Upgrade to 007ECM?
Greetings,
I need to replace an IFC in one of my 15 year old 007s and was wondering if it’s worth replacing the whole circulator with the ECM version. The pump circulates water through the whole first floor and is probably the most used of any of my 007s.
Any thoughts are appreciated.
Brent
Comments
-
It would pay for itself in energy savings.
0 -
-
really? Show us the numbers.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
is it a single zone? Or are there zone valves involved?
Where are you located, many utilities have rebates still
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
if you save even 25 bucks a year o electricity
And you get the 75- 100 bucks rebate
Numbers look good to me
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
But the question is… how much less electricity does it use? I hate to be fussy, and I recognise that there are applications where it is essential to save every tenth of a watt (space flight, for instance), but… even if the existing pump isn't working, you have to do the number.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
EEV's Electronic Expansion Valves in refrigeration also save Electricity dollars. In a supermarket there worth it. In a mom-and-pop shop, maybe one or 2 are not worth the extra expense and reliability issues.
0 -
a few things to consider, the motor itself, the ECM will be more efficient
But also most single speed circs are over-pumping with a wire to water efficiency below 20%
being able to adjust the speed to the load is also an improvementPump people tell you 50-80%
An 80 W circ moving only a few gallons through a single loop may be 10%!
All these questions can be answered with some number crunching
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
My heating system is zoned with circulators so this one serves just the first floor. I’m sure it’s over pumped as the loop is all 3/4” copper and fintube baseboard on the first floor.
Doubtful any rebates are available as we have municipal electric so rates are reasonable but not much for rebates.
0 -
So a 007, number 5 on the graph, at 3-4 gpm is running way to the left of curve, maybe 10- 12% efficiency
Mid curve is where pumps like to run, 8-12 gpm is a comfort range for an 007.
I’d guess an ECM may run 17- 20 watts to move 4-5 gpm
Here is where you find rebate $$
Unless 100 bucks is peanut s to you😏
www.dsireausa.org
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Well the price difference on SupplyHouse.com is between the007 and 007E is $71. I think you will recover that quickly, even without rebates.
i thought EnergyStar was a Fed program?
https://www.energystar.gov/rebate-finder
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
same thing with the ECM blower motors on a furnace. it all looks good on paper until you have to pay for a new motor and the labor to replace them. they even sell kits to convert a furnace to a PsC motor.
0 -
I have cheap electricity and even here the ROI on an ECM pump is about 2 years. If you have the typical wall of pumps, upgrading the often used zones is well worth it.
The one problem with PSC pumps is even when you turn them down, the use almost the same power. This adds up when you have 4-6 pumps running. An ECM on the other hand, on low speed might only use 10W.
I replaced my original PSC pump with an ECM because of noise. I could hear the motor through the piping in the rads at night when the house was quiet. The ECM pump is silent.
Lot of the house heat has changed in more than a decade since but that original Alpha is still chugging along. That was even without a mag filter on a gravity conversion with cast rads.
0 -
The reasons for changing iclude the efficienct bump and also I suspect the current cirs is way over-pumping if this is just a single loop 0f 3/4 fin tube. Generally a loop is 70' or so. 3/4 fin tube designs around 1 gpm.Or up to 4 if you need extra out put.
So call it 2 gpm and see where if falls on the 007 curve
I think the 007E is still way to much pump for a single loop fin tube.
I'm not up to speed on all the Taco, but a 0015 on speed 1 may be a better fit for a low flow circuit?
I like the B&G Vario where you can lock it at 9 different speeds. Speed 1 or two may do it 10- 15W perhaps.
I've been using ECM of all different brands since Wilo first introduced ECM circs. I have yet to have one fail.
Other that one I dropped🤨
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 123 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements