Strange flap inside condensate side of 2 pipe radiator

Options
ethicalpaul
ethicalpaul Member Posts: 8,959

My friend has a big old house in Hamtramck Michigan with a big 2 pipe system

He found this inside the union on the condensate side of a radiator. It swings freely. There is a trap under it in the basement.

Anyone know what it is? Some check valve to hold vacuum or something??

IMG_1889.jpeg

80549938711__0707727C-C92A-4356-B773-18D24947A612.jpeg

NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,721

    @ethicalpaul

    I don't know but looking at the trap in the basement it looks like with the extra elbows like it may have been added after the fact.

    What are the other radiators telling you?

    Maybe the little flapper was the trap and the thermostatic traps were added after, Any Name on anything? Any cross over traps or boiler return trap etc?

    ethicalpaul
  • mattmia2
    mattmia2 Member Posts: 17,763

    this smells a whole lot like a vapor system that someone put a radiator trap on because they didn't understand it. what do the radiator valves look like? any devices near the boiler?

    ethicalpaul
  • mattmia2
    mattmia2 Member Posts: 17,763

    @Steamhead, i don't think you need to tell @ethicalpaul what TLAOSH is…

    ethicalpaulold_diy_guybjohnhy
  • ethicalpaul
    ethicalpaul Member Posts: 8,959

    thanks all and @Steamhead for the ID

    I’m not near the system but I’ll ask him for those verifying identifiers.

    It would not surprise me at all if stuff had been incorrectly added over the decades

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Jamie Hall
    Jamie Hall Member Posts: 27,651

    Just to add a bit… that trap in the basement may have been added after some nit-wit raised the pressure and things stopped working properly. That system wants the pressure down around 4 ounces…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,721

    Just wondering if the other radiators also have the added traps.

    I would assume as @Steamhead posted the original system did not have radiator traps and relied on the flapper.

    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 8,959

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 17,763

    but most 1 pipe and non-vapor 2 pipe system can tolerate 2-3 psig. vapor systems rely on the pressure differential between the supply and return being under .5 psi or so and the size if the opening in the radiator valve to regulate the steam admitted to an emitter to less than the amount of steam that radiator can condense. if the pressure is too high steam will end up blowing through the emitters in to the returns.

    ethicalpaul
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,602
    edited July 13

    "…the opening in the radiator valve to regulate the steam admitted to an emitter to less than the amount of steam that radiator can condense. if the pressure is too high steam will end up blowing through the emitters in to the return"

    I'm surprised that @mattmia2 was not able to incorporate more words like: Emulator, Altimeter, and Ulcerates into that statement.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ScottSecor
  • mattmia2
    mattmia2 Member Posts: 17,763

    a lot of vapor systems use convector cabinets rather than standing cast iron radiators…

  • Steamhead
    Steamhead Member Posts: 18,774

    Give him time- shows he paid attention in his English classes.

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

    EdTheHeaterMan
  • ChrisJ
    ChrisJ Member Posts: 17,585

    The word of the day : Indemnification.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.