Strange flap inside condensate side of 2 pipe radiator
My friend has a big old house in Hamtramck Michigan with a big 2 pipe system
He found this inside the union on the condensate side of a radiator. It swings freely. There is a trap under it in the basement.
Anyone know what it is? Some check valve to hold vacuum or something??
    @ethicalpaul
    I don't know but looking at the trap in the basement it looks like with the extra elbows like it may have been added after the fact.
    What are the other radiators telling you?
    Maybe the little flapper was the trap and the thermostatic traps were added after, Any Name on anything? Any cross over traps or boiler return trap etc?
    this smells a whole lot like a vapor system that someone put a radiator trap on because they didn't understand it. what do the radiator valves look like? any devices near the boiler?
    @Steamhead, i don't think you need to tell @ethicalpaul what TLAOSH is…
    ethicalpaulold_diy_guybjohnhy
    ethicalpaul Posts: 9,076
    thanks all and @Steamhead for the ID
    I’m not near the system but I’ll ask him for those verifying identifiers.
    It would not surprise me at all if stuff had been incorrectly added over the decades
    Just to add a bit… that trap in the basement may have been added after some nit-wit raised the pressure and things stopped working properly. That system wants the pressure down around 4 ounces…
    Just wondering if the other radiators also have the added traps.
    I would assume as @Steamhead posted the original system did not have radiator traps and relied on the flapper.
    but most 1 pipe and non-vapor 2 pipe system can tolerate 2-3 psig. vapor systems rely on the pressure differential between the supply and return being under .5 psi or so and the size if the opening in the radiator valve to regulate the steam admitted to an emitter to less than the amount of steam that radiator can condense. if the pressure is too high steam will end up blowing through the emitters in to the returns.
    EdTheHeaterMan Posts: 12,952
    edited July 13
    "…the opening in the radiator valve to regulate the steam admitted to an emitter to less than the amount of steam that radiator can condense. if the pressure is too high steam will end up blowing through the emitters in to the return"
    I'm surprised that @mattmia2 was not able to incorporate more words like: Emulator, Altimeter, and Ulcerates into that statement.
    ScottSecor
    a lot of vapor systems use convector cabinets rather than standing cast iron radiators…
    Steamhead Posts: 19,007
    Give him time- shows he paid attention in his English classes.
    Semi-retired
  • ChrisJ
    ChrisJ Posts: 17,763
    The word of the day : Indemnification.
