Design Review - heat pump water heater with boiler coil redux
Hello All and thanks in advance for any thoughts you might have on the following approach to installing a hybrid heat pump water heater (HPWH/HP) that will hopefully become the main source of domestic hot water for a system that currently relies on an oil-fired boiler coil. I've followed many of the discussions on this general topic here on Heating Help and have hopefully used what I have learned to design a "mongrel" install that addresses the concerns raised when bypassing (but not removing) the coil. First some context: I live in southern Maine, so generally considered a cold climate though things are changing, summer is longer and hotter, winters shorter and cold but less predictably so. Current heating system is a 90's vintage Utica boiler with a Beckett burner and forced hot water baseboard distribution system. It's had fairly light use, runs reliably and still holds consistent temp and pressure, but obviously it doesn't owe me anything and I'm gradually preparing to replace it with an air to water heat pump system when she finally gives up the ghost. I run it at ~180 F on the high end, which still gives the two of us plenty of heat and hot water. We are conservative with resource use and have a wood stove to take the edge off in winter.
Here's the issue: I purchased a 50 gal. State HPWH, with a generous point of purchase rebate from Efficiency Maine and intended to use that exclusively for DHW. Low and behold, when reviewing the install instructions I discovered that the heat pump mode will not operate if water temperature in the tank is below 59 F. I knew about the HP cut out if the ambient air temperature is below 45 F (not a problem, it's in the basement next to the boiler) but I was unaware of the 59 F cut out for the tank water! In either case, if the temp is lower than the low default, the unit switches to the electric heating mode, which is not a step up in efficiency. We have a drilled well and the water temperature fluctuates from a high of ~52 in summer to a low around 45 F in winter, 7 - 14 degrees below the cut out year round. This is a problem since I purchase the HP to reduce our oil consumption (particular in the summer) and as part of an effort to improve energy efficiency. Though I am uncertain of how long the unit will have to operate only using the electric elements to raise the temp enough for the HP to kick in, time and experience will tell, I've decided to attempt an install that will allow use of either the boiler coil or the HP. The design I am proposing will allow me to isolate, drain and vent the boiler coil when using the HP and vise versa, if it turns out to be necessary to continue using the coil during the coldest months. I would appreciate any comments you might have on the functionality and safety of the proposed design and I will do my best to answer any questions.
I have attached three photos that hopefully describe the design in sufficient enough detail for reviewers to understand how the installation will work. I'll let them do the rest of the talking.
Thanks for any help,
Rusty
Comments
-
My user name is Rugged, not Rusty. That one was taken. Sorry folks!
0 -
Generally you do not pull the entire tank down to 55°. It shows average tank temperature, probably reading at mid point in the tank. Why would you be running hot water taps if water is below 55°?
So on first fill, if water is below 55 it will run electric only until it heats above 55° as I understand it. Then it goes to heat pump mode. This may be only on 120V models?
If you did pull the entire tank to 45, electric element warms to 55 then HP takes over.
It takes about 3400 btu to raise the tank from 45- 55°, so about 1.2 Kw. What are you paying for KWh?
Maybe plug it into one of those Kil O Watt meters to track for a month and see what you actually use for electric
You could plumb up either a manual or automatic bypass valve that reverts to tankless until the HP warms on its own. Maybe try it as is before you go to that trouble.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Depending on the temps of your basement, a holding tank to "prewarm" the well water before it enters hpwh, uninsulated tank, could be an option. Alternatively a basic electric water heater, set to 59F as a preheat tank.
More complex would be Drain water heat recovery system, your house may not be a set up for it.
0 -
seeing how most basements are 55* anyways that is lityle help.
Small solar collector(s) will help under the right condations.0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 132 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements