I am looking to potentially replace my boiler which was grossly oversized by the heating contractor who installed it in 2022. I engaged with a 3rd party to perform a manual J calculation for my house. I know, I know, this should have been done back in 2022 before they installed my current boiler. I have properly educated myself now and installer needs some refresher courses too!
3rd party determined that the heat load is 49,476, btu/hr. They also did a manual S calc to determine the proper size boiler for my house. I have a Burnham AL50SL indirect hot water heater. In performing the manual S calc, they multiplied the heat load by 1.4 to come up with a requirement of 70,000 btu/hr. Hmmm. When I asked why they did that, this was the reply:
"When you get into manual s you have overages to account for cold days and other variables in the design. So typically heat load you can add 140% to the load. So, if you multiply the total load 50,000 x 1.4 = 70,000. Based on this you will never find a boiler that is exact to your load so you pick the closest one. However, when you have an indirect water heater you need to size the boiler to that spec. this is why I gave you all the information. The boiler they are looking to install does meet the needs of the indirect and they should have it set to priority."
They also went on to say:
"You should use the home's manual J space heating load to size the boiler, provided the indirect water heater's required input does not exceed that heating load. If the indirect tank's minimum required BTU recovery rate is larger than the house heating load, you size the boiler to the larger of the two loads" Again, hmmm.
Per the Burnham spec sheet for the AL50SL, it states the minimum heat source should be 117,000 btu/hr. If I had a boiler installed to meet this I would be oversized by over 2X for what my heating load needs.
So, here are my questions:
  1. Is what I am being told accurate with the manual S calc or should I just go with a boiler that is closest to the 49,476 btu/hr load my house needs for heat? I also keep telling everyone that I consider my hot water demand low. Just me and my wife 90% of the time which means 2 showers in the morning. This is a 2nd home, so not here all the time. Run the dishwasher every 2 days or so when here. Laundry once in a while to do sheets and towels. Could we move here sometime in the future full-time, possibly but not likely. Wife wants to be near the future grandchildren.
  2. Should I consider replacing the indirect instead of the boiler with a reverse indirect like the TurboMax to eliminate the current short cycling. My understanding is that the reverse indirect would provide more thermal mass and thus increase cycle times. I do notice that when we do take showers that the boiler cycles are much increased unlike when the boiler is just supplying heat. I also have a couple of what you guys would consider "micro zones" for a few of the heating zones. Also, forgot to mention that my baseboard is fin-tube.
Appreciate any feedback and guidance.
    EdTheHeaterMan Member Posts: 12,657
    edited 2:35PM
    There is validity to the “size to the DHW demand” idea in some cases. Your home only needs 50,000 BTU NET. That is not the boiler size.
    The boiler size is usually stated by the input rating, which is the amount of fuel the boiler uses every hour of operation. On a 140,000 BTU oil boiler, that might be about 1.00 gallon per hour. On a gas boiler, that would be approximately 136 to 141 cubic feet per hour, depending on the chemical makeup and heating value of the natural gas.
    After you burn that gas or oil, most of the heat goes into the water in the boiler, and the rest is lost through the vent pipe. That determines the output of the boiler.
    Then there will be some additional heat loss through the piping between the boiler and the radiators. That is called the piping and pickup loss. On steam systems, the standard allowance is 30%. On hot-water radiator systems, the standard allowance is 15%.
    After those allowances are deducted, you arrive at the AHRI NET rating. On older equipment, this was called the I=B=R NET rating.
    Now, those fixed percentages are not necessarily the actual piping and pickup losses in every house. They are more of a standardized, somewhat worst-case allowance. Many homes will have actual piping and pickup losses below those percentages, but these are the standardized numbers used when sizing a boiler from a heat-loss calculation.
    Here is an example showing the AHRI NET rating and the older I=B=R NET rating.
    NEW Equipment
    Older Equipment:
    Now, here is where the difference with an indirect water heater comes in. If you use a smaller boiler with only 49,000 to 50,000 BTU of NET output, the indirect water heater will not operate at its full rated capacity.
    If you select a larger boiler with a higher NET output, the indirect can receive more heat from the boiler. That allows it to recover faster and produce more hot water in a given amount of time.
