Melted Coil drain pan
An AC problem but I think the cause is on the furnace side…
I Went to a "furnace leaking water" call today and it turned out to be a melted condensate drain pan under the coil. First one for me. The new pan won't be here for a week. The person is on oxygen and the sense I get probably end of life scenario. So we couldn't leave it. After getting the drain pan out I patched it up with angled aluminum, flex tape and got drainage to the condensate pump.
The reason I'm actually posting this is because I'm in the "why did this happen" mode and need to get this figured out before winter time rolls around again and the heat comes on. The owner tells me that this happened last summer as well but it wasn't as bad. The rust I see around the base of the Furnace tells me there was a pretty good bit of water around here last year.
I'm thinking there is a control issue where the temperature in the bonnet is being allowed to get too high or was allowed to get too high at some point. This (the high heat) might have possibly even been repaired before we got involved. I serviced this boiler in February and didn't see any issues with it getting too hot (net break temp 410) and had good combustion numbers and nothing to indicate a breach in the heat exchanger.
the furnace is an NOMF155E19, and the coil is an AllStyle ASUC48-M2866G-7-VP4
An evaporator coil cannot sit directly on top of an oil fired furnace. It needs a minimum four inch spacer.
If it does have the spacer, check the furnace ratings for heat rise and max supply air temperature, then start testing. Also make sure its the correct firing by checking the nozzle and pump pressure.
did you do the basic temp rise? Running wayyy too hot. The monkey will jump on your back if you put in a new pan and it happens again. Gotta get more air or less heat. Is the heat exchanger buggered?
150K BTU Oil Furnace?
What's the temperature Rise? What's the static pressure TESP?
Yes, there should be a 4-6" riser between the furnace and a/c coil!
maybe they were overly optimistic.
A riser may get the pan away from the HX but it won't change the air temp one bit.
many manufacturers recommend it!
I'm the last one to tune it which was earlier this year and it is the correct firing rate, nozzle, pump pressure and Proper draft over fire. I believe that spacing is correct but I wasn't looking for it so when I go back I will definitely check that and will checking Supply temperature
Long shot but, I can see people doing that.
I don't know why everybody uses upflow furnaces. With upside down you don't strictly even need a stinking drain pan.
leaks in the return dropping down to the floor are less of a loss of energy than hot air leaking as it makes a loop up to the supply trunk. hot air wants to rise up not be pushed down so the blower is working against gravity which also increases losses with leakage.
Leaks dropping down on a downflow furnace are worse. You would have all kinds of mold and God know what else. Every furnace needs a drain pan. The condensate has to go somewhere
you would want the coil under a downflow furnace so that it doesn't cool the hx and cause condensation on the fire side.
The ductwork's reversed direction actually reduces carryover.
My guess is that up flow is so common because they had to be when furnaces didn't have blowers? Also the reason why most are big boy? Efficiency ratings were higher for upside down before high efficiency came along.
- 87.7K THE MAIN WALL
- 129 Chimneys & Flues
- 122 Geothermal
- 79 Pipe Deterioration
- 396 Solar
- 17 Recall Announcements
