installing new cast iron forced hot water boiler set for 200 degree temps all the time
I have a customer that all radiators in the house are undersized. I discovered this doing heat loss calculation for his new boiler. He isnt looking to install new radiators so to give him some more BTUs (he has complained his rooms are a little cold, Id like his new boiler to be running always at 200 instead of 180. has anyone done this . are there any problems with doing this?
Thx
Joe
HHI Services
First of all, what type of radiators are we talking about?
EDIT:
When does the customer complain about not having enough heat? This should normally happen only during very cold outdoor weather.
For example, suppose the outdoor design temperature is 10°F and the desired indoor temperature is 70°F. The heating system must be able to maintain a 60°F temperature difference (ΔT) between indoors and outdoors.
If there is only enough radiator capacity to maintain a 55°F ΔT, the house should still heat properly during most of the winter. The problem would begin only when the outdoor temperature drops below about 15°F.
In other words, if the radiators can maintain 70°F indoors when it is 15°F outside, they are adequate until the outdoor temperature falls below 15°F. That said, if the customer is having a problem when it is only 30° or 40° outside then there is a different problem.
2 -
If in fact you need that high, use an ODR control. Most areas are at design temperature lerss than 10% of the heating season. That high operating temperature drives down efficiency.
Years ago the HI Hydronics Institute suggested a high 200°+ operating temperature to use less fin tube and come in with a lower bid than competitors.
You can pick up a small output increase with any heat emitters by increasing flow rate
Notice how fin tube shows output at 1 and 4 gpm flows. Same applies to fan coiuls, CI radiators, etc.
The higher flow increases the AWT average water temperature across the heat emitter, increasing output. 3/4 copper can run4 gpm without wear or noise issues.
Living the hydronic dream1 -
When below design temperature here that's 5°F outside my boiler runs all night long. The supply water runs around 175 - 180°F. The other 99% of the time its fine.
If he wants to pay for 200°F supply water all the time, fine it's his money.
They are all Sunrads..I appreciate the input.. i will ask him specifically how often he feels the cold
thanks
Joe