    That difference is shown on this chart:
    See how the same water heater provides less hot water when connected to the smaller boiler? With the larger boiler, the water heater can produce up to a 170-gallon First Hour Rating. But the tank itself also has a limit. Once you reach that limit, installing an even larger boiler will not increase the rating beyond 170 gallons.
    But do you really need that extra capacity? Maybe not.
    I grew up in a house with a 30-gallon gas water heater and a 30,000 BTU burner. There were six of us—Mom, Dad, and four kids—and I rarely remember running out of hot water. With a 50,000 BTU NET boiler and a 40-gallon indirect tank, you would already have more hot-water capacity than we had.
    If you want to use the 40-gallon indirect to its full rated capacity, then you may need a boiler larger than your home actually requires for heating. Personally, I don't think that is necessary. A reasonable compromise may be to choose the boiler size in between.
    Just remember: once you select the boiler size, you cannot easily increase its output later. If you eventually discover that you truly need more hot-water capacity, increasing the boiler size would usually mean replacing the boiler.
    I hope this makes sense after you read it 7 times.
  • Ironman
    Ironman Member Posts: 7,942
    edited 2:13PM
    Well, you never mentioned what boiler you presently have.
    However, unless you have an unusually high domestic load, the boiler should be sized to the space heating load.
    Let me explain: modern boilers are setup to give priority to domestic heating. In other words, the total output capacity of the boiler is directed entirely to the indirect during a domestic call. If the boiler has an output capacity of 50k btus, then that’s what going to the indirect. If you have a 50 gallon indirect with 50k btus going to it, that’s about the same as a 50 gallon gas water heater with a 48k btu burner. And that is more than sufficient for the average household.
    The minimum btu rating on an indirect is simply the minimum btus needed to get the minimum rated output from it. It doesn’t mean that it won’t function with a lesser input. It’s just a tank of water and it’s doesn’t know whether the btus are coming from an internal hot water coil fed from a boiler or from a gas burner directly.
    A btu is a btu!
    BTU: British Thermal Unit = the amount of heat needed to raise the temperature of one pound of water one degree Fahrenheit. Usually measured per hour.
    Whoever told you that nonsense doesn’t know what they’re talking about.
    Here’s another wrinkle: I’m only aware of one or maybe two manufacturers who presently offer mod/cons in the 50k range. Most start around 80k.
    Bob Boan
    HydronicMike
  • GGross
    GGross Member Posts: 2,035
    an indirect does not really have a minimum requirement (unless burnham does something weird!). your DHW usage and requirements dictate the required BTU/hr delivered to the indirect. That all being said most of what the 3rd party told you is true. not sure why they randomly added 40% though! in my experience, when done correctly, manual J is already applying a safety factor.
    checking your Burnham the wording is just strange, they do not actually require a minimum boiler output, that's just to meet the ratings shown on that sheet. so no they aren't doing anything weird, you still calculate your space heating needs, and your DHW needs, and size the boiler on the largest of the 2.
    EBEBRATT-Ed Member Posts: 20,826
    Use a boiler with about 50,000 btu Net capacity Heating output. With two people your indirect will be fine.
    It is normal for the boiler MFGs to tell what boiler size to use for an indirect but in you case that is not a concern. No boiler needs to be upsized for DHW unless you have a hot tub or some other high usage item.
    The 3rd party is CYA.
    Calculating the heat loss of the house is pretty straightforward. Everyone's DHW use is different. But with a 2 person house no upsizing is needed.
    How large is your old boiler? It is a shame to throw out a 4 year old boiler. If the boiler is otherwise ok I would work to resolve the short cycling issue and keep the boiler.
    Going to a smaller boiler any energy savings will be negligeable.
    JMHO
    GGrosspecmsg
  • HydronicMike
    HydronicMike Member Posts: 411
    If there's nothing wrong with your boiler, I'd add a buffer tank.
  • DCContrarian
    DCContrarian Member Posts: 1,545
    Yeah, I'd want to know what's wrong with the existing boiler and try to fix that before replacing one that's four years old.
  • DCContrarian
    @Ironman : "I’m only aware of one or maybe two manufacturers who presently offer mod/cons in the 50k range. Most start around 80k."
    This is going to be the real issue. You can make the Manual J as accurate as you can, but at the end of the day you're limited to the equipment that's available. Most installers have lines that they work with so you'll be limited to what they have.