Melted Coil drain pan
An AC problem but I think the cause is on the furnace side…
I Went to a "furnace leaking water" call today and it turned out to be a melted condensate drain pan under the coil. First one for me. The new pan won't be here for a week. The person is on oxygen and the sense I get probably end of life scenario. So we couldn't leave it. After getting the drain pan out I patched it up with angled aluminum, flex tape and got drainage to the condensate pump.
The reason I'm actually posting this is because I'm in the "why did this happen" mode and need to get this figured out before winter time rolls around again and the heat comes on. The owner tells me that this happened last summer as well but it wasn't as bad. The rust I see around the base of the Furnace tells me there was a pretty good bit of water around here last year.
I'm thinking there is a control issue where the temperature in the bonnet is being allowed to get too high or was allowed to get too high at some point. This (the high heat) might have possibly even been repaired before we got involved. I serviced this boiler in February and didn't see any issues with it getting too hot (net break temp 410) and had good combustion numbers and nothing to indicate a breach in the heat exchanger.
the furnace is an NOMF155E19, and the coil is an AllStyle ASUC48-M2866G-7-VP4
    109A_5 Posts: 4,759
    Restricted air flow (plugged filter or evaporator or other air flow restriction) and an inoperative high limit switch.
    Robert_H
    EBEBRATT-Ed Posts: 21,328
    Undersized ductwork either supply or return.
    Supply registers closed off.
    Supply or returns blocked by furniture or carpeting
    Robert_H
    some coil/furnace combinations are supposed to be installed with a spacer between the furnace and coil, especially oil furnaces, check the instructions.
    HVACNUT
    HVACNUT Posts: 7,784
    An evaporator coil cannot sit directly on top of an oil fired furnace. It needs a minimum four inch spacer.
    If it does have the spacer, check the furnace ratings for heat rise and max supply air temperature, then start testing. Also make sure its the correct firing by checking the nozzle and pump pressure.
  • GW
    GW Posts: 5,259
    did you do the basic temp rise? Running wayyy too hot. The monkey will jump on your back if you put in a new pan and it happens again. Gotta get more air or less heat. Is the heat exchanger buggered?
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    Robert_H
    pecmsg Posts: 7,634
    150K BTU Oil Furnace?
    What's the temperature Rise? What's the static pressure TESP?
    Yes, there should be a 4-6" riser between the furnace and a/c coil!
    109A_5 Posts: 4,759
    edited June 30
    Blower Off delay too short or not working correctly ?
    109A_5 Posts: 4,759
    Having a riser is not a bad idea, but I suspect something else is going on.
    Robert_H
    A riser may get the pan away from the HX but it won't change the air temp one bit.
    pecmsg Posts: 7,634
    many manufacturers recommend it!
    the radiant energy from the hx would fall off quite a bit moving it 6" away. you do need to look for closing off registers to "save energy" too though.
    Robert_H
  • Robert_H
    Robert_H Posts: 377
    I'm the last one to tune it which was earlier this year and it is the correct firing rate, nozzle, pump pressure and Proper draft over fire. I believe that spacing is correct but I wasn't looking for it so when I go back I will definitely check that and will checking Supply temperature
    I would also ask the owner if they are killing the furnace with the emergency switch instead of letting it run on the stat. That would kill the fan with a hot HX and no moving air which could melt it.
    Long shot but worth asking.
    GWRobert_H
  • Robert_H
    Robert_H Posts: 377
  • jumper
    jumper Posts: 2,625
    I don't know why everybody uses upflow furnaces. With upside down you don't strictly even need a stinking drain pan.
    leaks in the return dropping down to the floor are less of a loss of energy than hot air leaking as it makes a loop up to the supply trunk. hot air wants to rise up not be pushed down so the blower is working against gravity which also increases losses with leakage.
    Leaks dropping down on a downflow furnace are worse. You would have all kinds of mold and God know what else. Every furnace needs a drain pan. The condensate has to go somewhere
    you would want the coil under a downflow furnace so that it doesn't cool the hx and cause condensation on the fire side.
  • GGross
    GGross Posts: 2,104
    You just blow all the condensate down into the ductwork?
    EBEBRATT-Ed
  • jumper
    jumper Posts: 2,625
    The ductwork's reversed direction actually reduces carryover.
  • jumper
    jumper Posts: 2,625
    My guess is that up flow is so common because they had to be when furnaces didn't have blowers? Also the reason why most are big boy? Efficiency ratings were higher for upside down before high efficiency came along.
  • pedmec
    pedmec Posts: 1,488
    Make sure they didn't jump out the high limit to compensate for the undersized ductwork. That is a pretty good size furnace and i'll bet the ductwork is undersized. I had one where once it started to get real cold out the short cycling couldn't keep up with the heat lose so instead of fixing the ductwork the tech jumped out the high limit. When the pan melted and landed on the heat exchanger it smoked the tenants out. You should be able to tell it melted by visually inspecting it
  • Robert_H
    Robert_H Posts: 377
    edited August 9
    Thanks again for all the help!
    I returned today with the new drian pain and was happy to see that the patched up pan did not leak. Unfortunately I did not notice that the new pan wa for a single coil instead of a double coil before trying to install it.
    Oops
    While I was there I tested the heat rise at 83 which is close to the high end (55-85)
    Also tested the high limit shut off, blocking the filter. the install switch is a 180-30. measuring temp in the supply duct, it did not shut off once it hit 186F I pulled the blockage and stopped the test.
  • Robert_H
    Robert_H Posts: 377
    that's scary!
    PC7060