I mean how I installed it
0 -
if you don't mind me asking, what is bull headed tees mean?0
-
what I don't understand, the 2nd floor is good heat, even the back of the 2nd floor which is above where i am having some of my problems0
-
Technically, a bullhead tee is a fitting where the branch is a larger diameter than the run.
In this case, it means the flow of water is into the branch of the tee.0 -
what i did, to bring the 2 sides together?
is this a no no? I repeated what the other pluber did 35 years ago, on the return, the supply, he did not use a tee0 -
When your flow enters the side port of a tee and exits both end ports or vice versa, you are bull heading it and you get a large pressure drop as the result.0
-
the pressure on my tee is coming from both sides, then going to the near boiler pipping0
-
should I change this0
-
I put the heat on maybe 2 hours ago, to 75
again the living room is hot, so is the dining room, my bedroom is close, my bathroom is less, and my kitchen back radiator is cold, no heat at all, and the front entryway is a little warm0 -
It wouldn't hurt.0
-
I have a fairly large kitchen/ office in the rear of the house I have 3 radiators in there, 1 is warm, the other 2 are cold, so is the small bathroom, cold0
-
both return and supply, should i change
and how would i do it, bring all 4 pipes to the wall of my boiler?0 -
That drawing I posted earlier shows you how. It's a PDF0
-
why are the rooms on the 2nd floor not having any problems?
I just went upstairs, 3 radiators are hot, 2 are very warm0 -
Harvey, i ended up being able to open it, thanks0
-
help me understand how the 2nd floor, which is farthest from the boiler is hot, but directly below it in my kitchen is cold
a bigger pump will fix that?0 -
-
a thought came to my mind, mayb e i am way off, but, i want to put it out there
20 years ago, I remodeled my kitchen/office, fred put in 4 radiators 3 in the kitchen, and one in the small bath, he used 3/4" copper for the piping to the radiators, could this cause a problem?0 -
It will certainly contribute to the imbalance unless you have manually balanced them over the years.
If the house was heating satisfactorily before you changed the boiler, you can make it heat satisfactorily again.0 -
actually, the kitchen was too warm, I had to throdel down the radiators in the back0
-
but why the 2nd floor no problem now, and underneath, big problem, and entry way, big problem?0
-
should i redesign the piping that my old supply and return do not go into a tee, before it gets to the near by radiator piping
and get rid of the bull head tees0 -
I meant to say, the bull head tee going to the near by boiler pipping0
-
Hat
I'm sorry, but I don't understand the numbers you put on the post, can someone help me with that?0 -
I'm going to guess that the question above may have been directed at me? The forum SW nicely shortens any repeated spaces into one space, thus mis-aligning the table I made.
First row lists three pumps.
Next three rows start with feet of head and then show GPM for each of the three pumps.0 -
ok
is hat saying anything about what he might think would solve my
issue?0 -
Harvey did.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements