3/8 pex lines for tiny zones

Options
GW
GW Member Posts: 5,193

I haven't done 'new work' in forever, mostly chop-swap. As recall, the 3/8 pex/plastic lines will carry a good amount, 1 gpm under normal circumstances? Up to 10000 btu if we use traditional numbers? I have a guy that want's micro-zones (yes we have a buffer tank)

Thanks for any input.

Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com

Comments

  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,812
    edited June 26

    With 3/8" PEX, you could flow as much as 1.3gpm. At a 20°Δ, that's a max of 13,000 BTU's.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    GW
  • hot_rod
    hot_rod Member Posts: 27,873

    depends on the loop length.

    The PPI online calculator is good to run examples

    https://plasticpipecalculator.com/PressureDropHeadLoss.aspx

    100’ of 3/8 pex at 1 gpm

    14, head will take a high head circ

    IMG_2686.jpeg IMG_2685.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GWGroundUp
  • GW
    GW Member Posts: 5,193

    Just 6600 btu on the largest zone- should be good

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • mattmia2
    mattmia2 Member Posts: 17,500
    edited June 27

    i would figure .5-.75 gpm for 3/8" pex which gives you ~7000 btu/hr at 20f delta t. that is a pretty good sized radiator. if you're trying to do something low temp you might need to think about what flow you need.

    GW
  • GW
    GW Member Posts: 5,193

    Yes just regular temps- 180.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • hot_rod
    hot_rod Member Posts: 27,873

    50' of 3/8 with a .6 gpm flow

    Screenshot 2026-06-27 at 6.12.25 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,812
    edited June 28

    Sorry, this is wrong and .6 - 1.1gpm is correct. I was figuring ½” PEX.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    mattmia2
  • GroundUp
    GroundUp Member Posts: 2,528

    The biggest question is why? What's stopping you from using 1/2" that's available everywhere?

    Alan (California Radiant) Forbespecmsg
  • Dave H_2
    Dave H_2 Member Posts: 627

    I would second this, going to 3/8" makes it harder to locate fittings, manifold connections and pipe as there are not that many manufacturers extruding 3/8".

    When I do underfloor radiant, i try to always work with 3/8" for ease of install but in tyhis case of supply/return piping to high temp radiation, 1/2" is the way to go

    Dave Holdorf

    Technical Training Manager - East

    Taco, Inc

  • GW
    GW Member Posts: 5,193

    Why- there were some tricky routes to weave in and out of the framing.

    The HO wanted insulation the whole route(s), and drilling holes to accommodate the OD of the armaflex. I simply wanted to keep the holes to a minimum.

    3/8 fittings availability are not an issue

    We started this job yesterday. I chickened out and went 1/2”

    Yet the sociology is evident- we all mostly oversize to avoid questions.

    I remember 20 or 25 years ago this local vendor/heating designer proposed a design to a certain homeowner. I cannot recall specifics, but the gist was there was a little remodel going on the heating area (condominium) was going to double or triple. There was an existing 5/16 inch pex line. I grabbed the 5/16 and created a little manifold and did what I’m guessing was 200 or 300 ft.² of radiant. By human standards, this should not have worked. I recall the guy waiting two or three months to pay me because he didn’t think it would work. I eventually got the check in the mail. The lesson stayed with me, the fact that BTUs can do more work than we generally think they can.

    (Those were the old days, business doesn’t work like that anymore)